Japan Earthquake: Nuclear Plants at Fukushima Daiichi

AI Thread Summary
The Fukushima Daiichi nuclear plant is facing significant challenges following the earthquake, with reports indicating that reactor pressure has reached dangerous levels, potentially 2.1 times capacity. TEPCO has lost control of pressure at a second unit, raising concerns about safety and management accountability. The reactor is currently off but continues to produce decay heat, necessitating cooling to prevent a meltdown. There are conflicting reports about an explosion, with indications that it may have originated from a buildup of hydrogen around the containment vessel. The situation remains serious, and TEPCO plans to flood the containment vessel with seawater as a cooling measure.
  • #4,751
TCups said:
10,000,000 Curies?! Really? The equivalent radioactivity of ten thousand kilograms of radium?! Ten metric tonnes?!

What sort of things accumulate in precipitators? Co 60? Can someone tell us more about "radwaste buildings" please? Does contamination from the radwaste building fit with these early measurements? (see attached)

http://i306.photobucket.com/albums/nn270/tcups/4000d390.png

The U3 radwaste building would correspond to the radiation levels of 60 and 35 msv/hr. the radwaste building is to the left of the U3 reactor building.
 

Attachments

  • March 24_4.jpg
    March 24_4.jpg
    71.6 KB · Views: 416
Last edited by a moderator:
Engineering news on Phys.org
  • #4,752
http://energheia.bambooz.info/index.php?option=com_k2&view=itemlist&task=date&month=4&year=2011&lang=it"

http://www.rchoetzlein.com/theory/?p=171"
 
Last edited by a moderator:
  • #4,753
gmax137 said:
Some multi-unit sites have shared control rooms, some don't. There are pros and cons to each approach. Pro: It may be helpful to know firsthand what is going on with the other unit, some plant equipment may be shared between the units (eg, security, non-nuclear water treatment, etc.). Con: potential single point vulnerability affecting both units, potential distractions, etc. Most of the sites try to minimize the cons. For example, when one unit is down for an outage there is more activity (as maintenance crews request systems to be realigned for their work) -- nowadays this is usually re-located to another room to prevent it from distracting the operators on the boards.



This simply isn't the way it's done, at least in the plants I been to. The individual operators are assigned to one unit or the other, a two-unit control room has twice the operators as a one unit facility. And if you haven't been inside one of these control rooms you may have misconceptions as to what they are like. They are run with an essentially military protocol; they are quiet, organized, regimented places. Many (most?) of the operators are ex-navy reactor operators. At least that's how it is in the ones I've been to.

I've been a Shift Manager in a multi unit control room at the Bruce A NPP in Ontario, Canada. This design has the control panels for all 4 units in a circle. From an incident or upset perspective, I certainly liked this design from a command and control point of view. I could walk into the MCR and very quickly assess the impact on my 4 unit plant. We had a minimum complemet of operators on each unit and if we had excess - then they can quickly assist on the unit in trouble.

Are there cons - absolutely. There is additional distractions when a unit is in outage and some common mode issues - but these can be safely managed.
 
  • #4,754
michael200 said:
<..>the radwaste building is to the left of the U3 reactor building.

How do you know this is a radwaste building?
 
Last edited:
  • #4,755
michael200 said:
The U3 radwaste building would correspond to the radiation levels of 60 and 35 msv/hr. the radwaste building is to the left of the U3 reactor building.

near the unit of building3... look to one of the trajectories colored in yellow on the post https://www.physicsforums.com/showpost.php?p=3256828&postcount=4350". goes directly on it..
 
Last edited by a moderator:
  • #4,756
Is there any experience with TEPCOs efforts to stabilize the dust and small debris around the site by spraying a binder on the surface?
Afaik, it is common to spray oil on dirt roads in rural areas to keep the dust down, but here there is a good prospect for severe rains and possible storms as well. So does it all get washed into the sea?
 
  • #4,757
AS we have some operational knowledge here on the forum, let me ask some questions about the control rooms, to clarify the "cons" which in my mind are just not limited to distractions between shifts (even if this can be a factor, and has be a con in the example of TMI):

1) could you precisely locate the control rooms for the various reactors at Daichi plant, on a map or on a picture (position and at which floor)?

2) what kind of protections (mechanical and radiological mainly) do they normally have: resistance to explosions (thickness of concrete, etc.), shielding to some level of ambient radiations, resistance to water flooding, type of air filtering, etc.

My questions relates to the fact that in my mind, the problem with one common control room is that this is the opposite of some kind of redundancy principle in case of accident, because in this case there is "concentration" of the equipement: if one rooms becomes damaged or no more usable because of high radiations inside, how can you still continue to drive the second reactor even if it is undamaged in itself? This also lies to an other question: can a reactor be put in cold stop, and MAINTAINED -in the time, but how long?- in safe cold stop without any single operator acting on it?

At Tchernobyl, and this always amazed me to say the least, they continued even during the accident or soon after to operate the adjacent reactors: first because they HAD to do it for safety reasons (I read somewhere that they feared by the way that they could lose the control of those ones if the radiations or damages were still increasing after some possible new secondary explosions), and then because they continued to produce electricity with them on this Tchernobyl plant, until 2000 when international pressures (and fundings) pushed the russian to stop all the reactors at the Tchernobyl plant.

So my question relates to this simple consideration: in case of a common room, does it mean an increased risk for losing control over a second reactor in case the first one creates conditions where the working (ambient radiations) and operational conditions (damages) are no more possible in the shared control room?
 
Last edited:
  • #4,758
etudiant said:
Is there any experience with TEPCOs efforts to stabilize the dust and small debris around the site by spraying a binder on the surface?
Afaik, it is common to spray oil on dirt roads in rural areas to keep the dust down, but here there is a good prospect for severe rains and possible storms as well. So does it all get washed into the sea?

They've done this, see this https://www.physicsforums.com/showpost.php?p=3262956&postcount=4696".

@jlduh, normally there should be an emergency control room (not sure if the term is proper in English, not a native speaker) for each reactor, which is heavily shielded (like a bunker, including air filters) and somewhat remote and allows full control over the reactor (given you have power). I assume this is where the plant operators went after leaving the main control rooms. I don't know the internal layout of Fukushima, so I can't locate it for you or tell you about how it is built.
 
Last edited by a moderator:
  • #4,759
clancy688 said:
Yeah, you're right. If I understand the press reports correctly, there are releases of 0.69 TBq I131 and 0.14 TBq C137. That's the measurable activity. So all in all, you have 0.83 trillion decays per second, most of it I131. Telling that there are releases of <1 TBq/h is not wrong. If you convert it into equivalence, you'll get 6.4 TBq/h... in my opinion there's no mistake.
I get the impression that soon there will be some chaos regarding actual activity or I131-equivalence activity in the media.
They should just report I131 and C137 separately...



The conversion is used to get a standard of how dangerous an isotope is. Krypton-85 for example emits beta particles and has a half time of 10 years, plus there's much of it inside a nuclear reactor. But it isn't very dangerous because it has a very, very fast biological half life and stays in the atmosphere without contaminating anything.

Then we have I131 and C137. If there's a mass of I131 with an activity of 1000 Bq and a mass of C137 with an activity of 1000 Bq, then both are equally dangerous. But after a year there's virtually 0 Bq of that I131 left, so it's not dangerous anymore. But the 1000 Bq mass of C137 has still an activity of nearly 1000 Bq - because it has a half time of 30 years. And because there are MUCH more atoms released as for I131.

Basically, converting activity into an equivalence is done to express the danger of an isotope over a large timeframe - while the activity in Bq only describes the danger during the exact second of the measurement.

Understanding the equivalence methodology may be aided by reviewing FGR11 and FGR12 at the following link.

http://www.epa.gov/radiation/federal/techdocs.html#report12
 
  • #4,760
Some more information on the debris map, confirming that the reactor 3 area and the area close to the main building office are still (like the beginning) the worst ones from radioactive standpoint:

http://www3.nhk.or.jp/daily/english/24_17.html
 
Last edited by a moderator:
  • #4,761
jlduh said:
Some more information on the debris map, confirming that the reactor 3 area and the area close to the main building office are still (like the beginning) the worst ones from radioactive standpoint:

http://www3.nhk.or.jp/daily/english/24_17.html

They found debris on the hill next to #3 emitting 300mSv/h?
It also says they're going to store it in containers. But they will not analyze it??
 
Last edited by a moderator:
  • #4,762
That linked report says:
Radiation levels around the Number 3 reactor building, which was damaged by a powerful hydrogen explosion, are higher than in other locations, and 300 millisieverts per hour of radiation was detected in debris on a nearby mountainside.

300mSv/hr - really?

(I'm assuming 'mountainside' is a mistranslation of sloping bank or some such.)
 
  • #4,763
biffvernon said:
That linked report says:


300mSv/hr - really?

(I'm assuming 'mountainside' is a mistranslation of sloping bank or some such.)

That's what the NHK link is saying. I had to look twice myself. After the piece of "concrete" with 900mSv/h yesterday I find it plausible, yet disturbing.
 
  • #4,764
ascot317 said:
They've done this, see this https://www.physicsforums.com/showpost.php?p=3262956&postcount=4696".

@jlduh, normally there should be an emergency control room (not sure if the term is proper in English, not a native speaker) for each reactor, which is heavily shielded (like a bunker, including air filters) and somewhat remote and allows full control over the reactor (given you have power). I assume this is where the plant operators went after leaving the main control rooms. I don't know the internal layout of Fukushima, so I can't locate it for you or tell you about how it is built.

Exactly, there is a substantial effort ongoing.
The question is whether this is likely to pay off during the summer weather or rather have unexpected consequences. What is the prior experience with this technique and what issues have been noted?
 
Last edited by a moderator:
  • #4,765
jlduh said:
So my question relates to this simple consideration: in case of a common room, does it mean an increased risk for losing control over a second reactor in case the first one creates conditions where the working (ambient radiations) and operational conditions (damages) are no more possible in the shared control room?

SEparated and hardened secondary control rooms are provided within each unit to allow essential control, cool and contain functions.
 
  • #4,766
Last edited by a moderator:
  • #4,767
So has there been 150 times as much radioactivity released?
 
  • #4,768
RealWing said:
SEparated and hardened secondary control rooms are provided within each unit to allow essential control, cool and contain functions.
too bad they don't have separate and hardened secondary backup generators.
 
  • #4,769
biffvernon said:
That linked report says:


300mSv/hr - really?

(I'm assuming 'mountainside' is a mistranslation of sloping bank or some such.)

I've looked at the drone pictures again, I'm quite certain it's the area that also grows two large, red arrows. There is a lot of what looks like concrete debris and dust there.

Edit: The greyish "dust" area is also visible on the early sat pictures (a few minutes after #3 explosion).

I don't see any other "hills" that show traces of the reactor #3 explosion.

It's quite interesting, the building to the west of #3 has suffered severe damage to its roof. Are we talking about ballistic concrete walls or something else?
Dmytry said:
too bad they don't have separate and hardened secondary backup generators.

Yes, on the hills in the back would make sense. There was apparently little thought on tsunami when they built their backups.
 

Attachments

  • aerial-2011-3-30-0-50-45_crop_arrow.jpg
    aerial-2011-3-30-0-50-45_crop_arrow.jpg
    37.6 KB · Views: 493
  • 5525887859_e1934af238_o_Crop.jpg
    5525887859_e1934af238_o_Crop.jpg
    63.8 KB · Views: 417
  • aerial-2011-3-30-1-11-12_crop.jpg
    aerial-2011-3-30-1-11-12_crop.jpg
    54.6 KB · Views: 447
Last edited:
  • #4,770
robinson said:
So has there been 150 times as much radioactivity released?

I would like astronuc to awnser that one, but it seems it has more to do with the way you present the numbers.
 
  • #4,771
Um... very silly question which just plopped into my mind:

There were hydrogen explosions in Units 1 to 3, hydrogen was generated after zircalloy reacted with hot steam. To prevent explosions inside the RPV and to lower the internal pressure, hydrogen was vented. This vented hydrogen exploded then inside the reactor buildings.

The thing I don't geet: Why ended the relieved hydrogen up in the reactor buildings? If I would've to construct an emergency venting system at a nuclear power plant, I would make sure that the vented gas lands outside the buildings and dilutes in the air.
So why did they vent into the building?

The only possible explanation coming to my mind is rupturing of the relieve valves due to high pressure...
 
  • #4,772
Clancy688
That's the multibillion dollar question.
 
  • #4,773
michael200 said:
Clancy688
That's the multibillion dollar question.

And I know answer: yes, all bwr reactors after TMI were upgraded with additional venting system but it need power, no one expect that at one time reactor can lost 3 power lines and backup generators... no power no venting
 
  • #4,774
clancy688 said:
Um... very silly question which just plopped into my mind:

There were hydrogen explosions in Units 1 to 3, hydrogen was generated after zircalloy reacted with hot steam. To prevent explosions inside the RPV and to lower the internal pressure, hydrogen was vented. This vented hydrogen exploded then inside the reactor buildings.

The thing I don't geet: Why ended the relieved hydrogen up in the reactor buildings? If I would've to construct an emergency venting system at a nuclear power plant, I would make sure that the vented gas lands outside the buildings and dilutes in the air.
So why did they vent into the building?

The only possible explanation coming to my mind is rupturing of the relieve valves due to high pressure...
Last I heard they had an electrical operated shut off valve that failed shut. It needed electricity to open, and there was no electricity. Nobody has explained why that valve was in the system when the worst case scenario would have it that the reactor plant lost electricity. That, of course would result in overheating of the core and the necessary venting. Unfortunately if the valve is shut because of a loss of electricity, YOU ARE ROYALLY SCREWED.
 
  • #4,775
clancy688 said:
Um... very silly question which just plopped into my mind:

There were hydrogen explosions in Units 1 to 3, hydrogen was generated after zircalloy reacted with hot steam. To prevent explosions inside the RPV and to lower the internal pressure, hydrogen was vented. This vented hydrogen exploded then inside the reactor buildings.

The thing I don't get: Why ended the relieved hydrogen up in the reactor buildings? If I would've to construct an emergency venting system at a nuclear power plant, I would make sure that the vented gas lands outside the buildings and dilutes in the air.
So why did they vent into the building?

The only possible explanation coming to my mind is rupturing of the relieve valves due to high pressure...

This has been a point of discussion elsewhere, and perhaps here as well. The consensus in other discussions was that there should not be a design path to vent into the building and what occurred was not intended or expected. Failure of valves, structure, or perhaps the failure of seals due to over-pressure are possibilities for allowing H2 to vent inside the building.
 
  • #4,776
clancy688 said:
Um... very silly question which just plopped into my mind:

There were hydrogen explosions in Units 1 to 3, hydrogen was generated after zircalloy reacted with hot steam. To prevent explosions inside the RPV and to lower the internal pressure, hydrogen was vented. This vented hydrogen exploded then inside the reactor buildings.

The thing I don't geet: Why ended the relieved hydrogen up in the reactor buildings? If I would've to construct an emergency venting system at a nuclear power plant, I would make sure that the vented gas lands outside the buildings and dilutes in the air.
So why did they vent into the building?

The only possible explanation coming to my mind is rupturing of the relieve valves due to high pressure...

It has been reported that the plants had installed hardened wetwell vent systems to be used to vent the containment from the suppression pool airspace to the offgas stack outside the building. In the case of uniit one the containment pressure was more than 2 times the design limit before they started to vent. Containment may already have been leaking or the overpressure could have caused leaks in the vent piping inside the building. About 1 hour after completing the venting unit 1 exploded. The system was not designed to vent into the building, but something must have leaked.
 
  • #4,777
clancy688 said:
Um... very silly question which just plopped into my mind:

There were hydrogen explosions in Units 1 to 3, hydrogen was generated after zircalloy reacted with hot steam. To prevent explosions inside the RPV and to lower the internal pressure, hydrogen was vented. This vented hydrogen exploded then inside the reactor buildings.

The thing I don't geet: Why ended the relieved hydrogen up in the reactor buildings? If I would've to construct an emergency venting system at a nuclear power plant, I would make sure that the vented gas lands outside the buildings and dilutes in the air.
So why did they vent into the building?

The only possible explanation coming to my mind is rupturing of the relieve valves due to high pressure...

Page 117 and following deals with various venting related issues
http://www.galcit.caltech.edu/~jeshep/fukushima/ShepherdFukushima9April2011.pdf

even more interesting to read:
http://www.osti.gov/bridge/servlets/purl/6980202-feK1wp/6980202.pdf

"THE ROLE OF BWR SECONDARY CONTAINMENTS IN SEVERE ACCIDENT MITIGATION:
ISSUES AND INSIGH1S FROM RECENT ANALYSES"
 
Last edited by a moderator:
  • #4,778
This photo I believe was taken on the 11th or the 12th of March 2011:
[PLAIN]http://mw2.google.com/mw-panoramio/photos/medium/49439865.jpg

To state the obvious, this is before unit 4 blew up :-)

However, first question:
what, if not the existence of a hole in the east wall, to the south, low and below the service floor, could explain what we are seeing there?

Second question: The east wall appears to be divided into vertical sections, a broad one in the middle, somewhat narrower sections to the right and left of that, and again, to the right and left of those sections, two even narrower sections towards the ends of the wall. What produces this appearance?
 
Last edited by a moderator:
  • #4,779
|Fred said:
I would like astronuc to awnser that one, but it seems it has more to do with the way you present the numbers.

Most curious . Perhaps someone could offer a plausible explanation for the enormous discrepancies in the emissions figures?

I131 - NISA estimate total emissions to 12/4/2011 = 130,000 TBq
NSC = 150,000 TBq
CTBT network analysis estimate total emission to 15/3/2011 = 400,000 TBq

Likewise for

C137 - NISA = 6100 TBq to 12/4
NSC = 1200 TBq t0 12/4
CTBT = 33,000 TBq to 15/3

Also would I be correct in my assumption that whilst the Japanese statistics for TOTAL emissions would suggest combined airborne/seawater contamination the figures produced by analysis of CTBT data would be limited to airborne emissions?
 
  • #4,780
I'm just a CPA that has a strong interest in science and has been lurking here...but I do have a question. How did they vent the units without power? Was there a manual way to do it that was still operational?
 
  • #4,781
MiceAndMen said:
I would dispute that fig_un1_pools_and_walls.png shows the correct layout of the pools. There has been no confirmation that the smallest pool in the picture actually exists separately from the SFP in any of the reactor buildings.

Indeed. I found a blueprint of the service floor layout, supposedly of units #2--#5, in this page

http://fukushimafaq.wikispaces.com/3D+and+Autocad+Rendering+%26+Analysis

and a fisheye view of #4's service floor:

http://www.houseoffoust.com/fukushima/possibles.html
http://www.houseoffoust.com/fukushima/reactor4_insideplain.jpg

As others have observed, the layout of #2--#5 seems to be very different from that of #1. There is no separate pool for cask loading between the service pools and the elevator, and the N-S arrangement seems reversed, with SFP and elevator near the South wall. Presumably the the function of the cask-loading pool is performed by a small enclosure within the spent-fuel pool (square on the outside, round inside), at its NW corner.

Now if only I had the vertical cross-section blueprints of one of the 2--4 buildings
 
Last edited by a moderator:
  • #4,782
MadderDoc said:
This photo I believe was taken on the 11th or the 12th of March 2011:
[PLAIN]http://mw2.google.com/mw-panoramio/photos/medium/49439865.jpg

To state the obvious, this is before unit 4 blew up :-)

However, first question:
what, if not the existence of a hole in the east wall, to the south, low and below the service floor, could explain what we are seeing there?

Second question: The east wall appears to be divided into vertical sections, a broad one in the middle, somewhat narrower sections to the right and left of that, and again, to the right and left of those sections, two even narrower sections towards the ends of the wall. What produces this appearance?
2nd question: those lines were there before March 11th. See: [PLAIN]http://img.ibtimes.com/www/data/images/full/2011/03/15/74732-tokyo-electric-power-co-s-fukushima-daiichi-nuclear-plant-no-4-reactor.jpg

Don't know about 1st question.
 
Last edited by a moderator:
  • #4,783
MadderDoc said:
This photo I believe was taken on the 11th or the 12th of March 2011:
[PLAIN]http://mw2.google.com/mw-panoramio/photos/medium/49439865.jpg
what, if not the existence of a hole in the east wall, to the south, low and below the service floor, could explain what we are seeing there?

Indeed. Curiously the "hole" is not visible in the post-explosion photos; apparently it was covered by debris.

MadderDoc said:
Second question: The east wall appears to be divided into vertical sections, a broad one in the middle, somewhat narrower sections to the right and left of that, and again, to the right and left of those sections, two even narrower sections towards the ends of the wall. What produces this appearance?

Perhaps they are lightning rod conduits, or rainwater drainage pipes. According to the #1 blueprints, the roof is slanted by 30cm in the E-W direction (although in #1 the East is lower). They seem to follow the main concrete pillars of the building, but offset to one side or the other, rather than down the pillar's midline.
 
Last edited by a moderator:
  • #4,784
MadderDoc said:
This photo I believe was taken on the 11th or the 12th of March 2011:
[PLAIN]http://mw2.google.com/mw-panoramio/photos/medium/49439865.jpg

To state the obvious, this is before unit 4 blew up :-)

However, first question:
what, if not the existence of a hole in the east wall, to the south, low and below the service floor, could explain what we are seeing there?

Second question: The east wall appears to be divided into vertical sections, a broad one in the middle, somewhat narrower sections to the right and left of that, and again, to the right and left of those sections, two even narrower sections towards the ends of the wall. What produces this appearance?


can you give us the Source of the Foto (Original)
 
Last edited by a moderator:
  • #4,785
robinson said:
So has there been 150 times as much radioactivity released?
150 times as much as what?

According to the files in this thread - https://www.physicsforums.com/showthread.php?t=493058 - safety authorities are estimating that the release of Cs/I from Fukushima is about an order magnitude less than the release from Chernobyl. Chernobyl was one core, but Fukushima has three damaged cores, or four if one considers the off-loaded fuel from Unit 4.
 
  • #4,786
triumph61 said:
can you give us the Source of the Foto (Original)

My source: http://www.panoramio.com/photo/49439865

[PLAIN]http://mw2.google.com/mw-panoramio/photos/medium/49439865.jpg
 
Last edited by a moderator:
  • #4,787
elektrownik said:
And I know answer: yes, all bwr reactors after TMI were upgraded with additional venting system but it need power, no one expect that at one time reactor can lost 3 power lines and backup generators... no power no venting

At least at Unit 1 they manually operated the hardened vent valve. The worker who performed that task received a significant dose that was reported in TEPCO Press Releases. Since that was well after batteries would have been drained I assume they also vented units 2 and 3 manually.

The WSJ article posted by MSCHARISMA describes the fact that the venting was manual.
 
  • #4,788
Nice, that was probably the right question to ask - so many answers. :)

ascot317 said:
even more interesting to read:
http://www.osti.gov/bridge/servlets/purl/6980202-feK1wp/6980202.pdf

"THE ROLE OF BWR SECONDARY CONTAINMENTS IN SEVERE ACCIDENT MITIGATION:
ISSUES AND INSIGH1S FROM RECENT ANALYSES"

Indeed, very interesting:

Containment- Venting: Existing BWRs employ primary containuent venting systems
to provide the venting c apabi l i ty necessary for containment ine r t ing prior to
reactor s t a r t up and de - ine r t ing prior to personnel entry i n to the primary
containment. Most exi s t ing plant emergency operating procedures c a ll for
containment venning when containment pressure reaches or exceeds ths design
value (48 to €J psig or 331 to 414 kPa gauge) . 35-37 Failure of the vent system
ducting is l i k e ly under the se circumstances, since the systems were not
designed for such pressure d i f f e r e n t i a l s. Such ducting f a i l u r es would allow
the vented material to discharge directly into the reactor building, flooding
the building with steam and combustible gases, and e f f e c t I've ly eliminating
further access to the secondary containment. Backfitting of dedicated "hard"
vent systems (which employ high-pressure ducting throughout the ent i re system
but no f i l t e r s) has been suggested as one mechanism for improving vent
r e l i a b i l i t y. It should also be noted t h a t, exi s t ing containment venting
systems would not be functional during s t a t i on blackout sequences. Power
(d. c. or a . c. or di r e ct human manipulation) is required for vent valve
operation.

So the longer they waited, the more they increased the possibility of an explosion? Ouch...

But that's only Unit 1. As for Unit 2, the venting was apparently successfull - an explosion only occurred in the wetwell (torus). But what went wrong with Unit 3? Same failure as Unit 1? Does anybody know how high the core pressure was when they vented Unit 3?

Caniche said:
Also would I be correct in my assumption that whilst the Japanese statistics for TOTAL emissions would suggest combined airborne/seawater contamination the figures produced by analysis of CTBT data would be limited to airborne emissions?

Nope, it's not total emissions, the japanese statistics are airborne as well:

http://www.nisa.meti.go.jp/english/files/en20110412-4.pdf

[...]Nuclear and Industrial Safety Agency
(NISA) estimated the total amount of discharged radioactive materials
from the reactors of Fukushima Dai-ichi NPS to the air[...]

Outflow to the sea:

http://www.tepco.co.jp/en/press/corp-com/release/betu11_e/images/110421e2.pdf
 
Last edited by a moderator:
  • #4,789
clancy688 said:
Um... very silly question which just plopped into my mind:

There were hydrogen explosions in Units 1 to 3, hydrogen was generated after zircalloy reacted with hot steam. To prevent explosions inside the RPV and to lower the internal pressure, hydrogen was vented. This vented hydrogen exploded then inside the reactor buildings.

The thing I don't geet: Why ended the relieved hydrogen up in the reactor buildings? If I would've to construct an emergency venting system at a nuclear power plant, I would make sure that the vented gas lands outside the buildings and dilutes in the air.
So why did they vent into the building?

The only possible explanation coming to my mind is rupturing of the relieve valves due to high pressure...
They vented very late.
 
  • #4,790
MadderDoc said:
My source: http://www.panoramio.com/photo/49439865

[PLAIN]http://mw2.google.com/mw-panoramio/photos/medium/49439865.jpg[/QUOTE]

Thank you.
Sorry.. it´s look like a fake.
 
Last edited by a moderator:
  • #4,791
Jorge Stolfi said:
Indeed. I found a blueprint of the service floor layout, supposedly of units #2--#5, in this page
and a fisheye view of #4's service floor:
wiki is filled with unreliable data..
I posted the fish eye picture here with source it is not from #4 but from #5 (the one on the extreme north of the plant)
And the service floor BP linked on the webpage was posted here originaly few dozen pages down and is not from Fukushima.
 
  • #4,792
Jorge Stolfi said:
Indeed. Curiously the "hole" is not visible in the post-explosion photos; apparently it was covered by debris.

Actually the hole (if that is what we see on this photo from March 12th) is also present in the post-explosion photos, it just appears to have grown larger, to now include the whole of that particular wall panel (the panel at row 3,column 1 of the east wall). See attachments.

Perhaps they are lightning rod conduits, or rainwater drainage pipes. According to the #1 blueprints, the roof is slanted by 30cm in the E-W direction (although in #1 the East is lower). They seem to follow the main concrete pillars of the building, but offset to one side or the other, rather than down the pillar's midline.

By looking at the paint pattern of the still hanging on wall panels (row 1, column 3 and 4), I've been able to determine that the apparent vertical ridges of the center section closely follows pillar 3 and 5 of the wall structure, whereas the outer ridges towards the ends divide the panels at the ends of the wall. The apparent hole appears to include the bottom half of the involved wall panel, from the south end and in, as far north as up to the ridge dividing the panel.

I have looked through the early satelite photos, they all view the east face of the building in a rather sharp angle, however there are none of those photos I would say negate the presence of a hole, if anything they support the notion, that 'there is something there'. See attachment.
 

Attachments

  • vlcsnap-2011-04-24-20h35m15s221.jpg
    vlcsnap-2011-04-24-20h35m15s221.jpg
    38.3 KB · Views: 307
  • 20110312-13.jpg
    20110312-13.jpg
    36.2 KB · Views: 429
  • 20110324_east_4-3.jpg
    20110324_east_4-3.jpg
    60.9 KB · Views: 493
  • #4,793
Astronuc said:
150 times as much as what?
.
as much as they posted before , before "converting Bequerel from cesium to Bequerel from iodine equivalent"
 
  • #4,794
NUCENG said:
At least at Unit 1 they manually operated the hardened vent valve. The worker who performed that task received a significant dose that was reported in TEPCO Press Releases. Since that was well after batteries would have been drained I assume they also vented units 2 and 3 manually.

The WSJ article posted by MSCHARISMA describes the fact that the venting was manual.

Yes but you can't vent only manualy with holes, maybe they open vent valve but this wouldn't remove much hydrogene, there is another system for that but i t need power to work, you can see it on some pictures of bwr reactors for example in usa, but it is like venting system in normal buildings, it need power to pump off hydrogene from reactor hall...
 
  • #4,795
Re the image at http://www.panoramio.com/photo/49439865

triumph61 said:
Thank you.
Sorry.. it´s look like a fake.

Which indications do you see, that it is a fake?
 
Last edited by a moderator:
  • #4,796
|Fred said:
as much as they posted before , before "converting Bequerel from cesium to Bequerel from iodine equivalent"

Yeah... if I understand correctly, the previous numbers were 0.69 Tbq/h I131 and 0.14 TBq/h C137 (forgive me for mistakes, I'm reciting those numbers from my memory). They just added those two numbers and got 0.83 TBq escaping activity per hour.
That's not wrong... that's the activity you can measure. But if you want to tell people how bad that activity is (for example 1000 TBq Krypton-85 per hour would pose no real threat), you convert it into I131 equivalence.

They didn't do that with those numbers and have done that afterwards - but the number they got the second time wasn't per hour, but per day.

Before conversion:

0.69 TBq/h + 0.14 TBq/h = 0.83 TBq/h
0.83 TBq/h * 24h = 19.92 TBq/d

After conversion:

0.69 TBq/h * 1 + 0.14 TBq/h * 40 = 6.29 TBq/h
6.29 TBq/h * 24h = 150.96 TBq/d

The released activity didn't change at all. They only changed the math. It shows you now, that those 20 TBq of I131 and C137 which are escaping per day are as dangerous as 150 TBq I131.

If the number is stable then that's a radioactivity release on Three Mile Island Scale every four days. And a radioactivity release on Chernobyl scale every 110 years.
 
Last edited:
  • #4,797
MadderDoc said:
Re the image at http://www.panoramio.com/photo/49439865



Which indications do you see, that it is a fake?
The Foto is too small 40kb to see if it is real. It is made before B3 Explosion (no debrid on the Roof) No one says that soneone has made a hole in the Building or an Explosion before B3.
sorry in English ist is difficult to explain.
 
Last edited by a moderator:
  • #4,798
NUCENG said:
At least at Unit 1 they manually operated the hardened vent valve. The worker who performed that task received a significant dose that was reported in TEPCO Press Releases. Since that was well after batteries would have been drained I assume they also vented units 2 and 3 manually.
I am thinking about the security concept. Did I get this right:

- venting of the RPV is possible from a remote location or happens automatically even without power.

- venting of the containment requires electrical power. In case of a station blackout someone has to enter the recator building an manually open a valve?

So the security concept is based on the fact that you find somebody stupid enough to do that? Somebody who knows that he will receive a high dose of radiation and may be torn to pieces by a hydrogen explosion? Guess what I would have done in such a situation...
 
  • #4,799
triumph61 said:
No one says that soneone has made a hole in the Building
I guess the building must have a door - even a pretty big door to get equipment in and out. But that 'hole' does seem a long way above ground level and there's no sign of it in the earlier picture:

[PLAIN]http://img.ibtimes.com/www/data/images/full/2011/03/15/74732-tokyo-electric-power-co-s-fukushima-daiichi-nuclear-plant-no-4-reactor.jpg
 
Last edited by a moderator:
  • #4,800
biffvernon said:
I guess the building must have a door - even a pretty big door to get equipment in and out.
it is on the other side
 