The input current on a transformer does not need to match the rated output current to achieve that output, but the output voltage can vary based on the load and the transformer's regulation. For transformers with poor regulation, running below the rated load can lead to higher output voltage. The input current is calculated by dividing the output current by the turns ratio, with the relationship between input and output voltages following the inverse of this ratio. In a scenario with a 100V input and a 75V@50A output, the required input current would be 37.5A, assuming ideal efficiency. Understanding the power involved clarifies the relationship between input and output currents in transformers.
harblargh
Messages
3
Reaction score
0
Okay, now this may sound ridiculously stupid, but I know next to nothing about transformers and so I have a question:

Does the input current on a transformer have to match the rated output in order to get that output?

(i.e. A trans rated 5 amps putting out the full rated current on only 2.5 amps of input current.)
 
Engineering news on Phys.org
No, but depending on the regulation (essentially a measure of how efficient the transformer is) the output voltage maybe be dependent upon load--put another way, in order to get the stated output voltage given the correct input voltage, it must be run at or very near the rated load current. For transformers with good regulation, this is less important, but for those with relatively poor regulation, running it at much less than full rated load can result in a significantly higher output voltage. This may or may not be important, depending on the application's tolerance for voltage deviation.

However, to answer the question I think you're asking, the input current will be equal to the output current divided the turns ratio (the voltages will follow the inverse of this). For example, if your transformer has a load of 10 amps on the output and it's a 120-to-12 volt stepdown transformer, the input will be 10 A / (10/1) = 1 A, assuming an ideal transformer.
 
Oh. Thanks for the help.

The problem I just can't wrap my brain around is the actual flow of current. That's the issue.

For this hypothetical transformer, the rating is 50A with a matching load run though a VFD with a max load of 75V. Ergo, at maximum, the output would have to be 75V@50A.

What amperage would the 100V input would have to be to reach the maximum output rating?
 
Assuming decent regulation the loaded voltage ratio will roughly approximate the turns ratio (for a much more accurate figure, take the no-load voltage ratio). So, you can plug those figures into the equation in my previous post [input current = output current / (primary turns / secondary turns)] and that will be your answer.
 
Maybe it would help to look at the power involved.

Assuming a resistive load...

power in load = 75 volts times 50 amps = 3750 watts

The transformer is 100% efficient so...

3750 watts at 100 volts must mean a current in the primary of
(3750 watts / 100 volts) = 37.5 amps
since power = voltage times current.

This is the same answer as you get if you divide the output current by the turns ratio as above.
ie 50 amps /( 100 / 75 ) =37.5 amps.
 
Ah, I get it now. Thanks alot, I really appreciate it. :biggrin:
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...