What are load calculations for a transformer?

AI Thread Summary
Load calculations for a transformer involve determining the maximum current based on its kVA rating and the voltage supplied. For instance, a 3750 kVA transformer on a 44 kV line results in a primary current of approximately 49.2 amps per phase. The distribution of load among transformers depends on their rated power and impedance voltage. Understanding these calculations is crucial for effective transformer operation and load management. For further details, resources like Transformer Riddle No. 27 can be consulted.
shaibaaz3
Messages
2
Reaction score
0
what are load calculations for a transformer?

A 44kv line is distributed into the industry using around 8 transformers 3750kva, 2500kva and 1500kva. What does this mean and what are the load calculations for this? Also how is it distributed?
 
Engineering news on Phys.org


KVA is simply volts times amps. And, it's usually three-phase, so you divide the line-to-line voltage by the square root of 3 to find the line-neutral voltage. So, for example, if you have 44 kV into a 3750 kVA transformer, the maximum current will be 3750 / (44 / SQRT (3)) / 3 = 49.2 amps per phase primary current.
 


thank u...
 


Distribution of load on individual transformers is related to their rated power and impedance voltage. For detail calculation you can refer to Transformer Riddle No. 27 from http://electrical-riddles.com
 
Last edited:
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Back
Top