Virginia US Earthquake - Nuclear Plant

AI Thread Summary
A 5.9 magnitude earthquake struck near Mineral, Virginia, affecting the North Anna Nuclear Generating Station, which experienced reactor trips and a loss of offsite power. The plant was upgraded to an alert status, with emergency diesel generators activated to maintain power. Steam was vented as a normal safety procedure during the shutdown, and there was no release of radioactive material reported. Concerns were raised about the spent fuel pools, but it was clarified that they are equipped with backup power systems. Overall, the situation at North Anna was managed effectively, with all systems functioning normally post-event.
QuantumPion
Science Advisor
Messages
902
Reaction score
42
Virginia US Earthquake -- Nuclear Plant

The earthquake that just hit the east coast was centered on Mineral, VA, right where http://en.wikipedia.org/wiki/North_Anna_Nuclear_Generating_Station" is. :rolleyes:
 
Last edited by a moderator:
Engineering news on Phys.org


QuantumPion said:
The earthquake that just hit the east coast was centered on Mineral, VA, right where http://en.wikipedia.org/wiki/North_Anna_Nuclear_Generating_Station" is. :rolleyes:
From reuters:
Traffic lights were knocked out throughout Washington, and units at a nuclear power plant in Virginia went off line by the quake.
 
Last edited by a moderator:


QuantumPion said:
The earthquake that just hit the east coast was centered on Mineral, VA, right where http://en.wikipedia.org/wiki/North_Anna_Nuclear_Generating_Station" is. :rolleyes:

It was 5.9:

http://earthquake.usgs.gov/earthquakes/recenteqsus/Quakes/quakes_all.php

Edit: I am 100 % sure it was 5.9 a while ago. Just seconds ago they have updated it:
MAP 5.8 2011/08/23 17:51:04 37.936 -77.933 6.0 8 km ( 5 mi) SSW of Mineral, VA
So it's now 5.8.

Edit 2: And back to 5.9:
MAP 5.9 2011/08/23 17:51:03 37.975 -77.969 1.0 6 km ( 4 mi) SSE of Louisa, VA

The Operating Basis Earthquake for North Anna is 0.06 g (5.4 on
the Richter Scale) and the Design Basis Earthquake for North Anna is 0.12 g (5.9 on the Richter Scale).
(year 2003)

http://pbadupws.nrc.gov/docs/ML0334/ML033440194.pdf
http://www.expertglossary.com/definition/operating-basis-earthquake-obe
http://www.expertglossary.com/water/definition/design-basis-earthquake-dbe

This means there could be some damage but not for components important for safety.
(fingers crossed) :smile:
(If they have updated their earthquake parameters since 2003 the situation could be even better.)
 
Last edited by a moderator:


North Anna has upgraded the event from an unusual event to an alert. They are currently running on diesels.

They upgraded to an alert due loss of offsite power and having to shut down 1 out of 4 diesels. Everything else appears to be working normally.
 
Last edited:


from http://www.cnn.com/2011/US/08/23/virginia.quake.nuclear/" about North Anna quote:
"Amanda Reidelbach, an emergency management spokeswoman for Louisa County, said the plant vented steam, but there was no release of radioactive material."

Why are they venting steam? WTH? I hope it's just a misreporting.
 
Last edited by a moderator:


shadowncs said:
from http://www.cnn.com/2011/US/08/23/virginia.quake.nuclear/" about North Anna quote:
"Amanda Reidelbach, an emergency management spokeswoman for Louisa County, said the plant vented steam, but there was no release of radioactive material."

Why are they venting steam? WTH? I hope it's just a misreporting.

It's secondary steam, that is a normal occurrence with trips from full power. All the steam that was going to the turbine has to go somewhere! Here's a youtube clip of what it looks like (at Surry, same design as North Anna):

 
Last edited by a moderator:


I am curious about the spent fuel pools. They are not required to have back-up power and North Anna has some 1200 tons of spent fuel.
 


QuantumPion said:
...


Thanks, makes sense. That video is awesome and without you explaining would have been scary as hell.
 
Last edited by a moderator:


ChernobylMary said:
I am curious about the spent fuel pools. They are not required to have back-up power and North Anna has some 1200 tons of spent fuel.

Don't know where you heard that but it is incorrect. The spent fuel pool coolers run off the same backup power as every other safety-related system.
 
  • #10


""Why are they venting steam? ""

The steam generators are vented to atmosphere through relatively small valves in order to carry away decay heat when the turbine and condenser are unavailable as when you are starting up or shutting down the plant , or when the grid goes away.
They're called " Steam Dump to Atmosphere" valves and they're a normal means of temperature control when plant is in between cold shutdown and power operation - a state often called "hot shutdown".. it's very normal.

Another source of steam is the exhaust pipes from the Terry Turbines that supply the makeup water to the steam generators. Ours were adjacent the Steam Dump to Atmosphere silencers.


The water in the steam generators is ultra purified. It is separated from the reactor coolant water by the steam generator tubes.
You could drink that condensed steam except that ultra pure demineralized water gives you a tummy-ache because it is so mineral free it depletes your electrolytes.

Steam is normal. Do not be alarmed by that. The plant is capable of impressive displays of it, and shouild a steam generator relief valve have opened as a result of grid going down - well - that's quite noisy..
The diesels started, they're dumping steam, sounds like they're doing fine.
But a loss of grid doesn't happen every day - so I'm sure it's a bit hectic there just now. Pray everything goes smooth for them.

When you lose grid the turbine piping has to cool down without help of main condensate pumps and that's sometimes a bit noisy. If you've ever heard an old steam heating radiator creak and clank - imagne one with twenty inch pipes.

oops i see it's been handled... that youtube looks to me more like a relief valve than steam dump to atmosphere.. but i don't know that plant.

old jim
 
  • #12


To clarify, the link says that the spent fuel ponds are not required to have back up power, which is not the same as saying they don't have back-up power.
 
  • #13


ChernobylMary said:
To clarify, the link says that the spent fuel ponds are not required to have back up power, which is not the same as saying they don't have back-up power.
That's not entirely correct. That POGO article is a bit misleading.

The pools were originally designed for less fuel, but they re-racked to increase capacity. Originally, the US government was going to take the spent fuel and reprocess. Well, that didn't happen. Then the US DOE was going to build a final repository, and that hasn't happened. Now, utilities like the one operating North Anna put spent fuel in dry storage pending some government resolution.

The site is required to main coolability of the spent fuel pool. That pretty much guarantees that the pool cooling system has backup power. They aren't required to have an exclusive (independent) back up power system - but that doesn't mean that they don't have back up power.

Also, the steam turbine is part of the secondary system which does not contain radioactive water, unless the steam generator tubes leak. North Anna replaced steam generators, Unit 1 in 1993 and Unit 2 in 1995, in order to remove the original SG tubing, which was prone to IGSCC.
 
Last edited:
  • #14
Off-site power appears to have been restored.

http://dom.mediaroom.com/index.php?s=43&item=1015
 
  • #15


FYI

SUBJECT: EMERGENCY DECLARATIONS DUE TO SEISMIC EVENT
At 2:22 p.m. (EDT) on August 23, 2011, NRC entered the Monitoring Mode following the declaration of an ALERT at the North Anna Power Station Units 1 and 2, located in Virginia, at 2:03 p.m. The emergency was declared following a seismic event near the North Anna station. Both North Anna units experienced reactor trips and a loss of all offsite alternating current (AC) power (LOOP) to the emergency buses. The cause of the reactor trips and LOOP are being investigated. The on-site emergency diesel generators (EDGs) initially started and powered the station emergency buses. Subsequently, one of the EDGs was shutdown due to a diesel coolant leak. Another diesel generator was started and all emergency buses continue to be powered.

from - http://pbadupws.nrc.gov/docs/ML1123/ML112360103.pdf

See also - http://www.nrc.gov/reading-rm/doc-collections/event-status/event/en.html#en47181
 
Last edited by a moderator:
  • #16


jim hardy said:
oops i see it's been handled... that youtube looks to me more like a relief valve than steam dump to atmosphere.. but i don't know that plant.

old jim

For a trip where condenser vacuum is lost, full steam flow has to be vented to atmosphere. Condenser vacuum was lost because they lost offsite power.
 
  • #17


QuantumPion said:
For a trip where condenser vacuum is lost, full steam flow has to be vented to atmosphere. Condenser vacuum was lost because they lost offsite power.
Sounds like that's another possible accident problem and offsite dependency that could be avoided with a nuclear plant design based on the Brayton cycle? Yes I know the traditional PWR/BWR doesn't generate high enough temperatures, but other designs could.
 
  • #18


mheslep said:
Sounds like that's another possible accident problem and offsite dependency that could be avoided with a nuclear plant design based on the Brayton cycle? Yes I know the traditional PWR/BWR doesn't generate high enough temperatures, but other designs could.

It's not an accident problem, it's simply the design of the system.

A gas cooled reactor using the Brayton cycle would still have to have a way to dump decay heat on a trip, which would involve venting gas or steam to the atmosphere.

I don't understand your comment about LWR's not generating high enough temperatures for a Brayton cycle. You may be confusing with rankine cycle with superheated steam, which is true that most LWR's cannot produce superheated steam.
 
  • #19


mheslep said:
Sounds like that's another possible accident problem and offsite dependency that could be avoided with a nuclear plant design based on the Brayton cycle? Yes I know the traditional PWR/BWR doesn't generate high enough temperatures, but other designs could.

The reason for having to use the atmosphere as a heat sink is the fact that the ordinary heat sink (=sea / cooling tower) is lost due to stoppage of the condenser cooling pumps. The same goes for any nuclear plant no matter what the cycle used: if you lose the power needed for utilizing the normal heat sink, you need to use an alternative one. In a PWR, the most straightforward alternative heat sink is to blow secondary steam out to the atmosphere and refill the steam generators with fresh water; in a BWR the primary steam is blown to the containment suppression pool and the primary circuit is refilled with fresh weater. An isolation condenser in a BWR makes it possible to use the same decay heat removal method as a PWR.

Needing power for emergency feedwater pumps to replace the lost inventory is not "another" offsite dependency: that's exactly the reason power is needed after the shutdown at all.
 
  • #20


QuantumPion said:
It's not an accident problem, it's simply the design of the system.

A gas cooled reactor using the Brayton cycle would still have to have a way to dump decay heat on a trip, which would involve venting gas or steam to the atmosphere.
The issue here, as I think I understand it, is that with the Rankine a condenser is required and that when the condenser stops the system has no way of continuing to transfer heat to the turbine and removing energy (decay heat) from the system. I don't see the need for a condensor in a Brayton. Thus such a system could could continue running turbine at lower power and bleeding off energy after a reactor trip through the normal path.

I don't understand your comment about LWR's not generating high enough temperatures for a Brayton cycle. You may be confusing with rankine cycle with superheated steam, which is true that most LWR's cannot produce superheated steam.
Well IIRC 300K above ambient is typical for an LWR, where as a practical Brayton might run 700K above ambient. And I'm assuming, most likely, He as the gas. Under what trip circumstances He in a Brayton need to be vented?
 
  • #21


rmattila said:
The reason for having to use the atmosphere as a heat sink is the fact that the ordinary heat sink (=sea / cooling tower) is lost due to stoppage of the condenser cooling pumps. The same goes for any nuclear plant no matter what the cycle used: if you lose the power needed for utilizing the normal heat sink, you need to use an alternative one.
But not necessarily an active one, i.e. active heat removal via pumps. With a molten salt (MS) reactor the idea upon trip is to simply gravity feed the MS to a dump tank, where because of the high temperature (~1000K) it dissipates heat to ambient rapidly and passively. A MSR may have other problems, but a passive, independent shut down is not one of them.
 
  • #22


Thanks for all the great information.

If my understanding is correct, the ground acceleration exceeded the operational basis and this can account for the damage which caused the loss of offsite power.

The area that I know lacks clarity in my mind is the acceleration relative to design basis. It is my understanding that the design basis was only slightly exceeded, and since safety systems are typically over-engineered, there was probably no dangerous structural damage (though I have read of small cracks in the containment building that are not leaking radiation).

furthermore, it is my understanding that this was the strongest quake ever measured in the area, so such an event could not have been predicted by the NRC or the plant designers.

However, now that such a powerful quake is known to be a certainty in the area of the North Anna plant, will it be necessary to either retrofit or decommission the plant?
 
  • #23


swl said:
... the ground acceleration exceeded the operational basis and this can account for the damage which caused the loss of offsite power...

I'm pretty sure that 'ground acceleration' as a single value is not meaningful (in the context of the damage it can cause) without the corresponding frequency. In other words, a high acceleration at a high frequency may be much less damaging than a lesser acceleration at a low frequency. The seismic design is developed from a ground response spectrum, not a single 'g' value. Maybe someone with seismic design expertise could chime in here.
 
  • #24


gmax137 said:
I'm pretty sure that 'ground acceleration' as a single value is not meaningful (in the context of the damage it can cause) without the corresponding frequency. In other words, a high acceleration at a high frequency may be much less damaging than a lesser acceleration at a low frequency. The seismic design is developed from a ground response spectrum, not a single 'g' value. Maybe someone with seismic design expertise could chime in here.

Yes, it turns out the plant was designed to withstand earthquakes with a long wavelength which are characteristic of west-coast earthquakes. However this earthquake was a short wavelength one, which is why the concern over design basis limits. Note that it is only the aux building sensors which may have exceeded the design basis earthquake, not the whole plant.

Another interesting tidbit: the dry storage casks moved several inches. Or from what I've been told, the casks remained stationary while the ground underneath them moved!

Here is a video in the Richmond Times Dispatch showing a brief tour inside the plant, if you've ever been curious what it looks like:

http://www2.timesdispatch.com/news/news-video/2011/sep/02/2/a-post-earthquake-tour-of-north-anna-nuc-99830-vi-30316/
 
Last edited by a moderator:
  • #25


I've been water skiing in lake Anna, adjacent North Anna. It is remarkable how un-intrusive a couple GW of nuclear plant is to lake recreation.
 
  • #26


mheslep said:
I've been water skiing in lake Anna, adjacent North Anna. It is remarkable how un-intrusive a couple GW of nuclear plant is to lake recreation.

So how do you like the lake that wouldn't of been if not for the North Anna NNP?
 
  • #27


Argentum Vulpes said:
So how do you like the lake that wouldn't of been if not for the North Anna NNP?

More, or less than the wildlife, valleys and forests submerged by the lake?
 
  • #29


swl said:
More, or less than the wildlife, valleys and forests submerged by the lake?
Valleys? The lake is 13K acres, mostly shallow and 80' at its deepest. The area is in the Piedmont of Virginia. A large colony of beavers might have accomplished half as much 500 years ago. Still, the lake should be credited to the total area required by the NA plant.
 
  • #31
  • #33


nteresting meeting.

Dominion results show that the single values of 0.06g OBE and 0.12g DBE were exceeded at points along the frequency spectrum of the earthquake. Further their CAV limit was also exceeded (I'm goiung to need to look that up).

Based on the nature and number of questions raised by NRC staff, Dominion is going to be hard pressed to get Unit 1 up and running in the immediate future. NRC still has no idea what form of submittal or documentation they will require from ominion as a prerequisite to restart.

Basically Dominion made a case for restart after they complete inspections and surveilance tests based on the following points:

  1. The earthquake was of short duration and the total energy was low compared to what would be seen from a full OBE or DBE earthquake spectrum
  2. The actual event spectrum was at a level where they believe that simple non-commercial structures would have a safety margin factor of 3 before damage to stuctures would be expected.
  3. Industrial buildings and seismically qualified systems structures and components would have even greater margins. Therefor, they would expect no damage.
  4. Their inspections and tests have not detected any functional damage in non-safety or safety systems.
  5. They have seen no damage in non-safety equipment which would be considered at the lowest levels of standards such as building codes that cover domestic plumbing and waste systems. Dominion believes this gives credence to believe there is no hidden damage in safety systems.
  6. Unit 2 is off line for refueling now and will undergo a complete set of physical and surveilance tests for 100% of the systems and a complete civil engineering assesment of the structures. They believe this will allow restart of Unit 1 pending the same level of testing in 2012 during the next refueling outage.

Dominion managemment and NRC management at the table were talking in terms of restarting unit 1 in a matter of weeks or a few months. The staff that asked questions sounded like they were gearing up for a review that could take much longer. The KK plant in Japan actually had visible damage from an earthquake and was off line for years. Several of the NRC technical staff came to the microphone giving out there wishlists for information that sounded like licensing a new plant. North Anna may be held ransom to resolve the GSI-199 issue and the Fukushima lessons learned.

Only one member of the public spoke - Paul Gunther for those who know the intervenors out there. He raised the issue of buried piping.


Did anyone else listen in? What was your take?
 
  • #34


NUCENG said:
...North Anna may be held ransom to resolve the GSI-199 issue and the Fukushima lessons learned...
I can't see how this NRC action can resolve either beyond the specific case of Dominion's North Anna. US new plant construction is dead, and I can't imagine any major NRC action against the existing 104 US plants.
 
  • #35


I listened for a while although I didn't get many of the jargon (what is level 4 / level 6 status?)
It really sounded to me like there is no damage that would prevent it to go online... one of the important things they proved is that the fuel is undamaged using the chemistry of primary coolant.

There were some issues that were probably not handled very confidently, like they kept on stating that because the non-security related piping was checked and found problem-free then the security related piping was assumed to be problem-free. In an ideal world it makes sense but how about the stress that was in the pipes while earthquake hit?

I also noticed that NRC stated they don't (yet) have a set of requirements for approving online status after a beyond-design-basis event and one of the NRC guys said that the proposed timeline for restarting No1 is too short for them to come up with the proof that No1 can be restarted safely which sounded right to me.

Oh and one more thing - the diesel generator was manually shut down after a coolant leak from a gasket and they felt it's better to shut it down. It is assumed that a torquing technique was misused for that gasket and the other generators didn't exhibit the issue.

Apologies for any mistakes, I was multitasking...
 
  • #36


mheslep said:
I can't see how this NRC action can resolve either beyond the specific case of Dominion's North Anna. US new plant construction is dead, and I can't imagine any major NRC action against the existing 104 US plants.

It happens all the time. NRC is a large group of very smart and educated scientists and engineers. If a staff reviewer has a pet project it can be very difficult to keep them from making a mountain out of a molehill (or in government bureaucracy - an atom into a galaxy). They are very effectively protected by the NRC Differing Professional Opinion process. It goes along with another abusive tactic of "Regulating by Inspection." It is not uncommon for one plant to be forced into taking drastic actions to get a license amendment approved or a restart permission as in the case of North Anna. Once one plant is forced to submit to this blackmail it tends to be easier to force others to fall in step because the "precedent" has been set.

This may sound like sour grapes, but abusive regulation can actually divert attention and resources from other priorities. NRC has not yet concluded the processing of GSI-199 and there is a lot of the cause and lessons from Fukushima that we don't know. I will say for the record that seismic qualification issues needs to be at the top of the priority list, but that may not be good news for North Anna.
 
  • #37


shadowncs said:
I listened for a while although I didn't get many of the jargon (what is level 4 / level 6 status?)
It really sounded to me like there is no damage that would prevent it to go online... one of the important things they proved is that the fuel is undamaged using the chemistry of primary coolant.

There were some issues that were probably not handled very confidently, like they kept on stating that because the non-security related piping was checked and found problem-free then the security related piping was assumed to be problem-free. In an ideal world it makes sense but how about the stress that was in the pipes while earthquake hit?

I also noticed that NRC stated they don't (yet) have a set of requirements for approving online status after a beyond-design-basis event and one of the NRC guys said that the proposed timeline for restarting No1 is too short for them to come up with the proof that No1 can be restarted safely which sounded right to me.

Oh and one more thing - the diesel generator was manually shut down after a coolant leak from a gasket and they felt it's better to shut it down. It is assumed that a torquing technique was misused for that gasket and the other generators didn't exhibit the issue.

Apologies for any mistakes, I was multitasking...

Nope, those are good points. I didn't hear "level4/level6", probably because it made sense in context, do you remember anything about what they were discussing?
 
  • #38


NUCENG said:
Nope, those are good points. I didn't hear "level4/level6", probably because it made sense in context, do you remember anything about what they were discussing?

I've seen them on a slide, I think unit 2 would be in leve 6 (can't remember when) and unit 1 in level 4 meaning ready to restart.
 
  • #39


NUCENG said:
It happens all the time. NRC is a large group of very smart and educated scientists and engineers. If a staff reviewer has a pet project it can be very difficult to keep them from making a mountain out of a molehill (or in government bureaucracy - an atom into a galaxy). They are very effectively protected by the NRC Differing Professional Opinion process. It goes along with another abusive tactic of "Regulating by Inspection." It is not uncommon for one plant to be forced into taking drastic actions to get a license amendment approved or a restart permission as in the case of North Anna. Once one plant is forced to submit to this blackmail it tends to be easier to force others to fall in step because the "precedent" has been set. ...
Oh? Can you name such an instance? I'm not referring to NRC policy updates are universally mandated all the time but have little cost relative the plant itself. This time we are talking about major seismic upgrades of plants and/or spent fuel storage. Universal implantation of such a policy will force some of the marginal operators to simply close. Since 3-Mile Island, when has there been a similar case?
 
  • #40


NUCENG said:
It happens all the time. NRC is a large group of very smart and educated scientists and engineers. If a staff reviewer has a pet project it can be very difficult to keep them from making a mountain out of a molehill (or in government bureaucracy - an atom into a galaxy).
Or making a career out of an issue. :rolleyes:
 
  • #41


shadowncs said:
I've seen them on a slide, I think unit 2 would be in leve 6 (can't remember when) and unit 1 in level 4 meaning ready to restart.

OK, now I remember.

They initially kept Unit 1 in hot standby to keep steam driven safety systems available and the steam generators as a cooling path took Unit 2 to cold shutdown. If I recall they took Unit 2 down further because they had to shut down one of the two diesels. They also needed to enter the Unit 2 containment to retrieve the seismic scratch plates. Later when they discovered they had exceeded design basis peak ground acceleration they were required to take Unit 1 to cold shutdown as well.
 
  • #42


mheslep said:
Oh? Can you name such an instance? I'm not referring to NRC policy updates are universally mandated all the time but have little cost relative the plant itself. This time we are talking about major seismic upgrades of plants and/or spent fuel storage. Universal implantation of such a policy will force some of the marginal operators to simply close. Since 3-Mile Island, when has there been a similar case?

Okay, Millstone spent millions of dollars doing a complete reconstitution of instrument setpoints beyond anything eventually appklied to the rest of the licensees because they were under a confirmatory action letter. The entire control room habitability issue a few years ago cost the industry millions of dollars for an issue that was demonstrably of such low risk that it was ridiculous. NRC is holding up license amendments for BWR plants due to concerns over an issue known as "containment overpressure" that they have granted to other plants previously. And now North Anna may have stepped up to take one for the team. I could probably come up with more examples. It is inevitable when there is a difference of opinion whether the safety improvement is really necessay or justified.

Don't misunderstand me, in each of these cases the industry was asked to perform analysis, conduct tests, or modify the plant in a way that was more conservative than previous requirements. But nuclear plants are not research institutes. They are businesses and have customers who need energy at affordable prices and shareholders that deserve a fair return on investment. There is some truth in the old story that an elephant is a mouse that was designed to the Code of Federal Regulations.

These are not anywhere near the kinds of issues like Fukushima ignoring tsunami data or Davis Besse ignoring the boric acid caked on the RPV head or Maine Yankee modify a safety analysis code to get the results they wanted. Those are clear safety issues that must be remedied and also involve non-compliance with existing regulations and maybe even criminal laws. I am talking about arguments that come down to a question of "better" vs "good enough."

And remember, I repeat - seismic qualification is a legitimate high priority. North Anna is in the sights at a time when we don't yet know what needs to be done.
 
Last edited:
  • #43


""Oh? Can you name such an instance? ""

Long ago in a galaxy far away,,
some aggressive NRC staffer got a pet project called "Pressurized Thermal Shock".
He asserted that if a pressurizer were ever allowed to compeltely fill it would fracture from the sudden insurge of cold water.
Soo,,, Three Mile Island's operators were directed to never let their pressurizer fill.
Soo,,, that fateful morning when the pressurizer started to fill
the operator obediently shut off the pump.

The Three Mile Island accident lies squarely on the shoulders of that NRC staffer.

Is that why you asked
"Since 3-Mile Island, when has there been a similar case?"



old jim
 
Last edited:
  • #44


The case I'm looking for is one where the NRC has mandated that all US reactors make an in place plant change costing on the order of hundreds of millions of dollars or more, which a seismic withstand upgrade, or a fuel storage upgrade is likely to require.
 
  • #45


mheslep said:
The case I'm looking for is one where the NRC has mandated that all US reactors make an in place plant change costing on the order of hundreds of millions of dollars or more, which a seismic withstand upgrade, or a fuel storage upgrade is likely to require.

Post 9/11 security, estimates are $2 BILLION.
 
  • #46


NUCENG said:
Post 9/11 security, estimates are $2 BILLION.

[offtopic]Peanuts. 4 (count'em, four) B-2 bombers. Also, why would a national security problem get solved with the money of private companies, isn't that what the military is for?[/offtopic]
 
  • #47


zapperzero said:
[offtopic]Peanuts. 4 (count'em, four) B-2 bombers. Also, why would a national security problem get solved with the money of private companies, isn't that what the military is for?[/offtopic]

Most of us have been asking that for over ten years.

A couple of thoughts come to mind.

If you have flown recently and seen TSA in action would you want that group in charge of security, We'd be very well protected if terrorists used grandmothers, nuns, and children for the attack.

There is some evidence that the anti-nuclear lobby believes if they can make nuclear energy more expensive they can get rid of it. Unfortunately it simply increases power costs to customers.

Beyond some point iy is a waste, because the security is already going to make the chance of success unappealing for the terrorists. There are many easier softer targets out there.
 
  • #48


NUCENG said:
Most of us have been asking that for over ten years.

A couple of thoughts come to mind.

If you have flown recently and seen TSA in action would you want that group in charge of security, We'd be very well protected if terrorists used grandmothers, nuns, and children for the attack.

There is some evidence that the anti-nuclear lobby believes if they can make nuclear energy more expensive they can get rid of it. Unfortunately it simply increases power costs to customers.

Beyond some point iy is a waste, because the security is already going to make the chance of success unappealing for the terrorists. There are many easier softer targets out there.

I do not live in the US. This has advantages and disadvantages, in that I am never subjected to the gropings of the erstwhile unemployable (most of Europe actually has professionals working airport security), but I WAS herded without comment or recourse to the new X-ray machine on Schipol. Whenever I pass through airports these days, I think of Domodedovo and nothing else. I am actually less scared of flying commercial than pre-9/11, but more scared of the embarkation line, the security check line, the ticketing line, the taxi line. Sitting ducks.

I hope the TSA is not running the NPP security show, I really do.

Re anti-nuclear activists: those that I know of, at least, do believe exactly that. It's not a bright tactic, but it has potential to work great in the long term, unlike most other accessible ones. Some of these guys eat breathe and sleep leftist/anarchist revolutionary warfare. To them all war is economic war. The rising cost of energy actually plays into their hand. Dissent rises, revolution becomes possible. In the meantime, less people are born and more die because of the higher cost of everything.

Re: the point beyond which security is a waste. Unknown, unknowable. We can make fancy guesses wrt economic efficiency of an attack, speculate on likely threats, but it's all smoke and mirrors. Nuts come in a million flavors.
 
  • #49


NUCENG said:
Post 9/11 security, estimates are $2 BILLION.
$19M/plant. That's far less the seismic hardening might cost.
 
  • #50


mheslep said:
$19M/plant. That's far less the seismic hardening might cost.

And your point is?

Has this sort of expenditure been applied to other industries? Has parking been moved back from sports stadii by 100 yards? Are bridges and tunnels being fortifird? Does the security force at chemical plants outnumber their operating staff?

The point is that nuclear plants are frequently subjected to costly modifications and that is what you asked for examples. The industry has done what was required and still produces competitive power. My point is simply that NRC has never been afraid to regulate, unlike, Japan, apparently.
 