Magnetic Field Trouble in Los Angeles: Equipment Failures

In summary, the magnetic fields coming from the power line could be causing equipment failures in the building including a very sophisticated online battery back up. The best course of action at this point is to persist and try to get the power companies to act on the problem.
  • #36
Absolutely if you've got them all coiled up together on the floor. It's basically now become an inductor if that's the case and a back e.m.f. will be present. No shielding means it has no protection from this whatsoever.
 
Engineering news on Phys.org
  • #37
business man said:
Is it possible that there could be current running in the ground? We noticed that some of our conduits had current!

Like I said before this sticks out like a sore thumb. Try and find out how big these currents are. It's quite important as it will tell if this is the source of your other problems or not.
 
  • #38
Adder_Noir said:
What you said about testing each and every appliance until you find the potentially guilty one is exactly right. Most of the time that's how we end up sourcing electrical faults, by process of elmination.

It really is important for you to find out if you're still getting currents flowing through conductors when your building is isolated. This is a must. Call an electrician out as soon as is realistically possible and see if he can tell you if these disturbances are still present when isolated.

That makes sense

Do you have any neighbours nearby who might be using high current appliances? One further possiblity is that a local business or domestic property or something is feeding their return path through an Earth rather than neutral which runs into your property. Again it's just another possibility. The more suggestions you have ready when you've got a qualified person there the better :wink:[/
QUOTE]

My neighbors are mostly distribution companies, so this might be ruled out, they do not use big machinery. But what if this main feed to the city is improperly grounded??
 
  • #39
It's more a case of, what would happen if this main feed were not properly insulated from earth/ground. This would cause current loss at the substation and it would be obvious to the power company. If the feed is responsible for as much as it is suggested that it is then big problems would be occurring by now and the power company would likely already be all over it. I suspect it isn't the problem to be honest.

The only time an issue would arise when the main feed substation were not properly grounded would be during Earth fault conditions at your property. This would mean the Earth fault path would have to be greatly extended to the next Earth rod at the next nearest substation. This would lengthen the return path and lower the Earth conductor current.

I'm still betting on a faulty appliance or a wiring fault, i.e. an Earth in a neutral or vice versa by mistake :smile:
 
  • #40
Adder_Noir said:
Absolutely if you've got them all coiled up together on the floor. It's basically now become an inductor if that's the case and a back e.m.f. will be present. No shielding means it has no protection from this whatsoever.

They are not coiled up. It's a pretty straight run.
 
  • #41
Adder_Noir said:
It's more a case of, what would happen if this main feed were not properly insulated from earth/ground. This would cause current loss at the substation and it would be obvious to the power company. If the feed is responsible for as much as it is suggested that it is then big problems would be occurring by now and the power company would likely already be all over it. I suspect it isn't the problem to be honest.

The only time an issue would arise when the main feed substation were not properly grounded would be during Earth fault conditions at your property. This would mean the Earth fault path would have to be greatly extended to the next Earth rod at the next nearest substation. This would lengthen the return path and lower the Earth conductor current.
I'm still betting on a faulty appliance or a wiring fault, i.e. an Earth in a neutral or vice versa by mistake :smile:[/
QUOTE]

I will be all over this one tomorrow. Thanks

Any other comments? At this point I need to try everything.
 
  • #42
That's all I can think of for now. Doubtless something else will occur by tomorrow. For now I'm nipping off to bed. Best of luck pal :wink:
 
  • #43
I may have to sign off too :zzz:
 
  • #44
Here is the latest:

We set up our dedicated generator circuit last night with fused disconnect and so far that has been stable, so we are trying to start up the computers, which are running exclusively on that circuit.

Before leaving last night my Operations Mgr. switched off breakers to the HVAC systems and exhaust fans to see if they were the problem with regard to appliances or wiring.

When he arrived this morning other breakers had tripped and all morning we have been experiencing brown outs on various circuits. So based on the theory of interior appliance and wiring issues it seems we can rule out the HVAC/fan circuits now, correct?

The power company had six guys out to the building last night and not one of them was very helpful or even sympathetic, actually they were more adversarial.

Fortunately one of the guys was curious when he found out that breakers in our main service were tripping with little or no load, so they may want to investigate this further today.
 
  • #45
I would imagine yes you can rule out HVAC being the problem now.

business man said:
Fortunately one of the guys was curious when he found out that breakers in our main service were tripping with little or no load, so they may want to investigate this further today.

Sounds like they're not breakers mate they're RCD's or Residual Current Devices. They constantly look for even the slightest change in current between the live/phase and the neutral. If it detects one (can be as little as 10mA or so) it will trip the circuit.

The reason they throw when a change in current is detected is that the said change in current between the live and neutral means that some current is being lost to earth. If your man is correct I'd say that was a major breakthrough.

It means you have a faulty wire or appliance dumping current to earth. That may not be your only fault but it's the avenue I'd be charging down right now if I were in your shoes :wink:
 
  • #46
Here is a link to yesterdays report from Tom the expert from San Fransisco:
(It's a jpg from a scan so if it is too small, place cursor over document and wait for gold box to appear then click on center of gold box, which should make it readable.)

http://i141.photobucket.com/albums/r59/sunset91/sunset91.jpg

Please hang in there with me, it's far from being solved. Phone company is installing a new shielded T1 line today all the way to our phone equipment.
Right now we are dropping calls like crazy and loosing customers by the minute!
 
Last edited by a moderator:
  • #47
I was told that they are not RCD's, but in fact standard over current breakers, apparently not connected to neutral.

Could these breakers also trip for the same reason?

I just heard, minutes ago that a rep. from the power company witnessed an event personnally. Maybe now we will get some action from him!
 
  • #48
I work for a company that manufactures, installs and maintains electron microscopes. In order to determine if there is a lot of vibration or EMI we contract out to other companies. If this problem persists, there is a company called TCM that specializes in detection and cancellation of vibration and electromagnetic field. http://www.techmfg.com/index.htm?gclid=CNq8s8TAuIgCFTosGAodOlG4zA
 
  • #49
business man said:
I was told that they are not RCD's, but in fact standard over current breakers, apparently not connected to neutral.

Could these breakers also trip for the same reason?

No is the simple answer. Standard over-current breakers will not trip under low-load conditions. I'll print off Tom's report and have a read through it now.

Get someone to have another check as to what load they are tripping at if you can. Standard breakers tripping under low-load conditions is a very unusual event indeed and may mean something exceptionally weird is going on at your premises. This will be a fascinating discovery when the source of the problem is rooted out :wink:
 
  • #50
Here is one solution. In fact it might be the very reason this is going on. Looking at Tom's report it states they have observed bursts of high frequency current. This gave me an idea as to how your breakers could be tripping at low loads, or what appear to be low loads.

Have you ever heard of such a thing in electricity as harmonics?

They are caused by devices which draw current in non-linear fashions such as thyristor controlled drives. What they are, are very high frequency currents and voltages (much higher than the 60Hz being delivered being used as power) which contribute no useful power to anything but wreak havoc on electrical equipment.

Whenever we fitted a high current drive to a premises in my last job we always put huge inductors behind it to stop harmonics traveling back up the line. The reason is inductors oppose current with greater enthusiasm at high frequencies. Have a very, very good think if you've got anything like this kind of equipment on your premises. It would account for virtually all the phenomena you just mentioned, including the standard breakers going under what appears to be no/low-load but is infact a burst of high-frequency current operating at a frequency too high for a standard meter to pick it up.

It might not be the reason, but it certainly looks like it might be.
 
Last edited:
  • #51
Just read Tom's report and I would say indeed that this is what it is. CD drives will not open by themselves no matter how much current is being dumped to Earth by mistake.

Have a look at getting some harmonic filters (large inductors) fitted right away. I'm very sure that's what this is but it may indeed not be coming from your premises.

Tell the power company right away if they're still there that you think it may be a harmonic problem.
 
  • #52
Just a quick note before I go and make a cup of tea. These disturbances may well be originating outside of your property. They may infact be entering your property via the earth/ground line for example. This would account for why your problems got worse when you improved your grounding.

If I were you I'd be straight in touch with a contractor or the power company and get harmonic filters installed on your premises on your phase, neutral and Earth where your supply enters your property.

And the sooner the better :wink:

**Edit**

I'm signing off for the night. I'll pm ypu my mobile number in case you get really stuck during the night.
 
Last edited:
  • #53
I will get this info over to my guys asap. It's hard to get to them right now. They are all so busy directing traffic. I will try to update as more info comes back to me.

Thank you for your time and input.
 
  • #54
LURCH said:
Just a suggestion, but do you have a compass? If you take it just outside your building and it points to the power main instead of pointing North, then there's a good chance that the main is indeed the source of your woes.
The B-field from a transmission line points, not towards the line, but tangentially away from it. Furthermore, I know of no compass that has a response time below the 16 ms needed to detect an oscillating 60Hz field. A typical compass will not respond to a rapidly oscillating field; it will settle along the direction of the static field.

From what I've read so far, it seems there's a likely shielding problem here...has the office been checked for possible ground loops and such?

Also, with a half-decent oscilloscope and a length of wire, you can check for yourself if there's large 60Hz fields in the air (compared to someplace else).

<<Note: Just started reading this thread now (and haven't gotten past post#5), so if this is redundant, please ignore it.>>
 
Last edited:
  • #55
Thank you so much for taking the time to read this. We really need as many brains on this as we can get. I feel we are funneling down to something, or multiple things now.

The problem is far from being solved but at least now we are being recognized by the power company. Unfortunately even THEY may not be able to help, so that is why I am here, to try to get more intelligent possible solutions.

I am passing-on everything here, as it comes in, over cell phone, because they have no connection at the office.
 
Last edited:
  • #56
At about 8:45pm pst I was just informed by 2 employees working late, that several breakers tripped again, including lights, and they will not reset.
 
  • #57
The latest information regarding the power company is that they are FINALLY seeing how serious the situation is here but they do not have an answer yet.

They are going to power us down at noon tomorrow to change out a main breaker that they say is failing due to these ongoing problems. They are now at least very sympathetic to our situation and have assigned some senior more experienced people to the job.

Tom shaunessy from Powercet, our expert, is now saying that this is so serious that he feels a division of the military should be contacted about it. He doesn't seem like the kind of guy that would overreact, so I am really concerned now.

I can't imagine the losses if I have to move my entire operation to another building at this point, I am not sure if i could even find one. I am not sure if we can keep our servers running long enough to process payroll tomorrow, then there's invoicing, billing, payables, etc.etc. not getting processed now.

WE ARE SLOWLY AND PAINFULLY DIEING HERE
My operations manager, CEO, and computer tech are about ready to collapse from exhaustion. They have not gotten much sleep in the last few weeks.

Local Universities don't really want to talk to us. I think they are concerned about potential liability. We did get one that said if we submit a written report that they would look at it and get back to us. So far they have not done so.
 
Last edited:
  • #58
Blackadder;
I'm totally out of my league here, but I'm just going to try to clarify something. What you call an RCD seems to be, by your description, what we call a GFI (Ground Fault Circuit Interruptor). Is that correct?
 
  • #59
Danger said:
Blackadder;
I'm totally out of my league here, but I'm just going to try to clarify something. What you call an RCD seems to be, by your description, what we call a GFI (Ground Fault Circuit Interruptor). Is that correct?

That's the one mate. In fact that's a better name for it as it better explains what it does.

Business Man,

If you can mate I'd get someone into check for harmonic disturbances as your symptoms tie in very well with the problems they cause. Have you had a chance to check for anything like a drive or something which might be causing it?

Just one more thing that might be causing such things is a backfeed which could be generating a standing wave. I'm scraping my memory banks there but it's one suggestion and an Earth loop of some kind could I suppose be doing it as was mentioned above.

Your best bet mate is to shut down your property and slowly turn things back on again until you hit problems.

I still believe harmonic filters installed at your supply would help enormously if it can be proven that the source of disruption is external to your premises.
 
Last edited:
  • #60
I notice Tom's report states that the worry is the High Voltage DC line entering the city near your premises. Surely he means AC doesn't he? Or does he mean DC? I'm not sure what he means there can you check that one out please as it might be something that turns out to be important.

I've dug out my harmonics book and I'll list some of the things it states can be sources of such harmonic disturbances:

1)Transformer Magnetisation Non-linearities (a cracked core?)
2)Motors
3)Arcing devices - Electric Arc Furnaces, Discharge Type Lighting
4)Single phase rectification in D.C. power supplies (could be this one)
5)Three phase current sources (see explanation below)
6)Thyristor controlled drives
7)Inverter Fed A.C. Drives (don't even know what these are)

Three Phase Current Sources:

Had a little to do with these in my last job. A customer required some big pumps (and I mean big) to be run off an A.C. supply without rectification but with a voltage profile being a close match to D.C.. Problem is when you get that big it is either helpful or required (can't remember which) to use a method called twelve-pulse. It's done by taking an input from an A.C. source and routing one through a series of star and delta connections (very clever and totally beyond me) which alters the phase relationship between the two supplies which are then both fed into the motor by the same cable I believe. Reason is you super-impose one A.C. profile onto another in such a way that it reduces the ripple voltage going into the motor. Obviously anything slightly wrong with the phase relationship and you'll get some rather substantial problems, one of which being higher-than-normal supply frequency disturbances and magnitude spikes.

This could also I suppose (again I'm dredging everything up here) be caused by two supplies being connected to each other which are out of phase. Voltage spikes and high frequency disturbances could also occur here.

If I were you I'd get someone to check if your incoming Earth has current flowing in it when your building is powered down tomorrow. You really do need to know if the disturbances are originating in your premises or not.
 
  • #61
Emicro said:
I work for a company that manufactures, installs and maintains electron microscopes. In order to determine if there is a lot of vibration or EMI we contract out to other companies. If this problem persists, there is a company called TCM that specializes in detection and cancellation of vibration and electromagnetic field. http://www.techmfg.com/index.htm?gclid=CNq8s8TAuIgCFTosGAodOlG4zA

Also you might want to take down this guy's suggestion in case you need these folks. They might be able to help you with other stuff even if a magnetic field is not the issue.
 
  • #62
Ok, I am going over there in about an hour to make sure that all of the most logical suggestions here are contemplated or implimented.

Logically the first thing would be when they shut my power down at noon, we will use that time to check for current all over the building.

I did forget to mention one other thing but it may not be pertinent. I was told that in one of our servers with four or five drives, that one of the power suplies was arcing and had to be shut down.
Soon after that two or three hard drives failed so we are down to two drives now and they are limping along doing all the work but seem to be holding up.

The reason I bring it up now is because there has been discusion here about drives creating high frequency problems. The reason I did not bring it up earlier is because I think they have been shut down, and, or disconnected for a period of time and we were still having problems.

I must verify this today to see if the problems stop when circuits to the servers are swithched off.
 
Last edited:
  • #63
I just verified that the drive problem was suspect weeks ago. They completely isolated the server (disconnected) and we still experienced problems, so scratch that one off the list.
 
  • #64
Will do. Don't forget to report back your findings on Earth conductor current under isolation :cool:
 
  • #65
Just in case you need it here is my old employer's website.

John Merriman the guy who runs it is an uber expert on electrics. He is very busy though and you'd have to at least offer to re-imburse him if you were going to take up a lot of his time because he runs the company and it is very hectic, although I'm sure he'd be very glad to help.

http://www.jmsweb.co.uk"

His UK number is 0151 647 5092. I'm not sure how to ring it from outside the UK though, although I'm told it's very easy.

He might be the kind of guy who can point you straight to the problem.
 
Last edited by a moderator:
  • #66
What a day! Just got home. I am totally spent and overloaded with info.I will never be able to remember everything we did today. I met Tom today for the first time and all I can say is WOW is this guy sharp. He had so much cool eqiupment out there, I couldn't believe it!

I will keep it brief because more info will come to me later. Just want to hit the major points.

This is 99% most likely a EMF problem, and it may be one of the only combination of circumstances that exists in this country from what i am gathering.

The power line passing my building is D.C.! It was determined years ago that this is a more efficient way to get power transferred long distances, and was apparently government sponsored, but obviously not researched quite enough regarding easement and right of way guidlines and restrictions which are fairly well established for A.C.

I should say before I go too far, that when we shut down power to change out that main breaker, we saw a reading of around 280 mamps before and maybe around 260 after. This was checked in several places on both ends of the building and pretty consistant.

We checked several water lines outside, rebar below grade and in the wall.
DWP said he was ready to rule out that the problem was coming from ground but said he would leave a recording meter for 24 hrs.

We had several events today, breakers were tripping with normal loads, some while the guy was there, so he is actually saying that it could be EMFs from the D.C, line!

The best evidence came at 3:02 pm when just after an event, my computer guy runs back to the panel where we were all standing and says,"your not going to believe what i just saw"

One of our pallet wrappers was out in back and heard unusual crackling in the wires then a loud bang, and said a wire or wires were glowing!
So chris runs out to see the very end of the glowing wires before they went back to normal color.

more in a minute:
 
Last edited:
  • #67
DC on a major line?! WTF?! :confused:
 
  • #68
Tom, who you should know by now, was already thinking that the two lines running next to each other, should be fine no matter how much current was passing through them as long as they are balanced. His most recent theory is that when they are, for some reason out of balance, is when it causes our EMF problem.

The guy who manages this line has now been informed of the situation, and we took reports from three employees that saw or heard the wires at 3:02 along with our statements about the concurrent failure of magnetic breakers. He will also receive the report from the other DWP guy that will substantiate our claims of random failures that do not appear to be from ground or faulty wiring\appliances.

After this 3:02 event, I decided to take action. I had a bigger generator ordered, got it hooked up to our big UPS with line conditioner. Had the magnetic breaker bypassed, (still has fuse protection) so i wouldn't have to cage it. I had this hooked up to our phone system and computers with separate grounding using special receptacles that will not ground to the boxes but use ground wires inside conduit. I then had the computer cabinets grounded to the conduits.

In the phone room I went the extra mile, not only completing above tasks but also rigged a faraday cage from expanded metal lathe and twist ties that I grounded to conduit. I not only caged the equipment but also most of the hundreds of cables running in and out of the room, then grounded the metal wire rack that is sort of like a sideways ladder in a T shape that seemed like it needed to be grounded.

The only weekness here is that I could not complete the cage against the wall that the equipment is mounted to. That wall is away from the EMF source, or the far side, so I am hoping this does not compromise the cage's effectiveness too much.

The bottom line here is that I can run my business without lights and outlets for awhile, but not without phones and computers! So right now that's the priority.

When I left tonight they were just buttoning up the final connections. I am crossing my fingers. The last couple hits just before I left did not shut down the phones, which is a good sign, although the phones didn't always go down on every hit, I was encouraged and proud of my work.

We are crossing our fingers and toes.

There is a lot more to say about some of the readings from the awesome equipment Tom brought over, but I'm beat, I've got to be somewhere early A.M., will try to check in here sometime tomorrow.
 
Last edited:
  • #69
business man said:
Tom, who you should know by now, was already thinking that the two lines running next to each other, should be fine no matter how much current was passing through them as long as they are balanced. His most recent theory is that when they are, for some reason out of balance, is when it causes our EMF problem.

Wow no wonder you've had problems this really is a rare one. If I remember correctly then current running in one direction cancels out the magnetic field from current running in the opposite direction. That's why you have to use three core (actually four-cored) cable for two way lighting circuits so you never have a phase wire running departed from the neutral as it causes magnetic disturbance which can affect hearing aids.

If the operation relies on several lines running next to each other in opposite directions (or the same direction - I really can't remember which at the moment) to cancel out each others magnetic field then yes an imbalance woould cause a resultant magnetic field to be in effect.

Because it's D.C. the field would be stationary and would not fluctuate until something caused further imbalance in the line (someone turning on a big circuit somewhere) which might be what is causing sudden current spikes which are throwing your breakers. I believe however that your electronic equipment will still suffer even when the field is stationary.

My best guess is something extra has been routed onto this D.C. line recently which is drawing more current (alot more) but has not been compensated for in the other lines, i.e. all the load has been dumped onto one line. This will be causing the imbalance I think. It would be interesting to have a look at major construction projects which have been taking place in your town lately and see if this gives something away. Also maybe something has recently been de-comissioned causing the imbalance (perhaps more likely if these lines have been around a long time).

Remember when you said your computer guy said the T1 connection was super fast in one location of the building? Might be very interesting to see how that part of the building relates to the D.C. line's location compared to where it was situated when it was going very slowly.

The incident with your pallet wrapper is incredible and shows potentially just what a hopeless battle you've been fighting recently. I think it will be getting sorted out now though. I have to say I also suspect a lawsuit might be on the horizon for your lost earnings, assuming the power lines have been imbalanced without adequate investigation by the persons responsible for distributing their power.

Keep us informed please mate this is most interesting :wink:

*LOL just don't ask anyone with a hearing aid to visit your property at the moment either! :rofl:
 
Last edited:
  • #70
Just one thing to note although I suppose it's not your issue anyway but what the hell.

If the D.C. line relies on the neutral return path of each phase/live running next to each other to cancel out magnetic fields then if a phase/live has been routed back through the wrong neutral somewhere further down the line then that could be causing all this trouble. Might be worth mentioning :wink:
 

Similar threads

Replies
14
Views
2K
  • Electrical Engineering
Replies
4
Views
3K
Replies
22
Views
902
Replies
11
Views
1K
Replies
6
Views
3K
Replies
8
Views
2K
  • Electrical Engineering
Replies
10
Views
2K
  • Electromagnetism
Replies
4
Views
2K
  • Electromagnetism
Replies
10
Views
2K
Replies
9
Views
2K
Back
Top