I get a shock when touching water pipe

AI Thread Summary
An individual experienced electric shocks when touching a water tap in their apartment and conducted tests to identify the issue. They discovered a voltage of 120 V between the water pipe and hot wires after turning off all breakers and testing each outlet. The problem was traced back to a faulty refrigerator, which caused the shocks due to improper electrical connections. The user successfully resolved the issue by repositioning the refrigerator's plug to ensure correct hot and neutral alignment. The discussion highlights the importance of addressing electrical safety concerns promptly and suggests consulting a qualified electrician for similar issues.
adisabeba
Messages
1
Reaction score
0
I am living in an apartment and suddenly we started to get an electric shock, at random, when touching a water tap. Since I am an Electrical Technician, I started

my research on the origin of the problem, and after carrying out a series of tests I found out 'at the end' that turning off all the breakers (in the breaker box) and measuring the voltage between each hot wire and the metal box surface I got a full 120 V reading! The other tests I made were the following:

1- I turned off all the breakers and then turned each back on, and then off, sequentially and measuring the voltage at the corresponding outlet. In all

the cases I got a full 120V between the water pipe and the hot wire at the outlet. With this test I wanted to verify any leaking voltage of each breaker line.

2- When testing the heater line (turning its breaker on), I found out that there was a 90 V reading between the hot wire and each of the two ends of the

water heater resistance; of course, after I set apart the cables.

So, the only clue I have is the breaker box-to-hot-wires voltage, and I wonder where and how the water line and the electrical metallic conduits shake hands. Any help?
Thanks

I was not really sure whether to add comments to my previous post regarding the problem I reported, since it was closed with not right to reply and suggesting the get an electrical technician. In such cases, I would suggest the Administrator of this site to leave the door open, so the poster could reply whether or not he has solved the problem. In my case, I did solve the problem by myself and I am an Electrical Technician... Anyway, just for helping the audience with similar issues, "the problem was caused by my old refrigerator(1) and it was solved by swapping the electric plug position: the plug-outlet hot and neutral position must coincide." The electrical shock existed because the fridge's inlet water valve is connected to a copper tube and this to an external water filter. So, having a faulty fridge electrical issue, it explains the electric shock. I was really worried about the high life-threatening risk I was on, but it is luckily over.

Regards.


1- Whirlpool 8ED25DQXXN00
 
Last edited by a moderator:
Engineering news on Phys.org
Sounds like a bad Earth somewhere. My guess is that the case of the heater has an Earth wire connected to it but the other end of that Earth wire or the Earth for the whole place is bad. You might be seeing capacitive coupling between hot and this floating Earth wire. In effect the disconnected Earth wire is acting like an aerial and is picking up 80-120v and making it appears on exposed metal that is meant to be earthed.
 
PS This is quite a dangerous situation. You should get a qualified electrician to look at it. Have him show you the problem if you want to learn.
 
So, do you have 240 coming into your house ? Here in the US we get 240 3 phase which appears as 120 if you look at either of the hot sides versus neutral (ground). Anyway, I assume your breaker box is grounded and so is the water tap unless the pipe is plastic. So it is strange that you would get shocked and potentially dangerous. Also, do you have Ground Fault Interrupters? Well , they ain't workin! Like you said, it could be leakage which a high impedance meter would read as full scale. Interesting problem. If you never respond again, I will know what happened... :H
 
adisabeba said:
I am living in an apartment and suddenly we started to get an electric shock, at random, when touching a water tap. Since I am an Electrical Technician, I started

my research on the origin of the problem, and after carrying out a series of tests I found out 'at the end' that turning off all the breakers (in the breaker box) and measuring the voltage between each hot wire and the metal box surface I got a full 120 V reading! The other tests I made were the following:

1- I turned off all the breakers and then turned each back on, and then off, sequentially and measuring the voltage at the corresponding outlet. In all

the cases I got a full 120V between the water pipe and the hot wire at the outlet. With this test I wanted to verify any leaking voltage of each breaker line.

2- When testing the heater line (turning its breaker on), I found out that there was a 90 V reading between the hot wire and each of the two ends of the

water heater resistance; of course, after I set apart the cables.

So, the only clue I have is the breaker box-to-hot-wires voltage, and I wonder where and how the water line and the electrical metallic conduits shake hands. Any help?
Thanks
In cases like this you must employ a qualified electrician to diagnose and fix the fault, and you should do so immediately.

Thread closed.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...