Maximize Efficiency with Transmission Line Help - 99.5%, 577.4A, 692.88V

AI Thread Summary
The discussion focuses on calculating the efficiency of electricity transmission to a factory using specific parameters: 400 kW power consumption, 1.2 Ω resistance, and a 2 kW loss. The efficiency is determined to be 99.5%, but there is confusion regarding the current and voltage calculations, with incorrect values initially presented. The correct current through the transmission lines is derived from the power loss and resistance, leading to a voltage that is significantly higher than initially calculated. Participants emphasize the importance of using the correct units and understanding the distinction between power consumed and power lost. The thread serves as a reminder that hints are provided for educational purposes, not direct answers.
aliserwan
Messages
14
Reaction score
0
Homework Statement
A smaller factory uses 400 kW of power from the electrical grid. The total resistance of the pair of transmission lines carrying electricity to the factory is 1.2 Ω. The heat produced by the pair of transmission lines due to the motion of charges constitutes a loss in the process. The loss is 2 kW.
1-What is the efficiency of electricity transmission?
2- What current is carried by the supplying transmission line?
3- What voltage are the transmission lines connected to?
Relevant Equations
P=RI^2
V=RI or P/I
a) 99.5%
B) 577.4 A
c) 692.88 V
 
Physics news on Phys.org
aliserwan said:
Homework Statement:: A smaller factory uses 400 kW of power from the electrical grid. The total resistance of the pair of transmission lines carrying electricity to the factory is 1.2 Ω. The heat produced by the pair of transmission lines due to the motion of charges constitutes a loss in the process. The loss is 2 kW.
1-What is the efficiency of electricity transmission?
2- What current is carried by the supplying transmission line?
3- What voltage are the transmission lines connected to?
Relevant Equations:: P=RI^2
V=RI or P/I

a) 99.5%
B) 577.4 A
c) 692.88 V
B and C are wrong. Please post your working.
Hint: typical voltage for such would be many kV.
 
  • Like
Likes aliserwan
P=R*I^2 so I=(400000/1.2)^0.5=577.4 A
V=R*I so V= 577.4*1.2 =692.88 V
 
aliserwan said:
P=R*I^2 so I=(400000/1.2)^0.5=577.4 A
V=R*I so V= 577.4*1.2 =692.88 V
You are confusing the power consumed by the factory with that lost in the wires.
 
  • Like
Likes aliserwan
standard unit ? wat/aohm=Amber
v kvolt=kw/amber
??
 
haruspex said:
You are confusing the power consumed by the factory with that lost in the wires.
if i calculate:
I=(40/1.2)^0.5=18.25
v=I*R=18.25*1.2=21.9
but what about Units ? watt or Kw >> v or kv
 
efficiency=p-ploss /p =(400-2)/400 = 0.995
Ploss = I^2 * R then I = 40.8 A
P = V * I then V= 9.8 KV
 
  • Like
Likes aliserwan
ghaith7710 said:
efficiency=p-ploss /p =(400-2)/400 = 0.995
Ploss = I^2 * R then I = 40.8 A
P = V * I then V= 9.8 KV
This is a homework thread.
Please read the forum guidelines. We provide hints, point out errors, but do not provide solutions.
 
  • Like
Likes aliserwan
aliserwan said:
if i calculate:
I=(40/1.2)^0.5=18.25
v=I*R=18.25*1.2=21.9
but what about Units ? watt or Kw >> v or kv
You have not understood my post. All you have done there is lose the "k" in kW.

We do not know the resistance of the load in the factory. We know the resistance of the wires, and we know the power lost in the wires, so what is the current through the wires?
 
  • Like
Likes aliserwan
  • #10
Just a note in my capacity as moderator. I just want to reinforce what has been said - hints are provided - not answers. Just as a further hint - we are using KW ie thousands of watts. When calculating remember results will be in thousands as well. Now you know the resistance and power loss hence can calculate the current in thousands of amps. Knowing the resistance and amps, ohms law gives the voltage in thousands of volts across the wires, knowing the current in the device its connected to and power consumed you can calculate the voltage across it. Add them up.

Thanks
Bill
 
Last edited:
  • Like
Likes aliserwan