Phase relationships in Thévenin circuit

In summary: Exactly. The reactance drop j20 will be vertical, on the tip of the horizontal phasor (VL+20). It is in quadrature with the resistive drop.Where do I draw Vth?Vth is the "phasor addition" of voltages on horizontal and vertical axes. Don't draw Vth. Just show the equation (green line) and the phasors that go into it.In summary, the conversation discusses the construction of a phasor diagram for a circuit involving a storage heater load. The phasor diagram is used to determine the phase relationships between different voltages in the circuit, including the Thevenin voltage, Thevenin resistance drop, and Thevenin reactance drop.
  • #1
Weaver
70
6

Homework Statement


2014 Q2.png

2. Homework Equations

3. The Attempt at a Solution
PhotoScan.jpg

[/B]
For part (c), should the phasor diagram just have everything on a straight line, save for the Rt and Vrt?

Honestly not sure how to attempt part (d) as we never really covered phase relationships in lectures, just looking specifically at phase diagrams of a capacitor or inductor.
 
Physics news on Phys.org
  • #2
It would be convenient if you chose the load voltage as the reference phasor in your phasor diagram. You can solve all the questions upto e) once you draw this phasor diagram.
Start with the horizontal load voltage phasor VL∠0°.
 
Last edited:
  • #3
cnh1995 said:
It would be convenient if you chose the load voltage as the reference phasor in your phasor diagram. You can solve all the questions up to e) once you draw this phasor diagram.
Start with the horizontal load voltage phase VL∠0°.

Ok. So will all the Voltages, save for the Thévenin resistance voltage, be on the horizontal axis? Or is VL shifted as result of the complex impedance of RT before it.
 
Last edited:
  • #4
Conor_B said:
Ok. So will all the Voltages, save for the Thévenin resistance voltage, be on the horizontal axis? Or is VL shifted as result of the complex impedance of RT before it.

Actually, after thinking about it some more, would the voltage of VL be VTH - VR given the voltage from VTH isn't 'dropped' across anything else other then those two resistances?
 
  • #5
Conor_B said:
would the voltage of VL be VTH - VR given the voltage from VTH isn't 'dropped' across anything else other then those two resistances?
You are forgetting the j0.25 ohm reactance. Yes, VL and VR will add algebraically since they are in phase but that won't give you Vth. You need to draw the reactance drop phasor too.
 
  • #6
cnh1995 said:
You are forgetting the j0.25 ohm reactance. Yes, VL and VR will add algebraically since they are in phase but that won't give you Vth. You need to draw the reactance drop phasor too.

Ok, I am still not sure how the phasor diagram should look. Prior to this, the only phasor diagrams we have been taught is the general one for a capacitor and inductor.

Would it look like this?

PhotoScan.jpg
 
  • #7
Conor_B said:
Ok, I am still not sure how the phasor diagram should look. Prior to this, the only phasor diagrams we have been taught is the general one for a capacitor and inductor.

Would it look like this?

View attachment 110304
No. Vth and VL are not in phase. VR and VL are in phase. Recall KVL. Sum of the voltage drops across Thevenin resistance, Thevenin reactance and load is equal to the Thevenin voltage. You know the magnitudes of three of them and their phase relation.

Edit: Just to confirm, are we using the same terminology? I am taking VR as the voltage across the thevenin resistance, VL as the voltage across the storage heater load and Vth is the mains voltage.
 
  • #8
cnh1995 said:
No. Vth and VL are not in phase. VR and VL are in phase. Recall KVL. Sum of the voltage drops across Thevenin resistance, Thevenin reactance and load is equal to the Thevenin voltage.

Ok, that's what I meant when I said
Conor_B said:
would the voltage of VL be VTH - VR

I was taking VR to be the voltage drop for both the reactance and resistance.

Would the phasor diagram look like this then?

PhotoScan.jpg
 
  • #9
Conor_B said:
I was taking VR to be the voltage drop for both the reactance and resistance.
Ok. Let's call it the Thevenin impedance drop Vz.
cnh1995 said:
Edit: Just to confirm, are we using the same terminology? I am taking VR as the voltage across the thevenin resistance, VL as the voltage across the storage heater load and Vth is the mains voltage.
In your diagram, you have shown Vz leading Vth by 45°, which is not true. Phase difference between Vz and Vth is not 45°. You need to show the Thevenin reactance drop Vx too in the diagram (drop across the line reactance).
Start with the horizontal load voltage phasor VL. How will Thevenin resistance drop VR and Thevenin reactance drop Vx be added to VL? You know the magnitudes of these three and their phase relationship. You also know that their phasor addition will give you Vth. Could you proceed with this?
 
Last edited:
  • #10
cnh1995 said:
Ok. Let's call it the Thevenin impedance drop Vz.

In your diagram, you have shown Vz leading Vth by 45°, which is not true. Phase difference between Vz and Vth is not 45°. You need to show the Thevenin reactance drop Vx too in the diagram (drop across the line reactance).
Start with the horizontal load voltage phasor VL. How will Thevenin resistance drop VR and Thevenin reactance drop Vx be added to VL? You know the magnitudes of these three and their phase relationship. You also know that their phasor addotion will give you Vth. Could you proceed with this?

Ok. There's been confusion from terminology, so I'll use yours (Vth, Vr, Vx,VL)

Right. So Vth = Vr + Vx + VL

The current in the circuit is 80A

This means Vr = 80(0.25) = 25

And Vx 80(j0.25) = j25

VL = Vth - Vr - Vx
VL = (240 +j0) - 25 - j25
VL = 215 - j25

Is this right so far?
 
  • #11
Conor_B said:
This means Vr = 80(0.25) = 25

And Vx 80(j0.25) = j25
20 and j20...
Conor_B said:
VL = Vth - Vr - Vx
VL = (240 +j0) - 25 - j25
VL = 215 - j25
We are taking VL as reference here.
So, Vth= (VL+j0)+20+j20.
i.e.
Vth=(VL+20)+j20.

Can you draw the phasor diagram from this green equation?
 
  • #12
cnh1995 said:
20 and j20...

Sorry, do know what I was thinking there :sorry:

cnh1995 said:
We are taking VL as reference here.
So, Vth= VL+j0+20+j20.
i.e.
Vth=(VL+20)+j20.

I'm not sure. Do I take the VL and the 20(Vr) both to be on the horizontal axis and just put j20(Vx on the Vertical axis?

Where do I draw Vth?
 
  • #13
Conor_B said:
I'm not sure. Do I take the VL and the 20(Vr) both to be on the horizontal axis and just put j20(Vx on the Vertical axis?
Exactly. The reactance drop j20 will be vertical, on the tip of the horizontal phasor (VL+20). It is in quadrature with the resistive drop.
Conor_B said:
Where do I draw Vth?
Vth is the "phasor addition" of voltages on horizontal and vertical axes. Don't they form a right angled triangle? Vth is its hypotenuse. You know the magnitude of the hypotenuse and the vertical side. You can compute the length of the horizontal side and get the load voltage.
 
  • #14
cnh1995 said:
Exactly. The reactance drop j20 will be vertical, on the tip of the horizontal phasor (VL+20). It is in quadrature with the resistive drop.

Vth is the "phasor addition" of voltages on horizontal and vertical axes. Don't they form a right angled triangle? Vth is its hypotenuse. You know the magnitude of the hypotenuse and the vertical side. You can compute the length of the horizontal side and get the load voltage.

So, is this it?
PhotoScan.jpg
 
  • #15
Conor_B said:
So, is this it?
View attachment 110309
Your calculations are all correct, but in your phasor diagram, you should swap Vr and VL since you have assumed VL as the reference phasor. It's a standard practice to draw the reference phasor first and then draw the remaining ones.
 
  • #16
cnh1995 said:
Your calculations are all correct, but in your phasor diagram, you should swap Vr and VL since you have assumed VL as the reference phasor. It's a standard practice to draw the reference phasor first and then draw the remaining ones.

Ok. I'll do that in future. Can I draw the circuit currents in the diagram also? Is the 80A just along the VL?
 
  • #17
Conor_B said:
Ok. I'll do that in future. Can I draw the circuit currents in the diagram also? Is the 80A just along the VL?
Yes.
 
  • #18
cnh1995 said:
Yes.

Ok, so for part (d) Calculate the phase relationship between the Thevenin equivalent circuit voltage and the current

Do I work out the angle the current is lagging by?
 
  • #19
Conor_B said:
Ok, so for part (d) Calculate the phase relationship between the Thevenin equivalent circuit voltage and the current

Do I work out the angle the current is lagging by?
Yes. You can do it using elementary trigonometry.
 
  • #20
cnh1995 said:
Yes. You can do it using elementary trigonometry.

Grand. So it is:

ϕ = sin-1(20/240) ≈ 4.78°.

I take it for part(e) Calculate the total resistance of the storage heaters, it is:
V/I

VL / 80∠4.78°?
 
  • #21
Conor_B said:
VL / 80∠4.78°?
Load voltage VL and current are in phase. The phase angle of both is 0°.
 
  • #22
cnh1995 said:
Load voltage VL and current are in phase. You need not use the phase angle.

Ok, so it is (20√143 - 20)/80 ≈ 2.74 Ω ?

Do I have to use 2.74∠-4.78° to get it relative to the Vth ?
 
  • #23
Conor_B said:
Ok, so it is (20√143 - 20)/80 ≈ 2.74 Ω
Yes.
Conor_B said:
Do I have to use 2.74∠-4.78° to get it relative to the Vth ?
No.
 
  • #24
cnh1995 said:
Yes.

No.

Right. And then for (e) What happens to the power dissipated in the storage heaters if the supply frequency is raised above 50 Hz? Is it just:

Given the Vx is dependant on ω (which is 2πf), an increase in f will lead to an increase in Vx and so the current in the system will decrease and with that, the power output in the storage heater also decreases?
 
  • #25
Conor_B said:
Given the Vx is dependant on ω (which is 2πf), an increase in f will lead to an increase in Vx and so the current in the system will decrease and with that, the power output in the storage heater also decreases?
Right.
 
  • #26
cnh1995 said:
Right.

Great. Thank you very much!
 
  • #27
Conor_B said:
Great. Thank you very much!
You're welcome!:smile:
 
  • Like
Likes Weaver

What is a Thévenin circuit?

A Thévenin circuit is a simplified model of a complex circuit that contains a single voltage source and a single resistance. It is used to analyze the behavior of a circuit at a specific point by replacing the entire circuit with a voltage source and a resistor, known as the Thévenin equivalent circuit.

What is the purpose of analyzing phase relationships in Thévenin circuits?

The phase relationships in Thévenin circuits determine the relationship between the voltage and current at a specific point in the circuit. This allows for a better understanding of how the circuit behaves and how to optimize its performance.

How do phase relationships affect the overall behavior of a Thévenin circuit?

The phase relationships in a Thévenin circuit impact the overall impedance, power, and efficiency of the circuit. By understanding these relationships, scientists and engineers can make informed decisions on how to improve the circuit's performance.

What factors can influence phase relationships in Thévenin circuits?

The main factors that can influence phase relationships in Thévenin circuits include the type and value of the components used in the circuit, the frequency of the input signal, and the impedance of the load connected to the circuit. These factors can affect the phase angle and amplitude of the voltage and current in the circuit.

How can the phase relationships in a Thévenin circuit be measured and analyzed?

The phase relationships in a Thévenin circuit can be measured and analyzed using various techniques, such as oscilloscopes, network analyzers, and mathematical calculations. These tools allow scientists to visualize and quantify the phase relationships in the circuit, providing valuable insights into its behavior.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
19
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
8
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
12
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
3
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
9
Views
4K
  • Engineering and Comp Sci Homework Help
2
Replies
62
Views
6K
  • Engineering and Comp Sci Homework Help
Replies
3
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
3
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
11
Views
4K
Back
Top