The discussion revolves around calculating the appropriate cable size for a motor circuit with specific parameters, including a motor power of 0.37kW and a nominal current of 0.8 A. The user has calculated a target current of 1.5 A based on Bahraini regulations but is uncertain about the suitability of a 2.5mm cable, which has a higher current rating than needed. Concerns are raised about the voltage drop calculation, which exceeds the acceptable limit. Participants emphasize the importance of understanding local regulations and installation methods, suggesting that consulting a qualified local electrician is essential for compliance. The user is urged to review their training materials for further guidance on cable calculations.
walidabid
Messages
1
Reaction score
0
Good afternonn,
these are the motor and circuit data:

Motor power: 0.37kW,
Nominal current: I= 0.8 A
voltage: 415 V,
cable length = 80m
ambiant temperature: 50°C
Maximum voltage drop percentage =415*4% =16.6V

According to the Bahraini Regulations:
- temprature factor= 0.89
- core factor (3core cable)= 0.7

This is the calculation I did:
- target current=I/(0.89*0.7)=1,29A ==> 1,5A
when I check the current rated table, the suitable cable section will be 1.5mm but our contractor us a 2.5mm cable (I must verify his choice and prove that it's correct and submit the calculation to our consultant at least tomorrow morning!)

According to the current rated table, we get:
for the cable section: 2.5mm ==> current rating= 33A and Voltage drop /amp/m= 16

but when I calculate the Voltage drop /amp/m for my circuit, I find:
mV= dV*1000/(target current *L)= 16.6V*1000/(1,5A*80m) = 138,33mV >16 (from the table)

Now, what I have to do?
I don,t know how to proceed and finalize the calculation!

I have to make the verification for 20 different equipments with power variying between 0.37 and 48A!
Would you please help me and show me how to continue with the remainder calculation?

Your help is extreamly needed, I'am really blocked.
Thank you

Walid ABID
 
Engineering news on Phys.org
Walid ... your persistance is impressive how many more forums have you posted on?

Like I've mentioned before key to starting a cable calc for an inductive load is knowing what device you are going to protect the cable with as it will have to be able to cope with the inrush of the motor, having said that this is a very small motor and reduces that concern.
Secondly, regulations vary and unless one is knowledgeable of the bahraini electrical Reg's its thus a hard question to answer, we would need a copy of the regions electrical regs to attain the values to be applied.

Third and final you haven't stated what your cable type is nor its installation method, you have just given us values that you provide, we cannot confirm these without knowing you haven't made a mistake.

I assume you must be qualified to be requested to do this, if so you will have done this in your training and i recommend you review your notes or college books.

I can only re-iterate what i said before in that you need to discuss this with a local electrician who has knowledge of local rules and regulation, your tolerances in calcs may be tighter or more liberal than our (UK)... Hope you can appreciate how arkward trying to answer you question is, had you been UK base or even EU then it would have been a quick reply and full explanation.
 
If this calculation needs to be done to local codes, then we cannot help you here. Thread is closed.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...