Discussion Overview
The discussion revolves around the calculation of the maximum RMS voltage that can exist between the near phase conductors of two 3-phase AC transmission line circuits with a phase-to-phase RMS voltage of 100 kV, particularly when the circuits are not in phase. Participants explore the implications of phase relationships, grounding, and voltage measurements in this context.
Discussion Character
- Technical explanation
- Debate/contested
- Mathematical reasoning
Main Points Raised
- Some participants propose that the maximum RMS voltage between the near phase conductors could be 200 kV if they are 180 degrees out of phase, while others challenge this claim.
- There is a discussion about the definition of "near phase conductors" and whether it refers to the physically closest conductors or the phase voltages that are closest.
- Some participants assert that the maximum possible line-to-line voltage is 2 * (100/root3) kV, while others argue that this is incorrect and provide different calculations.
- One participant mentions that if the neutrals of the two systems are joined, the phase-to-phase voltage does not matter, and the phase-to-neutral voltage should be considered instead.
- There is a mention of the peak voltage being relevant for flashover conditions, with calculations provided for peak and RMS values based on phase-to-neutral voltages.
- Some participants express confusion about why a voltmeter would read a line-to-ground voltage instead of a line-to-line voltage when measuring between conductors of different circuits.
- Concerns are raised about the efficiency of grounding and its impact on voltage measurements, particularly when considering the Earth as a ground reference.
Areas of Agreement / Disagreement
Participants do not reach a consensus on the maximum RMS voltage that can exist between the conductors, with multiple competing views and calculations presented. The discussion remains unresolved regarding the implications of grounding and phase relationships.
Contextual Notes
Limitations include assumptions about grounding efficiency, the dependence on phase relationships, and the potential for confusion regarding voltage measurements between different circuits.