VSD output is erratic in no load test only.

  • Thread starter Thread starter ahendawy85
  • Start date Start date
  • Tags Tags
    Load Output Test
Click For Summary
SUMMARY

The forum discussion centers on a field service engineer's troubleshooting of a Variable Speed Drive (VSD) controlling a 3-phase induction motor in an electric submersible pump (ESP) application. During a no-load test at 50 Hz, the V phase exhibited erratic voltage readings, specifically 270 VAC compared to 380 VAC for the U-W phase. Despite static checks indicating that the VSD components, including SCRs and IGBTs, are functioning correctly, the presence of DC voltage at the output raises concerns about potential winding faults or timing issues. The discussion suggests that the V phase may require a small load to stabilize voltage readings.

PREREQUISITES
  • Understanding of Variable Speed Drives (VSD) and their control schemes, particularly constant V/Hz.
  • Knowledge of 3-phase induction motor operation and characteristics.
  • Familiarity with electrical testing tools, including AVO meters and true RMS voltmeters.
  • Basic principles of electrical phasor diagrams and their implications on voltage balance.
NEXT STEPS
  • Investigate the effects of load on VSD performance, specifically regarding phase voltage stability.
  • Learn about SCR failure modes and how to properly test SCRs under load conditions.
  • Research methods for diagnosing winding-to-winding faults in transformers.
  • Examine the use of true RMS voltmeters for measuring AC waveforms with DC components.
USEFUL FOR

This discussion is beneficial for field service engineers, electrical technicians, and anyone involved in the maintenance and troubleshooting of Variable Speed Drives and 3-phase induction motors.

ahendawy85
Messages
1
Reaction score
0
Hi all, I have a problem with a VSD at work that's been confusing.
I am a field service engineer for an oil service company, my line of work is in electric submersible pumps (ESP). The ESP motor is a 3 phase induction motor. Power here is 380V 50 HZ.We were using a VSD for motor control. The control scheme used by this VSD is constant V/HZ.
When performing a no load test the 2nd phase outputted a lower voltage than the other two.
For example when operating the VSD in no load at 50 HZ output frequency, measuring the output terminal phase to phase yields these readings:
U-V 270VAC
V-W 270VAC
U-W 380VAC
Obviously the V phase has a problem so I disconnect power and start doing some static checks on the VSD. I check the converter's SCR's and the inverter's IGBT's they all check out according to the VSD manual. Measured the DC bus and it does have the correct DC voltage value.
The confusing part is when I connected a small motor to the VSD and started testing it it checked out fine, readings are all balanced and the motor runs smoothly.
U-V 370VAC
V-W 380VAC
U-W 379VAC
Tried a no load test after and same thing happened, the V phase is giving erratic readings. And one last observation; the V phase has DC volts in it, when measuring with my AVO meter for DC volts at the output I get those readings:
U-V 80 VDC
V-W 80 VDC
U-W OL

I'm sorry if it took too long to explain, I just can't seem to find the problem. According to my static test results all components are intact. Any thoughts?
 
Engineering news on Phys.org
I'm guessing that your "no load test" actually draws more current then your "small motor test". If so (and I hope I'm not teaching my grandmother to suck eggs here) it looks as if one of the diodes that carries actual current is failing under load. Sorry if that's too basic but without schematics I'm only guessing.
 
if the parts are all good your symptom suggests timing.
but the DC suggests a winding-to-winding fault in transformer

is this drive the same make as your others? I O W is this unusual for that type VSD?

Perhaps it needs a small load to pull the voltages into phase -
imagine in your mind a star phasor diagram
three arrows pointing out from center 120 degrees apart
... if they re-arranged themselves into a tee instead of a star, eg 90 deg apart instead of 120, V would be closer to U and W than it should

but i can't get past the DC in output, that sounds suspicious

you said static checks
one failure mode for SCR's is "transistoring" where they act as a transistor instead of a switch so don't stay on after the gate pulse ends. Therefore in your static check you have to apply enough current to latch the scr, usually 50 ma or less but still several ma, and a dmm won't do that you need an old timey analog on RX1 . A Simpson 260 never let me down... but even it won't latch big SCR's.

good luck - I'm curious about this one keep us posted...
is there a neutral on this thing?
If phase to neutral voltages are okay but phase to phase unbalanced then you KNOW it's timing.

i'd lift leads and check that transformer for winding to winding short,,,,
then swap SCR's from another unit...
then swap SCR firing board

scratching my head with you... especialy about that DC component
i guess the motor shorts out the DC, so it must be coming through some substantial impedance else something would get real hot.

also- some true RMS voltmeters will correctly calculate the DC component of an offset AC waveform like you describe. That could complicate your observations, so check your DMM manual.


old jim
 

Similar threads

  • · Replies 9 ·
Replies
9
Views
4K
  • · Replies 10 ·
Replies
10
Views
5K
  • · Replies 8 ·
Replies
8
Views
7K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 5 ·
Replies
5
Views
4K
  • · Replies 5 ·
Replies
5
Views
4K
Replies
2
Views
2K
  • · Replies 3 ·
Replies
3
Views
5K
  • · Replies 31 ·
2
Replies
31
Views
4K
Replies
1
Views
5K