Transformer and power question mutiple choice

Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
7 replies · 2K views
Clara Chung
Messages
300
Reaction score
13

Homework Statement


The turns ratio of a transformer is 20:1 step down and the primary coil is connected to a 220V a.c. supply. If the secondary coil is connected to a '36W, 15V' light bulb and the efficiency of the transformer is 80%,find the current in the primary coil.

Homework Equations


P=IV, Ns/Np=Ip/Is

The Attempt at a Solution


I calculate by 36/0.8 = 45 W, 45/220 = 0.204A, which is the answer of D, but the correct answer is B, which is 0.11A, Am I wrong or the is the question wrong?[/B]
 
Physics news on Phys.org
Clara Chung said:

Homework Statement


The turns ratio of a transformer is 20:1 step down and the primary coil is connected to a 220V a.c. supply. If the secondary coil is connected to a '36W, 15V' light bulb and the efficiency of the transformer is 80%,find the current in the primary coil.

Homework Equations


P=IV, Ns/Np=Ip/Is

The Attempt at a Solution


I calculate by 36/0.8 = 45 W, 45/220 = 0.204A, which is the answer of D, but the correct answer is B, which is 0.11A, Am I wrong or the is the question wrong?[/B]
36W is the power rating of the bulb at 15V. The bulb is not getting 15V in this situation, so the power is not 36W. What is the actual operating voltage and resistance of the bulb?
 
Last edited:
cnh1995 said:
36W is the power rating of the bulb at 15V. The bulb is not getting 15V in this situation, so the power is not 36W. What is the actual operating voltage and resistance of the bulb?
That's all the information given. I think the resistance of the bulb can be found by 15^2 / 36= 6.25 ohm
 
Clara Chung said:
That's all the information given. I think the resistance of the bulb can be found by 15^2 / 36= 6.25 ohm
Right. Now what's the voltage across the bulb?
 
cnh1995 said:
Right. Now what's the voltage across the bulb?
Voltage 220/20 = 11V, but isn't there energy lost?
 
Clara Chung said:
but isn't there energy lost?
Yes. That will reduce the secondary voltage. But I think this is how it will be resolved..
If the secondary is kept open and you applied 220V across the primary, you'll get 11V across the secondary, which is the maximum OC voltage, or secondary induced emf E2. Now, if the secondary is loaded, the load voltage will drop. In practice, load voltage should be equal to the secondary induced voltage. A tap changer is used in the primary which will reduce the number of primary turns and hence, secondary induced emf will be increased such that load voltage remains 11V.
 
cnh1995 said:
Yes. That will reduce the secondary voltage. But I think this is how it will be resolved..
If the secondary is kept open and you applied 220V across the primary, you'll get 11V across the secondary, which is the maximum OC voltage, or secondary induced emf E2. Now, if the secondary is loaded, the load voltage will drop. In practice, load voltage should be equal to the secondary induced voltage. A tap changer is used in the primary which will reduce the number of primary turns and hence, secondary induced emf will be increased such that load voltage remains 11V.
thanks a lot with those extra information!:DDDDD now I get the answer by 11^2 / 6.25 =19.4 W, 19.4/0.8 =24.2 W ,24.2/220 = 0.11A :D
 
Clara Chung said:
thanks a lot with those extra information!:DDDDD now I get the answer by 11^2 / 6.25 =19.4 W, 19.4/0.8 =24.2 W ,24.2/220 = 0.11A :D
I'm not sure if my above reasoning is true for such a small system but in large power systems, this is how the load voltage is stabilized. Maybe this transformer has no copper loss and only iron loss is present. So this will not cause any voltage drops and you'll get 11V across the load.