I wonder if the LHC PCs and Macs still use surge strips.. although the main lines of course use SPD Type 1 and 2.
If anyone has any information about the surge protection technology used in LHC, please let me know.
Well I have spend several hours reading about surge protectors.. and have finally understood it. Now I'll share what I learnt.
First about Joules as specs... I read
https://www.nemasurge.org/faqs/
"Is the Joule rating of an SPD important?
While conceptually a surge protective device (SPD) with a larger energy rating will be better, comparing SPD energy (
Joule) ratings can be misleading. More reputable manufactures no longer provide energy ratings. The energy rating is the sum of surge current, surge duration, and SPD
clamping voltage.
In comparing two products, the lower rated device would be better if this was as a result of a lower clamping voltage, while the large energy device would be preferable if this was as a result of a larger surge current being used. There is no clear standard for SPD energy measurement, and manufacturers have been known to use long tail pulses to provide larger results misleading the end users.
Because Joule ratings can easily be manipulated many of the industry standards (UL) and guidelines (IEEE) do not recommend the comparison of joules. Instead they put the focus on actual performance of the SPDs with test such as the Nominal Discharge Current testing, which tests the SPDs durability along with the VPR testing that reflects the let-through voltage. With this type of information a better comparison from one SPD to another can be made."
The following are excellent resources that I spent many hours reading and mastering:
https://www.stevejenkins.com/blog/2014/10/whats-the-best-whole-house-surge-protection/
https://www.mikeholt.com/mojonewsar...Protection-Questions-and-Answers~20040708.php
As summary. Power Strips surge protectors which are rated in Joules don't have full data of more important specs.. these power strips are called Type 3. Type 1 is used between the power lines and service entrance and difficult to install because you need to coordinate with the power companies and some don't install these. The LHC definitely has Type 1 SPDs (maybe specially made?). Type II is the most important because they have better specs than most type 3 and you can install this in any breaker panel. What I learned in the above sites is you need to use both Type II and III for optimum protection.
I'll quote the above for these important specifications in choosing real Surge Protector Device (whose data or specs you can't find in the Type 3 power strip surge protectors that is based only on joules).
"
Comparing Type 2 Whole-House Surge Protectors
Because I won’t be installing a Type 1 SPD, I wanted to choose a high quality Type 2 whole-house surge protector to act as my first line of defense. During my comparison, I focused my analysis on
ten important criteria that should always be considered when evaluating a whole-house surge protection device:
Most importantly: is the unit
UL Certified under the UL 1449 3rd Edition and listed as a Transient Voltage Surge Suppressor (TVSS) on the equipment label?
- What Modes of Protection does the surge protector provide? Ideally, a good whole-house suppressor should protect, at the very least, Line to Neutral (L-N), Neutral to Ground (N-G), and Line to Ground (L-G) on both incoming lines.
- What is the Maximum Surge Current Capacity of the surge protector? This number should be measured in kA (thousands of amps) per phase, and essentially represents how big a jolt the unit can survive. It’s an important rating, but it’s not the only number to consider when evaluating a surge protector’s true capabilities (more on this later).
- What is the unit’s Short Circuit Current Rating (SCCR)? This represents the maximum level of short-circuit current that surge protector can withstand.
- What is the Voltage Protective Rating (VPR) for each Mode of Protection? This is sometimes also referred to as clamping voltage. VPR is like a golf score — lower is actually better. The VPR represents how much voltage is still “let through” to your equipment after the surge protector has done its job. When comparing surge protectors head to head, this rating should be compared based on the same Modes of Protection, and taking the Max Surge Current Capacity into consideration.
- What is the Maximum Continuous Operating Voltage (MCOV)? MCOV is probably the most important factor to consider when evaluating a surge protector. Higher is better, and it should never be lower than 115% of the system’s nominal voltage for both L-N and L-L. For example, if evaluating a 120V/240V unit and following the 115% rule, the L-N MCOV should be at least 138V and the L-L MCOV should be at least 276V. If it’s not, the surge protector isn’t any good.
- What is the surge protector’s https://www.nema.org/Products/Documents/nema-enclosure-types.pdf?
- What type of warranty is offered?
- What additional connections (phone, coax) are supported? Even if all your power cords are surge protected, surges can still travel through the coax cable that delivers your cable TV/Internet and satellite signal, or phone lines. A comprehensive power protection strategy should also include protection for these connections, too.
- Does the unit’s price represent a good value? If one unit is more expensive than another unit, is the increased price justified based on the increased features and/or performance?"
Right now I'm looking for a type 2 SPD with lowest Let thru voltage (so called Voltage Protection Rating or clamping voltage) but most seem higher than the Type 3 power strips. This is so because the more capacity is the surge element, the higher the clamping voltage. This is why combining type 2 and 3 may be the best of both worlds as you need cascaded protection and they are called type I, II and III because they are to be used cascaded.
Now back to LHC. What kind of surge protectors do they use? Are they specially made and designed? I haven't seen a power strip surge protection that has type 2 like specs besides joules. Maybe someone can take a look at what kind of surge protectors the LHC computers (PCs and Macs) are connected to? I also plan to visit LHC next year. Can I see the computers and surge protectors they are using?