They are tied together at the distribution transformer as per this website.berkeman said:In the US, this would be a red flag, since Neutral and Earth are tied at the house breaker panel. Are they not tied in your country?
They are tied together at the distribution transformer as per this website.berkeman said:In the US, this would be a red flag, since Neutral and Earth are tied at the house breaker panel. Are they not tied in your country?
At certain ages, that is considered a feature.Wrichik Basu said:my laptop is giving a tingling sensation
How far away is your distribution transformer? How many homes does it power?Wrichik Basu said:They are tied together at the distribution transformer as per this website.
Yeah. I tested five different outlets (all indoor), and all of them are giving around 45 V.Nik_2213 said:40+ Volts, even at fair impedance ?? That's not healthy.
We have a 440V to 220V 3-phase transformer about 100 m from our house, but I am not confident if that is the place where the Earth and neutral are tied together.berkeman said:How far away is your distribution transformer?
Sorry, no idea.berkeman said:How many homes does it power?
Switching off the outlet likely just disconnects the Hot lead, not Neutral or Ground.Wrichik Basu said:And another thing: the tingling doesn't go until I unplug the charger from the outlet. Simply switching off the outlet doesn't work.
Remember to always quote what you're responding to...DaveC426913 said:Nope.
BTW, don't ask me how I know that...berkeman said:some house outlets (in the US) do have wall switches that switch the Hot/Line wire to the outlet.

Secrets of the EMT!berkeman said:BTW, don't ask me how I know that...![]()
No, I wish. More like moving into a new place and thinking, "I wonder why this outlet doesn't work sometimes. Hey it works! Ack, it stopped working."jedishrfu said:Secrets of the EMT!

Same situation here, very confusing until tracked down! It turns out the standards this building was wired to required either a switched overhead light or a switched outlet.berkeman said:No, I wish. More like moving into a new place and thinking, "I wonder why this outlet doesn't work sometimes. Hey it works! Ack, it stopped working."![]()
That reminds me of a Steven Wright story.berkeman said:No, I wish. More like moving into a new place and thinking, "I wonder why this outlet doesn't work sometimes. Hey it works! Ack, it stopped working."![]()
I had a light switch in my house that didn't do anything. Every time I walked past, I would flip it. Last week I got a phone call. It was a woman in Germany. She said, "Cut it out."
It's a 3-pin plug that has L and N written on it. Probably it's not meant to be plugged in with L and N reversed.Tom.G said:@Wrichik Basu
If the power plug is not polarized, try inserting it the other way in the wall outlet.
This is a useful feature. In our living room there is a receptacle that can be turned on by a switch. You can walk into the room and turn on a floor lamp. I've wired three outlets in my outside shop to work the same way so that three fluorescent lights turn on from a wall switch. It's also possible to wire a receptacle so that one half is switched and the other half is always hot.berkeman said:If you're responding to my switch comment, some house outlets (in the US) do have wall switches that switch the Hot/Line wire to the outlet.
Definitely not. Most likely L = line (or hot) and N = neutral. The third pin, all by itself would be ground or earth.Wrichik Basu said:It's a 3-pin plug that has L and N written on it. Probably it's not meant to be plugged in with L and N reversed.
I can buy it, but is it actually required? As pointed out by @berkeman, ~45V between Earth and neutral lines means a faulty earthing connection.Mark44 said:The polarity tester that @berkeman showed in post #26 is a very handy tool to have. Just plug it in, and the lights on it will show if the receptacle is wired correctly.

It would be useful to check the other outlets in your house, and they are quite inexpensive. The one in your link works out to just under USD3.00.Wrichik Basu said:I can buy it, but is it actually required?
Or maybe a short between the hot wire and neutral. Whatever, the tester has several lights on it that can pinpoint exactly which wires aren't wired correctly.Wrichik Basu said:As pointed out by @berkeman, ~45V between Earth and neutral lines means a faulty earthing connection.
With the charger unplugged from the wall, what do you get for the resistance from each of the 3 pins of the plug to the outer and inner barrels of that charger?Wrichik Basu said:Also, I wanted to mention that yesterday I got a good shock by touching the negative pin of the laptop charger's DC jack.
This may be true in the US but is certainly not true everywhere.Mark44 said:It's also possible to wire a receptacle so that one half is switched and the other half is always hot.
No, in India (as well as the UK and most of the rest of the world except the US), 'L' stands for 'Live'. You should appreciate that the US 120V dual phase system means that things work very differently in the US (and the few other countries with similar systems).Mark44 said:Definitely not. Most likely L = line (or hot) and N = neutral.
No, ~45V between Earth and neutral means a faulty or overloaded neutral path anywhere in the system.Wrichik Basu said:~45V between Earth and neutral lines means a faulty earthing connection.
This is exceedingly dangerous: you must get this fixed immediately. Ideally, in order to protect against this you should install a Residual Current Device(s): in fact Wikipedia suggests that in India you should already have this. Clearly if you do then it is not working properly (it should trip when any current over a tiny threshold which is not enough to burn you flows to Earth except via the Neutral wire).Wrichik Basu said:Also, I wanted to mention that yesterday I got a good shock by touching the negative pin of the laptop charger's DC jack. I have touched that terminal thousands of time in the past without any problem. But yesterday, don't know what happened. Maybe the potential difference between Earth and neutral caused that shock? Not sure. I've got a black mark on my finger.
Do not confuse earthing (i.e. connection to Earth of the Earth wire - this is not what is wrong) with grounding or bonding of the Neutral return path).Wrichik Basu said:I will have to call a certified electrician to fix the earthing, but, as almost everyone knows, the second wave of the pandemic has hit us hard, and I don't want to call anyone unless absolutely necessary because these people are just not following any COVID-19 protocols.
No, that would blow the fuse or trip the overcurrent device (or melt the wiring if the fuse is overrated).Mark44 said:Or maybe a short between the hot wire and neutral.
Yes, the neutral return path is faulty or underrated. As you have discovered, 45V is sufficient to cause a nasty shock: if the current passes through the chest it could cause cardiac arrest. Depending on the cause, this could also cause a fire.Wrichik Basu said:I found something very interesting: We have one air conditioner of 1.5 ton in our house. When the above readings were taken, it was switched on. Later, after switching it off, I tested again, and the voltage b/w Earth and neutral became 23 V. Still much higher than normal, but lesser than the previous reading. When I switched on the AC again, the value climbed up to ≈ 44 V. I chose four different outlets in the house; same observation in each of them. Any idea why this fluctuation is occurring?
Well, "Live" and "Line" basically mean the same thing.pbuk said:'L' stands for 'Live'
My multimeter shows 0.L when the two leads are separated, so that means open circuit, or infinite resistance. Keeping that in mind,berkeman said:With the charger unplugged from the wall, what do you get for the resistance from each of the 3 pins of the plug to the outer and inner barrels of that charger?
Terminal 1 (in plug) | Terminal 2 (barrel in DC jack) | Value (in Ω) |
|---|---|---|
Live | Outer | ∞ |
Neutral | Outer | ∞ |
Earth | Outer | 1.011k |
Live | Inner | ∞ |
Neutral | Inner | ∞ |
Earth | Inner | 2.093k |
Okay then, I will buy one.Mark44 said:the tester has several lights on it that can pinpoint exactly which wires aren't wired correctly.
Okay, that explains it.pbuk said:No, ~45V between Earth and neutral means a faulty or overloaded neutral path anywhere in the system.
In that case, our "regular" electrician won't be able to find the fault perhaps, and I have to call the power supply company. This just got a lot complicated.pbuk said:The cause could be a connection that has become unreliable, a new load that has been attached or a fault in your ACU. If your neutral bonding is shared with another home or homes (illegal in many areas) the fault may be nothing to do with you
Nope, we don't have a RCCB. Our main circuit breaker is a simple 20A fuse. It was supposed to be replaced by a 64A C-curve DP MCB last year, but then lockdown started and the work hasn't been done.pbuk said:Ideally, in order to protect against this you should install a Residual Current Device(s): in fact Wikipedia suggests that in India you should already have this.
Perhaps, although the fact that your ACU which I'd guess draws about 10A accounts for about half the neutral return voltage indicates that the problem is fairly local.Wrichik Basu said:In that case, our "regular" electrician won't be able to find the fault perhaps, and I have to call the power supply company. This just got a lot complicated.