Is a Contactor Suitable for High Power 3 Phase Transfer Switching?

Click For Summary
SUMMARY

The discussion centers on the suitability of using a contactor for a 3-phase, 480VAC, 300A transfer switch to switch power to a generator during outages. Participants highlight that while contactors rated for this power level exist, static switches utilizing SCRs are also viable alternatives, particularly in critical applications. Mechanical interlocks are recommended to prevent simultaneous connections of both power sources. The conversation emphasizes the importance of professional electrical engineering knowledge when designing such systems.

PREREQUISITES
  • Understanding of 3-phase electrical systems, specifically 480VAC configurations.
  • Familiarity with contactor and static switch operation and ratings.
  • Knowledge of electrical interlocking mechanisms for transfer switches.
  • Basic principles of generator start circuits and time delay relays.
NEXT STEPS
  • Research "3-phase 480VAC contactors" for suitable options and specifications.
  • Explore "static transfer switches" and their applications in UPS systems.
  • Learn about "mechanical interlocks" for transfer switch designs.
  • Investigate "time delay relay" configurations for generator start circuits.
USEFUL FOR

Electrical engineers, power system designers, and professionals involved in critical power applications who are looking to implement or improve transfer switch systems.

littleblackdo
Messages
4
Reaction score
0
I am designing a transfer switch to switch main power to Generator when main power is lost. Main power is 3 phase, 480VAC and rated at 300amps. Is a contactor a good choice for this? I cannot seem to find one rated this high of power.
 
Engineering news on Phys.org
I'm curious. Why design and not just purchase a Automatic Transfer Switch?

http://www.abrahamindustrial.com/buy/images/upload/thum/ASCO_Series_300.jpg

Anyway, just do a google search on "3 phase 300 amp contactors". There's a bunch.
 
There are also "static switches" that easily handle 300 A at 480VAC. They use SCRs and are commonly used in large UPS installations.

For instance, http://www.redoups.com/F24156/static_transfer_switches_singlethree_phase_251000amp.html

Cheers,
Bobbywhy
 
Last edited by a moderator:
Are you looking for a True Transfer Switch - these are typically interlocked (electrically or mechanically) so both sources are not connected at the some time ( I prefer mechanical because electricians LOVE manually pushing contactors closed - so think of manually pushing the Gen Contactors closed when the line contactor is being used - ugly)
So there are mechanical "kits" for some of the larger 3 phase contractors so that both units are not in the same device -

I just googled Surplus ATS and they pop right up

Typically Static Switches ( Thyrisotr / SCR ) are not needed (or are cost justified) due to start up time of Generators - but in critical loads this is sometimes done - can also help with the transfer back to the line(utility)
 
I have to "conceptually" design this for a work project and was looking for ideas prior to meeting on it.

Main voltage is 480VAC, 3 phase Wye with 300A maximum. The Emergency/Alternate Source is 480VAC, 3 phase wye Generator. I was thinking of connecting the Main Source to 3 phase, 4 pole contactor. When power is lost, contactor closes time delay relay which will close another contactor after time limit expires to send start signal to Generator. Does the Contactor need to be rated at 277V or 480? Am I even on the right track with my ideas?
 
What if the generator doesn't start?
 
I am working on transfer switch. I should not have said "send start signal to Generator". I guess it will close contacts in start circuit.
 
littleblackdo said:
I have to "conceptually" design this for a work project and was looking for ideas prior to meeting on it.

Main voltage is 480VAC, 3 phase Wye with 300A maximum. The Emergency/Alternate Source is 480VAC, 3 phase wye Generator. I was thinking of connecting the Main Source to 3 phase, 4 pole contactor. When power is lost, contactor closes time delay relay which will close another contactor after time limit expires to send start signal to Generator. Does the Contactor need to be rated at 277V or 480? Am I even on the right track with my ideas?

Why try to formulate a "conceptual design" in a vacuum? The protection of "critical loads" with an UPS and diesel generator is a mature technology and has developed over many decades. Hundreds of equipment suppliers and thousands of consultants can easliy answer all your questions.

Cheers,
Bobbywhy
 
Thread closed temporarily for Moderation...
 
  • #10
So, littleblackdo, I'm uncomfortable with your lack of professional EE knowledge and the powers involved in your "project". If you have been given this as a work assignment, you should have the professional EE qualifications to answer these questions on your own. Posting high power high voltage questions in a web forum is not a good thing, and is against the PF rules for a reason. This thread is closed.
 

Similar threads

  • · Replies 25 ·
Replies
25
Views
5K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 3 ·
Replies
3
Views
2K
Replies
2
Views
1K
Replies
6
Views
4K
  • · Replies 3 ·
Replies
3
Views
3K
Replies
2
Views
2K
Replies
13
Views
4K
  • · Replies 10 ·
Replies
10
Views
2K
  • · Replies 31 ·
2
Replies
31
Views
5K