How Would You Calculate the Force of a Falling 220kV Conductor?

AI Thread Summary
Calculating the force of a falling 220kV conductor involves considering both vertical and horizontal forces, especially during scenarios like transferring the cable between towers or sagging it. The weight of the cable will not fully impact the scaffold, as some weight is supported by the towers and ground. When the cable breaks, it will not drop straight down but will be propelled towards the remaining attached tower, complicating the fall dynamics. Additionally, external factors like wind and ice can significantly affect the cable's behavior during a fall, necessitating a robust scaffold design. Proper mesh installation is essential to prevent cable loops from obstructing the railway.
Chadwick
Messages
2
Reaction score
0
TL;DR Summary
How would you calculate the force at a point of a falling 220kV Conductor?
Summary: How would you calculate the force at a point of a falling 220kV Conductor?

Hi, bit a of a funny one.
I need to calculate the force of a cable falling at a point (left edge of a scaffold) as detailed in the attached sketch. (Not to scale what so ever).
We’re building a scaffold between two towers to protect a railway. It needs to withstand at least 1 cable falling, if it were to fall it would release at the tower, I would consider whichever the worst case would be at.

Considering the worst case scenario what would the force be on the scaffold?

Now it would be simple if we treat the cable as a solid, but since it is a cable how would this affect the fall?
I imagine the whole weight of the cable would not be landing on the scaffold, some weight would be taken by the tower and possibly the ground.

Any help you can give would be appreciated!
 

Attachments

Engineering news on Phys.org
Wow. Tough question. I moved it to ME because it appears that the electricity plays no role.

How paranoid worst case do you need? I'm wondering of the end of the cable can snap like a bull whip.
 
Thanks for that!

Hard question when you're trying to balance over engineering and costs haha.
If our aim is to protect the railway we might be okay with assuming that the whip would occuur at the ends, far enough from the scaffold.Also, appologies, forgot to include a fairly crucial element to the problem.

Failure could potentially occur at when transferring a cable from one tower to the other, or when sagging the cable, this would introduce horizontal forces onto the cable which would impact the fall of the cable.

In transferring the winches would exert roughly 2.7t (27kN) horizontally onto the cable, when sagging a design 3.7t (37kN) would be applied.

In case it wasn't complicated enough :)
 
When a cable breaks it will probably be at the support point where there is an acoustic impedance mismatch.

The end where the break occurs will not start to fall until tension in the cable has been relieved. That involves the speed of a tension wave in the cable. The cable will not drop flat on the ground across your scaffold, it will be propelled toward the remaining attached tower by cable tension. It will coil, kink and tangle before it reaches the ground. The scaffold will need a mesh that prevents loops of cable falling through to obstruct the track.

Wind force on a cable during a wind storm is often greater than gravity, so you can expect the cable to fall sideways by more than one pylon height. I have found antenna elements 3 times further from the tower than the antenna height, some have not yet been found.

Ice buildup will change the game when lengths of ice fall on the tracks. Ice will increase windage, but will reduce the problem of stored energy in the tension.
 
  • Like
Likes russ_watters
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly
Thread 'What's the most likely cause for this carbon seal crack?'
We have a molded carbon graphite seal that is used in an inline axial piston, variable displacement hydraulic pump. One of our customers reported that, when using the “A” parts in the past, they only needed to replace them due to normal wear. However, after switching to our parts, the replacement cycle seems to be much shorter due to “broken” or “cracked” failures. This issue was identified after hydraulic fluid leakage was observed. According to their records, the same problem has occurred...
Back
Top