Single Phase Voltage from 3-Phase Line: Explained

AI Thread Summary
In a 3-phase line with a 25kV line-to-line voltage, the voltage of a single phase line is typically 14.4kV when referenced to a neutral. This is calculated using the formula L-N = Vl/sqrt(3). Single phase transformers are used to convert the higher voltage to a user-friendly level, and the neutral is essential for creating a complete circuit. In distribution systems, the preference is for line voltages without using the neutral directly, and the single phase voltage is determined by transformer ratings. Overall, the single phase voltage does not remain at 25kV but is stepped down to a safer level for distribution.
louie
Messages
10
Reaction score
0
If I'm considering a 3 phase line (25kV line-to-line voltage) that comes to a point and splits into single phase lines, what is the line voltage of one of the single phase lines ?

Does it remain 25 kV or is it 14.4 kV because you're only dealing with 1 phase and a neutral now ?

Any explanation would be great

Louie
 
Engineering news on Phys.org
Normally, they do not distribute L-N = Vl/sqrt(3)=14.4kV, only L-L =25kV. The phases can split AB, BC, CA. The single phase transformers convert 25K--> user voltage with the ground reference applied at the secondary neutral.
 
A single phase line by definition is a circuit with only one phase. So you need a neutral side to create a loop. The voltage differential between the line and the neutral is, of course, +/- 14.4 kV and not 25 kV.

If you use both line (AB, AC, or BC) ... I don't think that a single phase line. It may be within the category of two phase line :-)

aaNg
 
For distribution purpose only line voltages preferred so neutral is not used. And 25KV will not be splitted into single phase directly it will be step downed and than you will get a sinle phase line. sinle phase line voltage depends on the transformer rating.
rgds
Mahadev
 
Actually, The main method of urban and suburban over head and URD is done single phase with line-neutra *in the usa*, europe is 3-phase secondary distribution 3-phases+ 2*line voltage = 8* the secondary line distance over the US, the neutral designation is MGN, or multiple grounded neutral, It is a lower wire of the four, or sometimes used as a top wire overhead shield in lightning prone areas. the L-N is used as the final distribution to the LNL +120 N -120 final use in typical residential apps.
 
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Hello dear reader, a brief introduction: Some 4 years ago someone started developing health related issues, apparently due to exposure to RF & ELF related frequencies and/or fields (Magnetic). This is currently becoming known as EHS. (Electromagnetic hypersensitivity is a claimed sensitivity to electromagnetic fields, to which adverse symptoms are attributed.) She experiences a deep burning sensation throughout her entire body, leaving her in pain and exhausted after a pulse has occurred...