Measuring Voltage with Step-Down Adapters: Questions & Answers

  • Thread starter Thread starter whiterabbot1
  • Start date Start date
  • Tags Tags
    Measuring Voltage
AI Thread Summary
When building an energy monitor, understanding voltage measurement from a single outlet can be confusing, especially regarding step-down adapters. The low source impedance of AC mains power allows for accurate voltage measurement from any outlet, even when appliances like dryers and air conditioners are on separate circuits. This is because the power supply is designed to maintain voltage stability despite varying loads. Resources provided include links to HyperPhysics for further clarification on household electricity. Accurate voltage readings can be achieved as long as the two-phase loads are reasonably balanced.
whiterabbot1
Messages
2
Reaction score
0
I am currently building an energy monitor according the the specifications of this site,http://openenergymonitor.org/emon/node/59. I understand how the current is measured but I am confused by the voltage measurement circuit.
I do not understand how the step-down adapter can correctly measure voltage usage from one outlet. I understand that the lights and outlets are in series but I was reading that typically dryers and air conditioners are typically on a separate circuit. So how can the voltage used from these appliances be measured from the one outlet?

Thanks.
 
Engineering news on Phys.org
whiterabbot1 said:
I am currently building an energy monitor according the the specifications of this site,http://openenergymonitor.org/emon/node/59. I understand how the current is measured but I am confused by the voltage measurement circuit.
I do not understand how the step-down adapter can correctly measure voltage usage from one outlet. I understand that the lights and outlets are in series but I was reading that typically dryers and air conditioners are typically on a separate circuit. So how can the voltage used from these appliances be measured from the one outlet?

Thanks.

The source imedance for your AC Mains power is very low, so unless there is a fault somewhere, you can measure you whole-house AC Mains voltage from any outlet in your house. This assumes that your two phase loads are reasonably well balanced (USA comment).
 
I know that you can but I do not understand why you can. If you could point me to some good resources that would be great.

Thanks.
 
When berkeman says,
The source impedance for your AC Mains power is very low...
(bold p added by me), implies that the transformer that is providing this power is rated so the voltage won't sag when you take power from it. Also, the power company is able to deliver such large amounts of power that flipping on a light switch has really no effect on lowering what can be supplied.

Here's a couple of links that you might find interesting.
http://hyperphysics.phy-astr.gsu.edu/hbase/electric/hsehld2.html#c1"
http://hyperphysics.phy-astr.gsu.edu/hbase/electric/hsehld.html#c1"

Regards
 
Last edited by a moderator:
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...
Hello dear reader, a brief introduction: Some 4 years ago someone started developing health related issues, apparently due to exposure to RF & ELF related frequencies and/or fields (Magnetic). This is currently becoming known as EHS. (Electromagnetic hypersensitivity is a claimed sensitivity to electromagnetic fields, to which adverse symptoms are attributed.) She experiences a deep burning sensation throughout her entire body, leaving her in pain and exhausted after a pulse has occurred...