Japan Earthquake: Nuclear Plants at Fukushima Daiichi

AI Thread Summary
The Fukushima Daiichi nuclear plant is facing significant challenges following the earthquake, with reports indicating that reactor pressure has reached dangerous levels, potentially 2.1 times capacity. TEPCO has lost control of pressure at a second unit, raising concerns about safety and management accountability. The reactor is currently off but continues to produce decay heat, necessitating cooling to prevent a meltdown. There are conflicting reports about an explosion, with indications that it may have originated from a buildup of hydrogen around the containment vessel. The situation remains serious, and TEPCO plans to flood the containment vessel with seawater as a cooling measure.
  • #4,801
MadderDoc said:
On the Tepco hand out page at:
http://www.tepco.co.jp/en/news/110311/index-e.html
there are separate photos of the control rooms of unit 3, and 4, and also the photo you are discussing -- according to Tepco the 'Control room for Unit 3 and 4'.

The three photos can be compared, and it can be verified, that the control panel design in the right part of the photo of the 'control room for unit 3 and 4' perfectly matches the control panel design found shown in the individual photo of the control room of unit 3, and -- despite the darkness of it -- that the control panel design in the left side of the photo appears to match the one shown for the control room of unit 4.

Enhancing the contrast of the "unit 3 and 4" picture reveals details on the left, dark side of the picture. It does appear to be part of a control room. I'll accept that the dark part of the room on the left is for Unit 4.

I don't see that the left or the right of the "unit 3 and 4" picture matches up with anything in the individual control room pics for 3 and 4, however. For instance, in the half-dark "unit 3 and 4" picture, there's a diagram of the drywell and torus at the far right. I don't see that in the individual Unit 3 picture anywhere. Similarly, on the far left there are round dials to the left of the whiteboard. I don't see those anywhere in the Unit 4 by-itself picture.

Are we looking at the same pictures? I could be wrong. It wouldn't be the first time in this thread where people claim pictures show things that I don't see.
 
Last edited by a moderator:
Engineering news on Phys.org
  • #4,802
Indeed it is. Just exploring the possibility that the 'hole' is there on purpose. I think it's pretty unlikely. A shame the picture with the 'hole' isn't at a higher resolution. It does seem to be corroborated with the satellite pic. It's at a different angle but even lower resolution.
 
  • #4,803
MadderDoc said:
This photo I believe was taken on the 11th or the 12th of March 2011:
http://mw2.google.com/mw-panoramio/photos/medium/49439865.jpg

To state the obvious, this is before unit 4 blew up :-)

However, first question:
what, if not the existence of a hole in the east wall, to the south, low and below the service floor, could explain what we are seeing there?
Is not this a shadow from the top of one of the venting towers?
 
Last edited by a moderator:
  • #4,804
ascot317 said:
Page 117 and following deals with various venting related issues
http://www.galcit.caltech.edu/~jeshep/fukushima/ShepherdFukushima9April2011.pdf

even more interesting to read:
http://www.osti.gov/bridge/servlets/purl/6980202-feK1wp/6980202.pdf

"THE ROLE OF BWR SECONDARY CONTAINMENTS IN SEVERE ACCIDENT MITIGATION:
ISSUES AND INSIGH1S FROM RECENT ANALYSES"


The second paper linked is one I saw early on. On pp 4-5:
The secondary containments of domestic BWRs were designed and/or constructed
by ten different architect/engineering firms (Table 1) , and vary considerably in basic design characteristics such as volume, number of floors, the arrangement of stairways and elevator shafts, etc.

That was and is the basis for my contention that it's not a good idea to speculate too much on the exact locations of reactor building layouts and positioning of components inside. We know now pretty much where the SFPs are in units 3 and 4, but to my mind it was grossly premature to take the ubiquitous color GE artist's concept sketch of a Mark I reactor building and extrapolate too much information from it, and subsequently treat that speculation as fact.

We still have not seen any diagrams of the refueling floors at Fukushima Dai-ichi. In fact, except for a couple of elevation drawings we haven't seen much of anything regarding the internal arrangement of any building at the site. All we have are guesses; admittedly educated guesses, and on this forum they can be quite good, but there is a lot we don't know.
 
Last edited by a moderator:
  • #4,805
elektrownik said:
Yes but you can't vent only manualy with holes, maybe they open vent valve but this wouldn't remove much hydrogene, there is another system for that but i t need power to work, you can see it on some pictures of bwr reactors for example in usa, but it is like venting system in normal buildings, it need power to pump off hydrogene from reactor hall...

I think you are confusing the hardened vent and vent through the standby gas treatment system SBGT requires power to run, but is a low pressure system and shouldn't have been used on a pressurized containment. The hardened ven simply opens a path to the stack and vents the high pressure to the stack. No power needed it works on differential pressure.
 
  • #4,806
NUCENG said:
I think you are confusing the hardened vent and vent through the standby gas treatment system SBGT requires power to run, but is a low pressure system and shouldn't have been used on a pressurized containment. The hardened ven simply opens a path to the stack and vents the high pressure to the stack. No power needed it works on differential pressure.

Yes but it would only decrease pressure and would not remove hydrogene
 
  • #4,807
triumph61 said:
The Foto is too small 40kb to see if it is real. It is made before B3 Explosion (no debrid on the Roof) No one says that soneone has made a hole in the Building or an Explosion before B3.
sorry in English ist is difficult to explain.

You appear to be close to saying that because we think there wasn't a hole in B4 before the explosion in B3, then a photo which appears to show a hole in B4 before that must be a fake.

Consider, though, that independently taken satellite photos from Digitalglobe from the 12th and 13th of March show a quite similar defect of the wall, at the very same spot:

20110312-13.jpg


If there indeed was a hole in the east wall of unit4, before the explosions, as these photos appear to be showing, there is no need to hypothesise about an extra explosion to cause it, nor that someone made the hole deliberately. We need no further assumptions because, we know that the building had just before been exposed to an extraordinarily strong earthquake.
 
  • #4,808
MadderDoc said:
You appear to be close to saying that because we think there wasn't a hole in B4 before the explosion in B3, then a photo which appears to show a hole in B4 before that must be a fake.

Consider, though, that independently taken satellite photos from Digitalglobe from the 12th and 13th of March show a quite similar defect of the wall, at the very same spot:

20110312-13.jpg


If there indeed was a hole in the east wall of unit4, before the explosions, as these photos appear to be showing, there is no need to hypothesise about an extra explosion to cause it, nor that someone made the hole deliberately. We need no further assumptions because, we know that the building had just before been exposed to an extraordinarily strong earthquake.
They may have been trying to vent near the SFP. They vented Unit 2 in a similar manner, but they really needed the vent near the roof.
 
  • #4,809
Surely the opening is a door.
There is a flight of steps leading up to that level n the south side and there are what may be 4 heat exchangers on the roof between the reactor and turbine buildings. So it is a routinely accessed site.
It would be expected that the support structure of the reactor building, with a large elevator, would be used to help move large items to the roof of the turbine building, as we have here. That requires a big door.
 
  • #4,810
PietKuip said:
Is not this a shadow from the top of one of the venting towers?

That's what I thought too until it occurred to me by looking at the light and shadows that this photo must have been taken before noon. So the shadows of the exhaust towers are all on the west side of the buildings.
 
  • #4,811
clancy688 said:
Yeah... if I understand correctly, the previous numbers were 0.69 Tbq/h I131 and 0.14 TBq/h C137 (forgive me for mistakes, I'm reciting those numbers from my memory). They just added those two numbers and got 0.83 TBq escaping activity per hour.
That's not wrong... that's the activity you can measure. But if you want to tell people how bad that activity is (for example 1000 TBq Krypton-85 per hour would pose no real threat), you convert it into I131 equivalence.

They didn't do that with those numbers and have done that afterwards - but the number they got the second time wasn't per hour, but per day.

Before conversion:

0.69 TBq/h + 0.14 TBq/h = 0.83 TBq/h
0.83 TBq/h * 24h = 19.92 TBq/d

After conversion:

0.69 TBq/h * 1 + 0.14 TBq/h * 40 = 6.29 TBq/h
6.29 TBq/h * 24h = 150.96 TBq/d

The released activity didn't change at all. They only changed the math. It shows you now, that those 20 TBq of I131 and C137 which are escaping per day are as dangerous as 150 TBq I131.

If the number is stable then that's a radioactivity release on Three Mile Island Scale every four days. And a radioactivity release on Chernobyl scale every 110 years.

Now I'm confused . Is that 20TBq daily discharge a combined figure for I131/c137 ?
Anyhow the independent nuclear test ban monitors put the average daily discharge figures for c137 at 5000TBq's per day. So ignoring liquid discharge and overlooking the hygroscopic tendencies of Ce 137 ,after 50 days that puts the total discharge of radioactive Ce137 at roughly 250,000 TBq as compared with the stated fallout of 85,000 TBq from Chernobyl.
I'm probably wrong but from official figures it does appear that we waved goodbye to the chernobyl monster about four weeks ago Tuesday and just keep on growing :-(
 
  • #4,812
Jorge Stolfi said:
Indeed. I found a blueprint of the service floor layout, supposedly of units #2--#5, in this page

http://fukushimafaq.wikispaces.com/3D+and+Autocad+Rendering+%26+Analysis

I have seen that page. He got that floorplan layout from here after I originally posted it here on 15 April :smile:. It's from the Oyster Creek blueprint set, and is cropped from the original exactly the way I cropped it before posting it. There is no doubt in my mind he got that diagram from here.
FUKUSHIMAFAQ said:
Finally for now an image was posted this evening of a layout of the service floor showing the SFP etc, this I believe is the missing link which should allow me to finish the 3D model for some more interesting analysis, this also supports my view the reactor is off-centre.

The OC floor layout is probably close to the Fukushima Dai-ichi ones, but they are not identical. I'm glad he found it useful :smile:

As for buildings 2-4, I think I found a vertical elevation cross-section for Unit 3 in a Japanese-language PDF which I discovered a few days ago. I'll look for the link for you.
 
Last edited by a moderator:
  • #4,813
ascot317 said:
Page 117 and following deals with various venting related issues
http://www.galcit.caltech.edu/~jeshep/fukushima/ShepherdFukushima9April2011.pdf

even more interesting to read:
http://www.osti.gov/bridge/servlets/purl/6980202-feK1wp/6980202.pdf

"THE ROLE OF BWR SECONDARY CONTAINMENTS IN SEVERE ACCIDENT MITIGATION:
ISSUES AND INSIGH1S FROM RECENT ANALYSES"

The CalTech document is a great collection of pictures and data relating to the Fukushima accident. I read it 10 days ago but glad to see it posted here again for all to consider.

I think it will be determined at some time in the future's investigation that like most of the bad things that happened resulted because of the total station blackout - a beyond design basis event. IOW, they were screwed when the tsunami took out the generators.

The venting system relies on fans and filters to remove particles before discharge up the stack. Apparently, little thought was given to a natural draft type back-up venting plan. Top goal was preventing radioactive release. Being so focused on that primary goal, they designed systems that INCREASED such releases in a severe accident!


What I have not seen discussed (and in 300 pages I may well have missed it!) is service water. Was service water (sea water for cooling) available after the EQ? Would it have been available after the tsunami IF electrical power had remained available? Once the suppression pools reached 100 degrees C even the steam driven pumps would have become useless. Just how long does it take to heat the SC to 100C without service water cooling available? Did high SC temperature fail the steam driven pumps or did loss of battery power cause that?
 
Last edited by a moderator:
  • #4,814
Caniche said:
Now I'm confused . Is that 20TBq daily discharge a combined figure for I131/c137 ?

Bingo. http://www-pub.iaea.org/MTCD/publications/PDF/INES-2009_web.pdf" page 15 for further informations.

Anyhow the independent nuclear test ban monitors put the average daily discharge figures for c137 at 5000TBq's per day. So ignoring liquid discharge and overlooking the hygroscopic tendencies of Ce 137 ,after 50 days that puts the total discharge of radioactive Ce137 at roughly 250,000 TBq as compared with the stated fallout of 85,000 TBq from Chernobyl.

Source please? The austrian meteorological agency ZAMG http://www.zamg.ac.at/aktuell/index.php?seite=2&artikel=ZAMG_2011-04-02GMT09:28" the C137 releases from March 12th - 19th at 1000 - 70.000 TBq. Initial estimates were afaik up to 5000 TBq C137 per day. And they are using the nuclear test ban network (CTBTO).

But that doesn't count for ALL days. Watch http://fukushima.grs.de/sites/default/files/Messwerte_ODL_Fukushima_Daiichi_110421-1230_Gesamt.pdf"chart. You can see that there were big radioactivity releases between March 12th and 19th. And afterwards practically nothing.
The reactors were releasing up to 10.000 TBq per hour at one time, but only for a short period. Now it's at the 20 TBq per day, or 150 TBq converted.
 
Last edited by a moderator:
  • #4,815
etudiant said:
Surely the opening is a door.
There is a flight of steps leading up to that level n the south side and there are what may be 4 heat exchangers on the roof between the reactor and turbine buildings. So it is a routinely accessed site.
It would be expected that the support structure of the reactor building, with a large elevator, would be used to help move large items to the roof of the turbine building, as we have here. That requires a big door.

Consider the position of the apparent hole, and where this assumed door would lead into below the service floor. What use would a big door be of there? For lifting large items to the roof floor, it should be above the service floor.

But indeed the building appears to have had such a opening, however at the wall panel at row 2, column 4.

20110320_east.jpg


Note the distinctly different way this panel has been blown off, with remaining sharp edges and paint deco along those edges. We see the same phenomenon at unit 3, the exact same position, row 2, column 4. The opening that has been made in the east wall of unit 2 is also in this position.
 
  • #4,816
triumph61 said:
Here is a Picture of the Map

Here are some easier to read versions of the map, from the morning papers:

From Asahi Shimbun:
[URL]http://www.asahi.com/special/10005/images/TKY201104240165.jpg[/URL]

From Yomiuri Shimbun:
[PLAIN]http://www.yomiuri.co.jp/photo/20110424-585450-1-L.jpg

The numbers are all in mSv/h.

There is a notable accumulation of hot material around the NW corner of the Unit 1 reactor building. Is Unit 1's SFP on the north side of the building?

Unit 4 does not appear to have scattered much radioactive material onto the ground.

Unit 3's stuff went all over the place.
 
Last edited by a moderator:
  • #4,817
Interesting, the 300 and 900 mSv/h chunks were found where the big debris from the Unit 3 explosion must have gone down.
 
  • #4,818
MadderDoc said:
This photo I believe was taken on the 11th or the 12th of March 2011:
http://mw2.google.com/mw-panoramio/photos/medium/49439865.jpg

To state the obvious, this is before unit 4 blew up :-)

However, first question:
what, if not the existence of a hole in the east wall, to the south, low and below the service floor, could explain what we are seeing there?

Hard to tell what the sun angle is, but it looks to me like the shadow of the top of the south vent stack.
 
Last edited by a moderator:
  • #4,819
Ok, seriously, why convert it to I-131 equivalent? It is so meaningless. The Cs-137 is a long term hazard, accumulates in muscle tissue. The I-131 is a short term hazard, it accumulates in thyroid, it is preventable with iodine tablets. I will refrain from telling what I think about this conversion of everything to "I-131 equivalent".
 
  • #4,820
MadderDoc said:
That's what I thought too until it occurred to me by looking at the light and shadows that this photo must have been taken before noon. So the shadows of the exhaust towers are all on the west side of the buildings.

Unit 4 was down for service. There is a flight of stairs, yes, but it accesses the roof adjacent to the open panel. More likely it is a door or a removable service panel to allow equipment to be moved onto or off of the roof. Low resolution, but at magnification, it does not look to be damage due to an explosion or fire. There is no corresponding debris on the adjacent roof either.
 
  • #4,821
elektrownik said:
Yes but it would only decrease pressure and would not remove hydrogene

The theory of operation of the hardened wetwell vent starts with a containment inerted with nitrogen. The accident releases steam and hydrogen into the containment via the SRVs to the suppression pool where the steam is condensed. As the suppression pool heats up and containment pressure rises torus to drywell vacuum breakers will equalize pressure venting some of the hydrogen back into the drywell. The venting via the hardened vent is done from the airspace at the top of the airspace in the suppression chamber/torus. The venting will remove some of the hydrogen along with stteam and other non-condensible gases. As pressure in the torus drops the differental pressure in the drywell will displace water in the downcomers allowing noncondensiblesm hydrogen and steam from the drywell to vent to the torus and out the vent as well. You are right that it does not remove all of the hydrogen. It is only designed to reduce pressure and prevent containment failure from over-pressurization.
 
  • #4,822
etudiant said:
Surely the opening is a door.
There is a flight of steps leading up to that level n the south side and there are what may be 4 heat exchangers on the roof between the reactor and turbine buildings. So it is a routinely accessed site.
It would be expected that the support structure of the reactor building, with a large elevator, would be used to help move large items to the roof of the turbine building, as we have here. That requires a big door.

BWRs have doors at the other side of the building in the area where casks are loaded or onladed onto transporters. I have never seen a door in that location at a BWR.
 
  • #4,823
NUCENG said:
The theory of operation of the hardened wetwell vent starts with a containment inerted with nitrogen. The accident releases steam and hydrogen into the containment via the SRVs to the suppression pool where the steam is condensed. As the suppression pool heats up and containment pressure rises torus to drywell vacuum breakers will equalize pressure venting some of the hydrogen back into the drywell. The venting via the hardened vent is done from the airspace at the top of the airspace in the suppression chamber/torus. The venting will remove some of the hydrogen along with stteam and other non-condensible gases. As pressure in the torus drops the differental pressure in the drywell will displace water in the downcomers allowing noncondensiblesm hydrogen and steam from the drywell to vent to the torus and out the vent as well. You are right that it does not remove all of the hydrogen. It is only designed to reduce pressure and prevent containment failure from over-pressurization.

Hydrogen/air mixtures are explosive over a very wide range, from 5%-40% if memory serves. So having the hydrogen diluted but more widely spread may actually increase the hazard.
Was this risk given serious study or is it just another unexpected issue that cropped up as operations became more frequent?
 
  • #4,824
MiceAndMen said:
<..>
I don't see that the left or the right of the "unit 3 and 4" picture matches up with anything in the individual control room pics for 3 and 4, however. For instance, in the half-dark "unit 3 and 4" picture, there's a diagram of the drywell and torus at the far right. I don't see that in the individual Unit 3 picture anywhere. Similarly, on the far left there are round dials to the left of the whiteboard. I don't see those anywhere in the Unit 4 by-itself picture.
<..>

That is true, you don't see that. My take on it is that the two 'by itself' photos of unit 3 and 4 are pointed in such disparate directions in the room, that they do not overlap with any part of the combination photo taken at the boundary between the two. However, consider the designs of the control panels, in particular the hand railings along them, and the cupboards below (see attachments). This is of course not proof, but it is a strong indication that we are looking at two parts of the same unit 3 control board, and two parts of the same unit 4 controlboard
 

Attachments

  • Controlroom3.jpg
    Controlroom3.jpg
    41.4 KB · Views: 434
  • Controlroom4.jpg
    Controlroom4.jpg
    49 KB · Views: 423
  • #4,825
etudiant said:
Hydrogen/air mixtures are explosive over a very wide range, from 5%-40% if memory serves. So having the hydrogen diluted but more widely spread may actually increase the hazard.
Was this risk given serious study or is it just another unexpected issue that cropped up as operations became more frequent?

As long as the containment is pressurized above atmosphere the amount of oxygen inside containment should remain low. The elevated release point would allow any hydrogen deflagration or detonation to occur away from the vital equipment. Of course if they delayed venting until it caused leaks in the containment or in the vent piping, then you get hydrogen where you don't want it. Good questions!
 
  • #4,826
MiceAndMen said:
Hard to tell what the sun angle is, but it looks to me like the shadow of the top of the south vent stack.

It is clear from the shadows that this photo has been taken well before noon, (the sun is towards the seaside). The shadow of the south vent stack does not hit the south east corner of the unit 4 building until after noon.
 
  • #4,827
clancy688 said:
Bingo. http://www-pub.iaea.org/MTCD/publications/PDF/INES-2009_web.pdf" page 15 for further informations.



Source please? The austrian meteorological agency ZAMG http://www.zamg.ac.at/aktuell/index.php?seite=2&artikel=ZAMG_2011-04-02GMT09:28" the C137 releases from March 12th - 19th at 1000 - 70.000 TBq. Initial estimates were afaik up to 5000 TBq C137 per day. And they are using the nuclear test ban network (CTBTO).

But that doesn't count for ALL days. Watch http://fukushima.grs.de/sites/default/files/Messwerte_ODL_Fukushima_Daiichi_110421-1230_Gesamt.pdf"chart. You can see that there were big radioactivity releases between March 12th and 19th. And afterwards practically nothing.
The reactors were releasing up to 10.000 TBq per hour at one time, but only for a short period. Now it's at the 20 TBq per day, or 150 TBq converted.

Yes I see the chart ,thank you ,most reassuring. Still confused though because even if the data was accurate only up to the date of issue ,12/4/2011 that still gives 30 x5,000TBqs of Ce137 average daily emission or 2 x chernobyl in one month as opposed to i x every 100 years.
Any idea what happened after the 19th to reduce discharge to ripe banana levels? Did the containment barriers heal up ? Did the damaged fuel rods (up to 70%) get better, or did the water bombs water cannon and 'concrete pumps' get enough liquid on to prevent most airborne discharge?
 
Last edited by a moderator:
  • #4,828
Most Curious said:
What I have not seen discussed (and in 300 pages I may well have missed it!) is service water. Was service water (sea water for cooling) available after the EQ? Would it have been available after the tsunami IF electrical power had remained available? Once the suppression pools reached 100 degrees C even the steam driven pumps would have become useless. Just how long does it take to heat the SC to 100C without service water cooling available? Did high SC temperature fail the steam driven pumps or did loss of battery power cause that?

I too have wondered about the service water pumps, and did they survive the EQ & tsunami. I'm pretty sure I asked about that somewhere way up the thread, but I never got an answer. Looking at the photos of the intake area, the damage looked pretty severe to me, and that's where one usually finds the service water pumps. I'm not sure what they're called in a BWR, so I don't know how to ask more directly.

I had my doubts that the steam-driven cooling would fail on loss of DC; seems like the valves (steam to the turbine & water from the pump to the reactor) would either fail-as-is on loss of power, or have handwheels for local manual operation. Along with procedures, communications, emergency lighting, and accessabilty to take such action. That's what I'm used to seeing in PWR designs.
 
  • #4,829
TCups said:
<..> it does not look to be damage due to an explosion or fire. There is no corresponding debris on the adjacent roof either.

True it doesn't look like the result of an explosion or a fire, but we cannot deny that it could be the result of the shaking of the building and its internals during the earthquake. We have indications that the FHM4 may have collided with the east wall (the bent hockey stick), and we cannot say whether that damage happened during the unit 4 explosion, or before it.

Debris from a putative before-explosion hole would be expected to be covered up by the debris of the explosion.
 
Last edited:
  • #4,830
Caniche said:
Yes I see the chart ,thank you ,most reassuring. Still confused though because even if the data was accurate only up to the date of issue ,12/4/2011 that still gives 30 x5,000TBqs of Ce137 average daily emission or 2 x chernobyl in one month as opposed to i x every 100 years.
Any idea what happened after the 19th to reduce discharge to ripe banana levels? Did the containment barriers heal up ? Did the damaged fuel rods (up to 70%) get better, or did the water bombs water cannon and 'concrete pumps' get enough liquid on to prevent most airborne discharge?

You raise the same question that has bothered me for some time.
ZAMG was the only source that provided overall emission estimates from an early period. They initially estimated about 1/10th Chernobyl output daily, measured in bequerels and claimed that the levels found after several days by the CTBT network were within a factor of two of the measures generated by their model using those assumptions.
Since then, they have added that their estimates represent an upper bound and might be high by as much as a factor of 1000, but the evacuation zone in Japan is growing and in some dimensions now rivals that at Chernobyl, so there is concern.
Perhaps ZAMGs more positive recent estimates will prove correct.
However, it would be very useful to have a credible and comprehensive assessment of the scale of the airborne emissions.
Of course, the summer winds and rains will provide ground truth on the scale of these emissions by their contamination of central Japan. It would be useful though to have some specific idea of the damage to be expected.
 
  • #4,831
MadderDoc said:
It is clear from the shadows that this photo has been taken well before noon, (the sun is towards the seaside). The shadow of the south vent stack does not hit the south east corner of the unit 4 building until after noon.

Agree it was taken before noon, but the stack is SE of the #4 reactor building (the center pipes are anyway) so I would expect a shadow of the top to hit that wall in the morning. This picture shows a different kind of hole in the exact same spot:
http://www.flickr.com/photos/digitalglobe-imagery/5522088312/sizes/l/in/photostream/
It looks like a hole shaped for Mickey Mouse or perhaps the Easter Bunny. It's hazy and hard to tell what it is exactly, but it does look like a hole and it does not look rectangular. I think it, too, is a shadow from the vent stack.

Then there are the two pictures at the bottom of this page:
http://cryptome.org/eyeball/daiichi-npp2/daiichi-photos2.htm

They show that a shadow from the stack could, under the right circumstances, be projected onto the east side of the building. Curiously, and in favor of your hypothesis however, the last picture on that page does show a green patch of some sort right near where this "hole" is located! Very interesting.

This is another case where a lack of precise drawings and site layout/dimensions hamper our armchair analyses. IF we knew where the south vent stack was in relation to bldg #4 and IF we knew exactly how high the stack is, it would be trivial to set up a 3D simulation of the sun traversing the sky on the dates in question and determine, once and for all, whether the vent stack could cast a shadow on the building of the right shape and size in that spot. But, alas, that is data we do not have.
 
Last edited by a moderator:
  • #4,832
The two attached photos of unit 4 are frames from a video taken by a helicopter that overflew the facility on March 11th, shortly after the tsunami.

They show the same thing as the other photos I've posted on this matter: an apparent hole in the lower south end of the east wall, and this right after the earthquake. A visual effect of a cast shadow can here be entirely ruled out, the sunlight was simply too diffuse to cast any perceptible shadow at the time of these photos.
 

Attachments

  • 20110311_Screenshot-6.jpg
    20110311_Screenshot-6.jpg
    34.4 KB · Views: 359
  • 20110311_Screenshot-7.jpg
    20110311_Screenshot-7.jpg
    31.4 KB · Views: 409
  • #4,833
MiceAndMen said:
Agree it was taken before noon, but the stack is SE of the #4 reactor building (the center pipes are anyway) so I would expect a shadow of the top to hit that wall in the morning. This picture shows a different kind of hole in the exact same spot:
http://www.flickr.com/photos/digitalglobe-imagery/5522088312/sizes/l/in/photostream/
It looks like a hole shaped for Mickey Mouse or perhaps the Easter Bunny. It's hazy and hard to tell what it is exactly, but it does look like a hole and it does not look rectangular. I think it, too, is a shadow from the vent stack.

Then there are the two pictures at the bottom of this page:
http://cryptome.org/eyeball/daiichi-npp2/daiichi-photos2.htm

They show that a shadow from the stack could, under the right circumstances, be projected onto the east side of the building. Curiously, and in favor of your hypothesis however, the last picture on that page does show a green patch of some sort right near where this "hole" is located! Very interesting.

This is another case where a lack of precise drawings and site layout/dimensions hamper our armchair analyses. IF we knew where the south vent stack was in relation to bldg #4 and IF we knew exactly how high the stack is, it would be trivial to set up a 3D simulation of the sun traversing the sky on the dates in question and determine, once and for all, whether the vent stack could cast a shadow on the building of the right shape and size in that spot. But, alas, that is data we do not have.

Yes that could be fun :-), however not necessary at all. We have ample access to photos taken from satellites indicating how the shadow of the south vent tower travels across the building of unit 4. Furthermore we have photos of the putative hole, taken under diffuse daylight, completely mooting the question.

The green blob in the photo from cryptome.org is quite interesting, although the photo is rather earlier, from 2010 according to the caption -- but, can it really be a coincidence that it is in the same spot? What could that green blob be, since it does not appear to be a constant feature of the building? I shall have to think about that.

Re the mouse/bunny shape, it appears from photos that it could be produced by the holes upper edges not being teared off cleanly. Indeed from a satellite photo from the same period looking more directly from the south along the east side, it appears that some irregular piece of wall is protruding, above the putative hole. See the attachment.
 

Attachments

  • 20110312-13Digitalglobe.jpg
    20110312-13Digitalglobe.jpg
    55.2 KB · Views: 767
Last edited by a moderator:
  • #4,834
MadderDoc said:
The green blob in the photo from cryptome.org is quite interesting, although the photo is rather earlier, from 2010 according to the caption -- but, can it really be a coincidence that it is in the same spot? What could that green blob be, since it does not appear to be a constant feature of the building? I shall have to think about that.

The green blob is very interesting indeed. Cryptome says the picture was taken on 18 September 2010, which was before the shutdown for the core shroud replacement job. Maybe they did some work in that part of the building in preparation for that task. It seems like an odd out-of-the-way spot for an access hole, however.

@Jorge, this is for you, too :smile: ... these are the links for the Building 3 cross sections I found.

So what is on that level of the building? From 2 diagrams I found in a couple of Japanese-language PDFs I believe (if Unit 4 is similar to Unit 3) the floor at that elevation coincides with the bottom of the SFP, which we have placed in the SE corner of the building, yes?

This PDF shows a diagram on page 17 comparing Unit 3 RB construction with Unit 5:
http://www.pref.fukushima.jp/nuclear/info/pdf_files/100805-1.pdf​
Unit 3 is on the left. Notice the bottom of the SFP coincides with the floor at OP 26.9 meters.

Now have a look at page 35 of this PDF:
The top drawing is the same as the earlier one, so I'm assuming the drawings on this page are also for Unit 3 (even though I can't read Japanese). The second drawing on that page is an elevation view from the other direction. It looks like OP 26.9m is also the elevation of the low-bay part of the building to the east towards the turbine building (height above ground = 16.9 m = 55 ft.). This would be the "deck" area that the stairs on the south side of the building lead to. It would also be the lower extremity of your hole. On the same level as the bottom of the SFP.

Make of it what you will. Your diffuse lighting arguments re. shadows are persuasive, but I'm not at the point yet where I'm convinced it's a hole. We shall see! (It is good that we can disagree and be civilized and friendly about it.)
 
Last edited by a moderator:
  • #4,835
Most Curious said:
The CalTech document is a great collection of pictures and data relating to the Fukushima accident. I read it 10 days ago but glad to see it posted here again for all to consider.

I think it will be determined at some time in the future's investigation that like most of the bad things that happened resulted because of the total station blackout - a beyond design basis event. IOW, they were screwed when the tsunami took out the generators.

The venting system relies on fans and filters to remove particles before discharge up the stack. Apparently, little thought was given to a natural draft type back-up venting plan. Top goal was preventing radioactive release. Being so focused on that primary goal, they designed systems that INCREASED such releases in a severe accident!


What I have not seen discussed (and in 300 pages I may well have missed it!) is service water. Was service water (sea water for cooling) available after the EQ? Would it have been available after the tsunami IF electrical power had remained available? Once the suppression pools reached 100 degrees C even the steam driven pumps would have become useless. Just how long does it take to heat the SC to 100C without service water cooling available? Did high SC temperature fail the steam driven pumps or did loss of battery power cause that?

Emergency service water pumps would have been abvailable until the loss of AC. General service water woulld have been available in a reduced form. Most plants can power a reduced number of service water pumps in an emergency. I have no information about Fukushima service water.

The TEPCO reports in the first couple of days recorded when suppression pool temperatures reached 100 degC because they had to report that as an emergency event. Unit 1 had no steam driven pumps. They only had an isolation condenser. Units 2 and three were using steam driven pumps. Unit 2 stuck with RCIC until the suppression pool reached 100 degC. At some point for reasons I haven't seen, operators at unit3 switched to HPCI which requires higher steam flow than RCIC. Later they tried to switch back to RCIC, but failed. Unit 3 reported a loss of residual heat removal as an emergency port. I think this was before the suppression pool reached 100 degC. Use of SRVs would have continued to heat the suppression pool. In the US, Emergency Operating Procedures call for manual depressurization when the suppression pool reaches a temperature whre the suppression function is lost.
 
  • #4,836
MiceAndMen said:
The green blob is very interesting indeed. Cryptome says the picture was taken on 18 September 2010, which was before the shutdown for the core shroud replacement job. Maybe they did some work in that part of the building in preparation for that task. It seems like an odd out-of-the-way spot for an access hole, however.

@Jorge, this is for you, too :smile: ... these are the links for the Building 3 cross sections I found.

So what is on that level of the building? From 2 diagrams I found in a couple of Japanese-language PDFs I believe (if Unit 4 is similar to Unit 3) the floor at that elevation coincides with the bottom of the SFP, which we have placed in the SE corner of the building, yes?

This PDF shows a diagram on page 17 comparing Unit 3 RB construction with Unit 5:
http://www.pref.fukushima.jp/nuclear/info/pdf_files/100805-1.pdf​
Unit 3 is on the left. Notice the bottom of the SFP coincides with the floor at OP 26.9 meters.

Now have a look at page 35 of this PDF:
The top drawing is the same as the earlier one, so I'm assuming the drawings on this page are also for Unit 3 (even though I can't read Japanese). The second drawing on that page is an elevation view from the other direction. It looks like OP 26.9m is also the elevation of the low-bay part of the building to the east towards the turbine building (height above ground = 16.9 m = 55 ft.). This would be the "deck" area that the stairs on the south side of the building lead to. It would also be the lower extremity of your hole. On the same level as the bottom of the SFP.

Make of it what you will. Your diffuse lighting arguments re. shadows are persuasive, but I'm not at the point yet where I think it's a hole. We shall see! (It is good that we can disagree and be civilized and friendly about it.)

While unit 4 has the same power rating as units 2 and 3, it is a Hitachi built unit, while 2 and 3 were GE-Toshiba.
There may therefore be differences in the design specifics and the building layout.
 
Last edited by a moderator:
  • #4,837
etudiant said:
While unit 4 has the same power rating as units 2 and 3, it is a Hitachi built unit, while 2 and 3 were GE-Toshiba.
There may therefore be differences in the design specifics and the building layout.

That is true. This news article, though, does state...
A midlevel TEPCO official also said money was a big reason why repairs and changes to the No. 1 plant were not made.

"The blueprints for the reactor cores at the No. 1 plant were bought 'as is' by Toshiba Corp. from General Electric Co., so the priority at that time was on constructing the reactors according to those blueprints," the official said.

When the Fukushima No. 1 plant was being built, Japan was importing technology from the United States and learning from a more advanced nuclear power nation.

The No. 1 plant was considered a "learning experience."

A former TEPCO executive said, "The Fukushima No. 1 plant was a practice course for Toshiba and Hitachi Ltd. to learn about GE's design on a trial-and-error basis."

With the exception of the No. 6 reactor, the other five reactors at the Fukushima No. 1 plant are Mark I boiling-water reactors developed by GE.

http://www.asahi.com/english/TKY201104060126.html

I would bet money that the interior layouts of units 2-4 are quite similar, if not identical in most respects. Their external dimensions seem to be identical, as was their power output. I wouldn't be a lot of money on it, but I would bet some.
 
Last edited by a moderator:
  • #4,838
biffvernon said:
I guess the building must have a door - even a pretty big door to get equipment in and out. But that 'hole' does seem a long way above ground level and there's no sign of it in the earlier picture:

[PLAIN]http://img.ibtimes.com/www/data/images/full/2011/03/15/74732-tokyo-electric-power-co-s-fukushima-daiichi-nuclear-plant-no-4-reactor.jpg[/QUOTE]

I think it is a door. If you look really closely at biffvernon's picture, you can see the outlines of it on the right-hand side of the area that looks like a hole in other pictures. When it is open, it swings out to cover the left (as seen from the outside), so the square "hole" seen in other pictures is the combination of the inside of the open door and the interior of the building seen through the open door frame.

Note that there is a staircase going down the south side of reactor building 4 from the roof area accessed by that door.

I'm guessing that the door was either already open at the time of the earthquake for whatever reason, or it was opened by workers evacuating the building afterwards.

The bit of protruding concrete noted by MadderDoc may be a little rectangular rain guard over the door, to keep rainwater sliding down the wall away from the door seals, or else possibly a lighting fixture:
attachment.php?attachmentid=34848&d=1303695578.jpg
 
Last edited by a moderator:
  • #4,839
|Fred said:
service floor BP linked on the webpage was posted here originaly few dozen pages down and is not from Fukushima.

OK.

MadderDoc said:
If there indeed was a hole in the east wall of unit4, before the explosions, as these photos appear to be showing, there is no need to hypothesise about an extra explosion to cause it, nor that someone made the hole deliberately. We need no further assumptions because, we know that the building had just before been exposed to an extraordinarily strong earthquake.

I believe that just opposite to that hole, on the west side, there is a covered gallery that leads into the building, passing under the elevator that is used to move fuel casks in and out of the building. Perhaps the earthquake displaced a truck that was parked inside (or a cask that was about to be lifted, or whatever) and it hit the wall, knocking out one of the panels.

It seems that building #1 has very thick solid walls that get thicker in the lower levels, while buildings 2--4 have a skeleton of concrete columns with a relatively thin concrete shell loosely anchored on them. The hole seems to be on the lowest row of "panels". In the after-the-explosion pictures that row is almost buried under the rubble.

MadderDoc said:
But indeed the building appears to have had such a opening, however at the wall panel at row 2, column 4. Note the distinctly different way this panel has been blown off, with remaining sharp edges and paint deco along those edges. We see the same phenomenon at unit 3, the exact same position, row 2, column 4. The opening that has been made in the east wall of unit 2 is also in this position.

I vaguely recall a statement that those panels were weaker on purpose, meant to be knocked out in case of overpressure. I have also heard conflicting explanations about the #2 holes: some say they were made by the workers to avoid H2 buildup, some say they were caused by the explosion in #2, some say they were a consequence of #3's explosion. Which version is correct?
 
  • #4,840
MadderDoc said:
Second question: The east wall appears to be divided into vertical sections, a broad one in the middle, somewhat narrower sections to the right and left of that, and again, to the right and left of those sections, two even narrower sections towards the ends of the wall. What produces this appearance?

Jorge Stolfi said:
Perhaps they are lightning rod conduits, or rainwater drainage pipes. According to the #1 blueprints, the roof is slanted by 30cm in the E-W direction (although in #1 the East is lower). They seem to follow the main concrete pillars of the building, but offset to one side or the other, rather than down the pillar's midline.

They look like rainwater drainage pipes to me.
 
  • #4,841
Don't know if this link has already been posted. It's the latest video-ed press briefing plus all the previous ones. The 60 odd minutes left me with a strange empty feeling but someone may get something interesting out of it, especially the foreign press' question and answer period.

http://http://nettv.gov-online.go.jp/eng/prg/prg2107.html"
 
Last edited by a moderator:
  • #4,842
MiceAndMen said:
@Jorge, this is for you, too :smile: ... these are the links for the Building 3 cross sections I found.

They look authoritative. Thanks!
 
  • #4,843
Jorge Stolfi said:
I believe that just opposite to that hole, on the west side, there is a covered gallery that leads into the building, passing under the elevator that is used to move fuel casks in and out of the building.

Oops, forget, this does not seem to be correct. The "hole"is two stories up from the cask entrance. But it is the correct height for that floor. See the blueprint of #3 below:
 

Attachments

  • un3_building_cut_N_2.png
    un3_building_cut_N_2.png
    33.4 KB · Views: 464
Last edited:
  • #4,844
Update on the sub-drain isotope ratio measurements (time-series plots begin on page 3):
http://www.meti.go.jp/press/2011/04/20110423004/20110423004-5.pdf
 
Last edited by a moderator:
  • #4,845
Jorge Stolfi said:
OK.



I believe that just opposite to that hole, on the west side, there is a covered gallery that leads into the building, passing under the elevator that is used to move fuel casks in and out of the building. Perhaps the earthquake displaced a truck that was parked inside (or a cask that was about to be lifted, or whatever) and it hit the wall, knocking out one of the panels.

It seems that building #1 has very thick solid walls that get thicker in the lower levels, while buildings 2--4 have a skeleton of concrete columns with a relatively thin concrete shell loosely anchored on them. The hole seems to be on the lowest row of "panels". In the after-the-explosion pictures that row is almost buried under the rubble.



I vaguely recall a statement that those panels were weaker on purpose, meant to be knocked out in case of overpressure. I have also heard conflicting explanations about the #2 holes: some say they were made by the workers to avoid H2 buildup, some say they were caused by the explosion in #2, some say they were a consequence of #3's explosion. Which version is correct?

In US BWRs there are two blowout panels on the 5th floor, refueling area. These panels will pop at a few inches of water pressure. They are designed to vent off building pressurization during high energy line breaks or negative pressure events like a tornado.
 
  • #4,846

Attachments

  • vlcsnap-2011-04-25-07h33m35s94.jpg
    vlcsnap-2011-04-25-07h33m35s94.jpg
    39.9 KB · Views: 400
  • #4,847
rowmag said:
Update on the sub-drain isotope ratio measurements (time-series plots begin on page 3):
http://www.meti.go.jp/press/2011/04/20110423004/20110423004-5.pdf

Looks like this sample point is still acting different. Same observations and discussion as in my last post.
 
Last edited by a moderator:
  • #4,848
Danuta said:
Don't know if this link has already been posted. It's the latest video-ed press briefing plus all the previous ones. The 60 odd minutes left me with a strange empty feeling but someone may get something interesting out of it, especially the foreign press' question and answer period.

http://http://nettv.gov-online.go.jp/eng/prg/prg2107.html"
The Times asked why the new rules forcing people out of the evacuations zones did come now.

Part of the answer (translation starting at 32:00 in the video) was that one could not permit people to stay there, because if they came out of the exclusion zone, their contamination might be a danger for others.

Sorry, but this sounds like bollocks to me.

The press conference ended with a question about SPEEDI, why it does not give data. The basic answer was that the system does not have good input data, so that it cannot make forcasts.

So this expensive system is completely useless when Japan needs it...
 
Last edited by a moderator:
  • #4,849
etudiant said:
ZAMG was the only source that provided overall emission estimates from an early period.

There's also an IRSN estimate from March 22th: http://www.irsn.fr/FR/Actualites_presse/Actualites/Documents/NI-terme-source-22032011-tableau.pdf

90.000 TBq I131 and 10.000 TBq C137 - that's close to the numbers NISA and NSC released on April 12th.

Still confused though because even if the data was accurate only up to the date of issue ,12/4/2011 that still gives 30 x5,000TBqs of Ce137 average daily emission or 2 x chernobyl in one month as opposed to i x every 100 years.

You can't say "5000 TBq * 30". I'd expect that between 5000 and 15.000 TBq C137 escaped between March 11th and March 21th. Not per day. Overall number!
That's 10% of Chernobyl. And from March 21th on we can use these 0,14 TBq C137 per hour. And that's what I meant with "Chernobyl every 110 years".
 
  • #4,850
The government is taking TEPCO's side concerning the leak into the sea:
http://english.kyodonews.jp/news/2011/04/87554.html

It's probably based on the TEPCO's explanations found in this paper:
http://www.tepco.co.jp/en/press/corp-com/release/betu11_e/images/110421e2.pdf

But we all remember there were significant leaks into the sea even in March. For instance on 25th of March there was a sudden and significant rise in the radioactive density of seawater:
http://www.tepco.co.jp/en/press/corp-com/release/betu11_e/images/110326e5.pdf

So any ideas what caused this rise of radiation if not the leak they were able to stem on 6th of April?
 
Last edited by a moderator: