Troubleshooting Strange Noise from 250kw 3 Phase Motor

Click For Summary

Discussion Overview

The discussion revolves around troubleshooting a strange noise from a newly installed 250kw 3-phase motor connected to a variable frequency drive (VFD). Participants explore potential causes of the noise, which occurs intermittently during operation, and consider mechanical and electrical factors that may contribute to the issue.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant describes a noise resembling metal tapping, occurring intermittently when the motor is powered, and notes that the sound disappears when the motor is free-spinning.
  • Another participant questions whether the noise could be indicative of sparking, to which the original poster clarifies it sounds more like a clang.
  • Concerns are raised about the motor's balance, with a suggestion that a professional assessment might be warranted given the motor's power level.
  • Participants discuss the possibility of the VFD being the source of the problem, with one suggesting that the manufacturer should be consulted for both the motor and VFD.
  • The original poster provides details about the current balance across phases and confirms that winding and insulation resistance checks are satisfactory, along with stable VFD output voltages.

Areas of Agreement / Disagreement

Participants express differing views on the potential causes of the noise, with no consensus reached on whether the issue lies with the motor, the VFD, or another factor. The discussion remains unresolved as various hypotheses are presented without definitive conclusions.

Contextual Notes

Participants mention various tests and checks performed on the motor and VFD, but there are limitations in the discussion regarding the thoroughness of mechanical assessments and the potential need for professional evaluation.

lottis
Messages
3
Reaction score
0
Hi guys

I have been testing a brand new 250kw 3 motor wired in delta. I have it connected to a 170 amp vfd with no load for testing. It draws 105 amps at 50hz and is balanced.

Intermittently the motor makes a strange that i have not heard before. It sounds like a spoon taping another spoon, a metal on metal sound tapping at no more than 1 hz off and on. When power is removed and the motor free spins to a stop the sound is gone. I have tried different carrier frequency but it does not make any difference.

Sometimes while making the noise the vfd trips on over current but not on output short circuit. The drive does not show a raise in current before tripping.

The motor has been check for mechanical issues, bearing/loose parts etc and none have been found.

I have tried the motor on another drive (250 amp) and it does not make the noise. I have tried other motors (55kw and smaller) on the vfd and they do not make the noise.

Thanks
 
Engineering news on Phys.org
Does it sound like it could be a spark?
 
No not like a spark, a clang but not loud, spoon on spoon is the best description i can think of. When i heard it first i would have sore there was something loose in the motor, like a balance or something, but nothing loose was found.
If these was a short to Earth or across a winding the vsd would either fault "output short" or "earth fault" i would assume.
 
You are saying the motor is balanced? How did this get checked? At 250KW it is worth the investment to get a professional to assess it. ( there are a lot of tests to consider: http://www.motordiagnostics.com/papers/AC%20Motor%20Testing%20and%20Predictive%20Maintenance.pdf )

Also as a new motor - you can ask, or pay for the manufacturer to come check it out, and then have them certify the warranty is intact, it may cost a few $ now - but to ensure the warranty is valid it may be well worth it.

The VFD could be the problem, again at this power level - I would lean on the manufacturer.
 
Last edited by a moderator:
The current is balanced across each phase +/- 2 amps at 105amps 50hz. The vfd shows the current for each phase and i also checked with a clip on ammeter. I also checked winding resistance and insulation resistance which both check out fine.
The dc bus is stable and the vfd output voltages are also stable and balanced.
 

Similar threads

Replies
7
Views
3K
  • · Replies 27 ·
Replies
27
Views
2K
  • · Replies 19 ·
Replies
19
Views
4K
  • · Replies 27 ·
Replies
27
Views
1K
Replies
23
Views
7K
  • · Replies 14 ·
Replies
14
Views
7K
  • · Replies 15 ·
Replies
15
Views
2K
  • · Replies 15 ·
Replies
15
Views
4K
Replies
0
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K