Apologies for getting the math (wildly) wrong;
@phinds numbers are correct, and I updated the sketch to match.
fourthindiana said:
Therefore, I still don't know the answer to the following question: Why does my instructor say that the multimeter would measure zero voltage across the contacts of the contactor in the ladder diagram in the attached photograph?
Lets view the question from another perspective. Fluke 116 meter specs for the default, auto-ranging voltmeter function "Auto-V LoZ" is a 600.0 V range with a resolution of 0.1 V. Per the manual, auto-ranging also "sets the Meter’s input impedance to approximately 3 kΩ to reduce the possibility of false readings due to ghost voltages."
We don't know what the contact resistance is (although we do know it ought to be very nearly zero ohms), the current through the contacts is 27.6 amps, and meter resolution is 0.1 volts. Solving Ohm's law for resistance (R=E/I), 0.1V/27.6 amps = 0.0036 ohms.
This particular meter will read contact voltage drop as no more than 0.1V when contact resistance is 0.0036 ohms (3.6 milliohms) or less. Chances are this is why your instructor claims it will read zero voltage. It depends on the characteristics of the contacts in question, but 3.6 milliohm (preferably, significantly less) would be necessary for a contact set capable of conducting this high a current. Why do I say this?
Power=Volts * Amps = I
2R.
27.6
2 * 0.0036 ohms = 2.76 watts, and that translates to a fairly high amount of contact heating. For comparison, specs for a typical "ice-cube" relay with 6A rated contacts is 50 milliohms maximum contact resistance, which produces 1.8 watts (6
2 A * 0.05 ohms).
In your example circuit, if contact resistance was much higher than 0.0036 ohms they'd be dissipating even more heat, and would tend to be unreliable. For instance, power dissipation for a 0.05 ohm (50 milliohm) contact resistance at 27.6 amp is 38 watts. This is on par for a mid-range soldering iron heating element, and would fairly quickly burn up the contacts.
fourthindiana said:
That is totally in contradiction to what my HVAC instructor writes. Why does my HVAC instructor say otherwise? Is it because the voltage is zero across the elements but the voltage difference (whatever that means) is not zero across the elements?
My assumption reading your sketch is of a typical U.S. residential circuit where L1 to neutral is 115V, L2 to neutral is 115V, and voltage between L1 and L2 is 230V. No neutral is shown in the sketch, and makes it somewhat ambiguous.
fourthindiana said:
But I am asking about putting a voltmeter across a normally closed contactor, not a short. Why are you talking about shorts?
To add to the answers above, imagine what would happen if a closed contact set was wired across a 230V source. For the 0.0036 ohm contact set postulated above, I=E/R, 230V/0.0036Ω, or just shy of 64,000 amps. Chances are the source wouldn't be able to provide that much current, and circuit protection (breakers, and/or fuses) would clear, but probably not before the contacts were destroyed.