NUCENG said:
Re: AntonL #3051, NUCENG #3053 BOREK #3054
As promised. I looked at the TEPCO sequence of events and JAIF Plant Status reports.
Explosions were reported on 3/12, 3/14, and 3/15, Unit 4 was damaged about the 15th or 16th.
Seawater had been injected into RPVs on Units 1 and 3.
Seawater injection into containment was still being planned/considered on 3/16.
TEPCO is still reporting no coolant leakage into containment on all units. ?
Conclusion: Sea water injection into contaiment followed explosions and therefor oxygen dissolved in seawater could not have been responsible for creating an explosive mixture inside containment. The only remaining possibility would have been containment failures from the earthquake, but since there was a high pressure in containment, it would be tough to get air inleakage. Unless I missed something about the mixture of steam, oxygen, hydrogen, and nitrogen in containment, I just don't see an condition that could lead to an explosion inside containment.
Time line based on TEPCO/NISA and Der Spiegel reports.
http://www.nisa.meti.go.jp/english/files/en20110327-2-1.pdf
http://www.spiegel.de/images/image-193266-galleryV9-quxr.jpg
16:36 March 11 - Loss of cooling (EDGs) at Unit 1 (about 1 hour, 50 min after earthquake, which is just after the tsunami hit the site)
15:36 March 12 -
Explosion of Unit 1 (Upper containment heavily damaged)
20:20 March 12 - Seawater injection into Unit 1 RPV (via fire extinguisher line)
20:41 March 12 - Venting of Unit 3
08:41 March 13 - Venting of Unit 3
09:20 March 13 - Steam release from Unit 3
11:55 March 13 - Fresh water started to be injected to RPV via the Fire Extinguish Line.
13:12 March 13 - Seawater started to be injected to RPV via the Fire Extinguish Line.
01:10 March 14 - Seawater injection for Units 1 and 3 was interrupted due to the lack of seawater in pit.
03:20 March 14 - Seawater injection to RPV for Unit 3 was restarted.
05:20 March 14 - Operation of Vent
07:44 March 14 - The pressure in Primary Containment Vessel (PCV) of Unit 3 rose unusually.
07:52 March 14 - TEPCO reported to NISA on the event falling under the Article 15 of the Act on Special Measures Concerning Nuclear Emergency Preparedness.
11:01 March 14 -
Explosion of Unit 3
19:20 March 14 - Seawater injection into Unit 2 RPV (via fire extinguisher line)
06:10 March 15 -
Sound of Explosion in Unit 2 - explosion seems to be in containment.
06:14 March 15 - It was confirmed that a part of wall in the operation area of Unit 4 was damaged.
11:00 March 15 - The fire (hydrogen deflagration?) at Unit 4 occurred. (09:38 March 15th) TEPCO reported that the fire was extinguished spontaneously.
It would be useful to review the progression of damage to Unit 4 after the explosion of Unit 3, because immediately after the explosion of U3, the upper containment of Unit 4 seemed to be more or less intact.