How to derive the voltages seen in a three phase, Y connected transformer.
Assume a transformer as above, with 230V L-N, and I want to work out the L-L voltage. A phasor diagram will show me that the voltages are 120° out of phase.
(230∠0°) + (230∠120°) = (230cos0 + j230sin0) + (230cos120 + j230sin120) = 230 + (-115 + j199.2)
115 + j199.2 = 230∠60
What I’m looking for is, of course, 400V. I know √3 is involved, but how, and is that an exact calculation or a useful rule of thumb?
This is not homework.
The specified 230 Vac is RMS, so the signal amplitude is 230 * √2 * Sin( ).
Guineafowl said:
Summary:: How to derive the voltages seen in a three phase, Y connected transformer.
How exact do you need to be? In reality, the three phases are never exactly balanced.
Edit: But in the ideal balanced case, ##\sqrt{3}## is exact.
It’s not important, just a theoretical question really.I think I have it worked out. Because, on the phasor diagram, the L-N voltages oscillate either side of the origin (0V), the angle between each phasor and the nearest is actually 60°.
So:
VL-L = (230∠0°) + (230∠60°) = (230) + (230cos60 + j230sin60)
= (230) + (115 + j199.2) = 345 + j199.2
|VL-L| = 398.4 V (∠30°)
EDIT: And because the magnitude of L-L voltage depends on cos 30°, and that of L-N depends on cos 60°, the ratio of voltages (400:230) is similar to the ratio of cos 30:cos 60, which is 1.73, or ≈√3.
When L1 is at zero volts, L2 will be at +60°, and L3 will be at –60°.
The L2 to L3 voltage will then be 2 * Sin( 60° ) = 2 * √(3/4) = √3.
According to vectorial diagram:
Thanks - I see you’ve ignored the (-) sign when adding the vectors. I assumed that if the voltage magnitudes are of opposite sign they subtract. Is that not correct?
Phasors point from the origin, neutral or ground.
The Line to Line voltage is therefore not the sum, it is the voltage difference.