Start capacitors on 2 phase equipment

AI Thread Summary
Issues with a replacement chiller unit requiring 230VAC single phase are discussed, particularly regarding its operation on a 2-phase 110VAC supply. The failure of the compressor to start consistently, despite running previously on a similar setup, raises questions about the adequacy of the starter capacitor. It is noted that the new motor may not handle the lower voltage effectively, leading to higher current demands that the existing capacitor cannot meet. The discussion emphasizes the importance of understanding phase angles and suggests that using a larger start capacitor or a "hard start" kit could resolve the starting issues. Overall, the electrical supply configuration and component specifications are critical to ensuring proper motor function.
tonyole
Messages
2
Reaction score
0
Hi there. So here goes.

I have been having issues with a replacement chiller unit that requires 230VAC single phase.
An identical unit was running on 2 phases of a 110VAC 3 phase supply. I had a start capactior fail in this unit. When I connected the replacement unit, the compressor failed to kick on however it started when bumped with my fist. After kicking off however, the compressor would not always kick back on when required.

So... Since the power supply I'm using to "mimic" a single phase 230VAC supply is ACTUALLY a 2 phase 110VAC (2 of 3 phases) ie. not 180° opposed but 120° then 240°, does this mean that with regard to starting capacitors, polarity becomes an issue?

I am aware that the resultant voltage is 208VAC, however the original unit has run on this supply for a number of years without issue.

Thanks for any insight.

T
 
Engineering news on Phys.org
The starter capacitor with the new motor may be insufficient to pass the necessary starting current at the lower voltage.

Induction motors do not like low voltages, as they then draw a high current.
The starter capacitor has less voltage and a higher current demand. It will be too small.

New motors are built closer to the minimum spec. Old motors are more tolerant to abuse.
 
Are there two or three power wires going into the motor ?

A 208/120 system
is 120 single phase when connect from phase to neutral
and when you connect with just two wires from phase to phase it's 208 but still single phase

so your assumption about phase angle
Since the power supply I'm using to "mimic" a single phase 230VAC supply is ACTUALLY a 2 phase 110VAC (2 of 3 phases) ie. not 180° opposed but 120° then 240°, ...
is not correct unless all three phases, not just two of them, are carried to the motor.

Draw your phasor triangle.

Baluncore seems on right track. A bigger start capacitor may help. Electrical supply houses sell "hard start" kits for residential airconditioners - basically just more starting capacitance.
 
Thanks guys. I appreciate the input.
 
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Hello dear reader, a brief introduction: Some 4 years ago someone started developing health related issues, apparently due to exposure to RF & ELF related frequencies and/or fields (Magnetic). This is currently becoming known as EHS. (Electromagnetic hypersensitivity is a claimed sensitivity to electromagnetic fields, to which adverse symptoms are attributed.) She experiences a deep burning sensation throughout her entire body, leaving her in pain and exhausted after a pulse has occurred...