What is the difference between pound-mass and pound-force in HVAC equations?

  • Thread starter Thread starter russ_watters
  • Start date Start date
AI Thread Summary
The discussion clarifies the distinction between pound-mass and pound-force in HVAC equations, specifically regarding the density of air. It addresses confusion over the term "pounds" on psychrometric charts and confirms that 14 lb/ft^3 refers to the weight density of air. The derivation of the velocity pressure equation VP=4005 V^1/2 is explored, revealing that the constant 4005 is derived from unit conversions and is affected by the ASHRAE handbook. The conversation highlights the importance of correctly placing density in the equation and the challenges of using the Imperial system compared to the metric system. Overall, the participants emphasize the need for clarity in understanding these concepts for accurate HVAC calculations.
Messages
23,694
Reaction score
11,136
I'm having a slow day (pun intended) today, and I need a little help. I'm getting pound-mass and pound-force mixed up in my head. On a psychrometric chart, it just says "pounds", but is 14 lb/ft^3 the mass or weight density of air? I've been using cheater equations for the past few years, but now I need to do derive the typical hvac cheater equation for pressure vs velocity:

VP=4005 V^1/2

VP = velocity pressure in inchess of water
V = Velocity of air in feet per minute

So where does the 4005 come from...?
 
Physics news on Phys.org
Ok, so it would appear that I'm not a complete idiot. See, the problem my boss and I were having is that we were not able to reconcile equation 1 on PDF page 55 http://www.alnor.com/downloads/manuals/1980497B.pdf with our "cheater" equation. The problem -- the equation is wrong in our flow-hood manual. Still, I'd like to finish the derivation...
 
Last edited by a moderator:
(P1-P2)/Rho = V^2/2g (P1 is the total pressure, against the flow, and P2 is the static pressure, perpendicular to the flow, of the measurement)

Density of air at STP is, approximately, 0.075lbm/cu.ft.
1lbf/sq.ft = 0.1922 inches wg
g = 115820 ft/min^2

So, V = [2g(P1-P2)/Rho]^1/2 = [2x115820(VP)/(0.075x0.1922]^1/2 = 4008.66(VP)^1/2

Better conversion factors yield the result close to the standard constant 4005.
 
(eh.. with all hatred towards IP system) Change that g to gc (32.2 lbm.ft/lbf.sec^2)

By the way, the constant 4005 is derived not because better unit conversions are used but the decimal value is chopped off (courtesy : ASHRAE handbook of fundamentals 2005)

Only correction required to the eq. given in the above reference is to put the density under the square root.
 
Thanks - I must've worked on that for an hour and couldn't get my units straight. I've only been in "the real world" for 4 years and already I'm starting to get rusty...
 
I know the feeling! Possibly the best thing about the ISO/SI system is that it forces a clear distinction between mass and weight?
 
russ_watters said:
I'm getting pound-mass and pound-force mixed up in my head. On a psychrometric chart, it just says "pounds", but is 14 lb/ft^3 the mass or weight density of air?
One of the primary reasons I prefer metric/SI! IP is so . . .
 
Back