klmnopq said:
sorry friends
I got more worried
we difference between
1-single phase 2 wire
not as USA and has only 2 wires for current & return??
IN AC current alternate so, Isn't neutral must carrry current &therefore not safe
2-single phase 3 wire
as in USA there is 3 wires and there is the same problem
The debate has got a bit side-tracked, so let's go back to the 'physics' of your question which I'm sure we'll all agree on. Firstly - please re-read my first post - I think you have some basic misunderstandings.
'Dangerous' means current flowing through
you, not through a wire.
You are standing on the ground, then to a reasonable approximation you are grounded, i.e. at what we usually call 0 V. This will be a better approximation if you stand in a pool of water.
The live wire is at, for example, 240 V relative to ground.
The neutral wire is at (give or take) 0 V relative to ground.
If you touch the live wire, there will be a 240 V potential difference between your hand and your feet and hence ground. Your resistance is not that high, so a big current will flow and you'll probably die.
If you touch the neutral wire, there will be (in principle) a 0 V potential difference between your hand and your feet - nothing will happen.
There is a voltage drop of 240 V across the 'load' - this can be your TV or, if nothing is plugged in, air.
If it's your TV, then there is a relatively low resistance, and so there is a current running through the live wire, across the load, through the neutral wire and back into the supply. If the 'load' is air (nothing is plugged in) then the resistance is huge and the current running along this path is essentially zero.
Either way, it doesn't matter - only a current running through
you is dangerous and that depends on the voltage drop across
you (and your resistance).
Having said all that, in practice things might be slightly more complicated, and I wouldn't suggest you still metal objects in the neutral plug.