Solving 3 Phase 11kV Line w/ 4.1 MW & 2.6 MVAR Lag

  • Thread starter Thread starter ads114
  • Start date Start date
  • Tags Tags
    Transmission
AI Thread Summary
To solve the problem of a 3-phase 11kV line delivering a load of 4.1 MW and 2.6 MVAR lagging, the first step is to calculate the apparent power (S) using the power triangle, where S = √(P² + Q²). The power factor can then be determined by the formula cosθ = P/S, converting the reactive power into a power factor value between 0 and 1. The series impedance of the line is given as (7.2 + j12.1), which will be used to calculate the sending end voltage and load angle. Understanding these calculations is crucial for accurately determining the electrical parameters of the system.
ads114
Messages
11
Reaction score
0
hi there.

can anybody advise with this one please?

a short 3 phase 11kv line delivers a load of 4.1 mw,2.6 mvar lag if the series impedance of the line is (7.2 +j12.1 ) calculate the sending end voltage and load angle.

the thing which is confusing me is the 2.6mvar lag bit,i know i need to get a power factor from this to work things out, how do i change this into a power factor value ie 0-1?

any pointers appreciated.
 
Physics news on Phys.org
You have P=4 MW and Q = 2.6MVAR, so you can get S using the power triangle and then you can easily get the power factor, cosθ = P/S.
 