What is the difference between a switch leg and a hot leg?

  • Thread starter Thread starter sevensages
  • Start date Start date
Click For Summary
A hot leg provides continuous power directly from the electrical panel to a load, while a switch leg connects to a switch first, controlling the power to the load. The discussion centers around whether a new electrical outlet can be installed on the same circuit as a ceiling fan, depending on whether the fan operates on a hot leg or a switch leg. If the ceiling fan runs on a switch leg, the outlet would also be controlled by the same switch, which may not be desirable for continuous use. Participants emphasize the importance of proper wiring practices and suggest consulting a professional electrician for safety and code compliance. Understanding the distinction between hot and switch legs is crucial for effective electrical installation.
sevensages
Messages
177
Reaction score
48
TL;DR
What is the difference between a switch leg and a hot leg?

How can I tell if my ceiling fan is run off a switch leg or a hot leg?
I would like to get an electrical outlet installed in my enclosed back porch. I am a long distance trucker. Recently I was in the Driver's Lounge at a truckstop talking to another trucker who used to be an electrician about how I would like to get an electrical outlet installed in my enclosed back porch. There is a ceiling fan in my enclosed back porch. I asked this other trucker if I could get the new electrical outlet that I want to install in the wall of my back porch to run off the same circuit as my ceiling fan. He said that i could only get this new electrical outlet to run off the same circuit as the ceiling fan if the circuit that the ceiling fan runs off of is a hot leg. He said that if my ceiling fan runs off of a switch leg, then I cannot have the new electrical outlet run off the same circuit as the ceiling fan. I have two questions about this:

1# What is the difference between a switch leg and a hot leg? My speculation is that if the ceiling fan runs off a hot leg, that means that there are TWO HOT wires going to the ceiling fan. And my speculation is that if the ceiling fan runs off a switch leg, that means that one of the two wires that goes to the ceiling fan is a hot leg, and the other leg that goes to the ceiling fan is a neutral wire. Is my speculation correct?

2# How can I tell if the circuit that my ceiling fan runs off of is a hot leg or a switch leg? I am totally baffled as to how to tell whether my ceiling fan runs off a hot leg or a switch leg. I mean I just don't have the first clue of how to find this out.
 
Engineering news on Phys.org
sevensages said:
1# What is the difference between a switch leg and a hot leg? My speculation is that if the ceiling fan runs off a hot leg, that means that there are TWO HOT wires going to the ceiling fan. And my speculation is that if the ceiling fan runs off a switch leg, that means that one of the two wires that goes to the ceiling fan is a hot leg, and the other leg that goes to the ceiling fan is a neutral wire. Is my speculation correct?
Donning your Googles will help.

A hot leg runs directly from the panel to the load
A switch leg runs to a switch first, then to the load.

sevensages said:
2# How can I tell if the circuit that my ceiling fan runs off of is a hot leg or a switch leg? I am totally baffled as to how to tell whether my ceiling fan runs off a hot leg or a switch leg. I mean I just don't have the first clue of how to find this out.
Are there any mysterious switches on walls in or near the room?
 
DaveC426913 said:
Donning your Googles will help.

A hot leg runs directly from the panel to the load
A switch leg runs to a switch first, then to the load.


Are there any mysterious switches on walls in or near the room?

There is a light switch for the ceiling fan light in my back porch that is in my dining room. I don't know if I would use the word mysterious to describe the light switch though. It is just a light switch.
 
sevensages said:
There is a light switch for the ceiling fan light in my back porch that is in my dining room. I don't know if I would use the word mysterious to describe the light switch though. It is just a light switch.

It is not clear how many fans you have - or will have - or where they are located.

You Say you want to install a ceiling fan in your back porch but it seems you now say there is a ceiling fan in your back porch that has a switch in the dining room.

*the "mysterious" aspect would be having a switch that doesn't seem to do anything at the moment, since - as it was originally understood - there was nothing hooked up to it out on the porch.)


Anyway, are you having this line for the ceiling fan installed by a pro? If so, it won't be a problem. He will likely run a new line from the panel.

If you are planning on installing the line yourself, are you sure that's a good idea?
 
DaveC426913 said:
It is not clear how many fans you have - or will have - or where they are located.

You Say you want to install a ceiling fan in your back porch but it seems you now say there is a ceiling fan in your back porch that has a switch in the dining room.
No. Please read the OP again
I did not say that I want to install a ceiling fan in my back porch. I said that I want to install an electrical outlet in my back porch.

There is a ceiling fan in my back porch that has a switch in the dining room.



DaveC426913 said:
Anyway, are you having this line for the ceiling fan installed by a pro? If so, it won't be a problem. He will likely run a new line from the panel.

If you are planning on installing the line yourself, are you sure that's a good idea?
I haven't made up my mind yet whether I want to install the electrical outlet myself or hire an electrician.
 
  • Like
Likes DaveC426913
If the circuit was installed correctly the wire to the fan is not hot unless the switch is on. You could extend the circuit to an outlet if you are OK with the switch turning the outlet on and off. Otherwise you'd need to wire it from upstream of the switch.
 
DaveC, you edited post #4 and added the quote below after I made post #5. I would like to address that.

DaveC426913 said:
*the "mysterious" aspect would be having a switch that doesn't seem to do anything at the moment, since - as it was originally understood - there was nothing hooked up to it out on the porch.)

As I said in the OP, the ceiling fan in my back porch has been in my back porch since I bought this house. The light switch in the dining room was never mysterious to me because it has always controlled the ceiling fan light.
 
russ_watters said:
If the circuit was installed correctly the wire to the fan is not hot unless the switch is on. You could extend the circuit to an outlet if you are OK with the switch turning the outlet on and off. Otherwise you'd need to wire it from upstream of the switch.

To me, your second and third sentences seem to contradict what the trucker told me. That doesn't necessarily mean that you are wrong.

Based on the description of a switch leg that Dave told me in post #2, i believe that my ceiling fan light runs off a switch leg (not a hot leg) because the light switch in the dining room turns on and off the ceiling fan light. My understanding of your statement "You could extend the circuit to an outlet if you are OK with the switch turning the outlet on and off" is that you are telling me that I could extend the switch leg that goes to the ceiling fan light to the outlet if I am ok with the light switch in the dining room turning the outlet on and off. But the trucker told me that if the ceiling fan light is a switch leg, then the circuit could not be run from the ceiling fan. Do you see the contradiction? Maybe the trucker told me that if the ceiling fan light was on a switch leg, the circuit would have to run directly from the switch to the outlet because he thought it would be undesirable to have the light switch in the dining room turning the outlet on and off. Do you agree ?

Edited to add: I don't understand why you wrote "Otherwise, you would need to wire it from upstream of the switch."

Couldn't I wire it from right at the switch (not upstream of the switch)?
 
Last edited:
sevensages said:
DaveC, you edited post #4 and added the quote below after I made post #5. I would like to address that.



As I said in the OP, the ceiling fan in my back porch has been in my back porch since I bought this house. The light switch in the dining room was never mysterious to me because it has always controlled the ceiling fan light.
Right. Got it now.

So you could install an outlet on the same line, but the outlet would be subject to the whims of the wall switch.
 
  • #10
sevensages said:
But the trucker told me that if the ceiling fan light is a switch leg, then the circuit could not be run from the ceiling fan.
I'd say "could not" was an over-reach.

You could do it, it just might not have the effect you desire.


I have this in my own house. I have an "after-market" sun room (i.e. previous owner built it). It has electrical outlets that are controlled by the light switch inside the back door of the house proper.
This is not desirable because I keep plants in the sunroom over the winter and, if the light switch gets turned off, all the lights and heaters in the sun room go off. It doesn't take long for them to freeze.
 
  • #11
DaveC426913 said:
Right. Got it now.

So you could install an outlet on the same line, but the outlet would be subject to the whims of the wall switch.

I gotcha. Yeah, that would be somewhat undesirable to run the outlets off of the switch leg to the ceiling fan light because I would like to plug battery chargers for cordless drills and other cordless tools in the back porch and leave them charging there overnight. If I ran the outlet off of the switch leg, charging up the batteries in battery chargers in those electrical outlets would entail leaving my ceiling fan light on all night, which is quite undesirable. I will have the new electrical outlet run off the switch, not the switch leg for the ceiling fan light.
 
  • #12
By the way, I edited post #8 at the very end of the post. If you have already read my post #8, please read the edit at the end of post #8.

DaveC, I invite you to answer the question at the end of post #8 in addition to Russ.
 
  • #13
sevensages said:
Couldn't I wire it from right at the switch (not upstream of the switch)?

There's "you could" and "you should".

As in: you should not be running a new line out of a switch box like that. I am almost certain it is against code.

Most of what you are going to encounter here is going to be less about "what will work for you" and more about "what will meet code" - which, by the way, can be considered synonymous with "won't void your insurance if it's ever discovered".

You don't know what might be plugged in to that outlet down-the-line, which is why it ought to be on its own circuit.

But at least you should not split off a switchbox like that; you would install a new octagon - upstream of the switch - and split off there to the two loads. Still not good, but not as bad as splitting from a switchbox.

Caveat: I am no electrician.

I'll leave it to Russ to weigh in.
 
  • #14
sevensages said:
hire an electrician.
Yes, do this. Your question(s) are pretty basic for electrical work.
If you haven't (yet) taken the initiative to map out your existing wiring and understand where to connect things, then I fear there are other things that you need to learn that you might not.
If you are going to do it yourself, then you need to put more effort into studying this subject instead of asking basic questions on SM and getting answers from people you don't know.
 
  • #15
sevensages said:
To me, your second and third sentences seem to contradict what the trucker told me. That doesn't necessarily mean that you are wrong....

Maybe the trucker told me that if the ceiling fan light was on a switch leg, the circuit would have to run directly from the switch to the outlet because he thought it would be undesirable to have the light switch in the dining room turning the outlet on and off. Do you agree ?
Yes: It's not a contradiction, it's a choice. Your choice.
Edited to add: I don't understand why you wrote "Otherwise, you would need to wire it from upstream of the switch."

Couldn't I wire it from right at the switch (not upstream of the switch)?
On the upstream side of the switch, yes.
 
  • #16
The term switch leg I am familiar with and what is described in post #2 contradicts it.
-
To source power for an outlet you need to be sure the box you are hooking into has both a hot and a neutral. A switch leg does not. Where I come from a switch leg is a pair of wires coming from the ceiling light box that this pair of wires interrupts the hot. In that case there is a constant hot and neutral in the ceiling box.
-
The term hot leg I'm not familiar with.
 
  • #17
Averagesupernova said:
To source power for an outlet you need to be sure the box you are hooking into has both a hot and a neutral. A switch leg does not. Where I come from a switch leg is a pair of wires coming from the ceiling light box that this pair of wires interrupts the hot. In that case there is a constant hot and neutral in the ceiling box.
Where does the "switch" part come in to that definition?
 
  • #18
DaveC426913 said:
Where does the "switch" part come in to that definition?
I didn't think I needed to point out the obvious. It hooks to the two wires at the end of the switch leg.
 
  • #19
This diagram contains a switch leg:
images.webp

This one does not:
images (1).webp
 
  • #20
Averagesupernova said:
I didn't think I needed to point out the obvious.
It is obvious to someone who is familiar with it. Clearly, it is unfamiliar.

Averagesupernova said:
It hooks to the two wires at the end of the switch leg.
OK, so it sounds like you're talking about the same setup as us, just describing it from a different point of view.

But yeah, your diagrams are a good visual aid.

As a non-electrician, visualizing it does not come easy. I've combined the illos into one to highlight the differences.

Is this correct?
1746715626544.webp


Functionally, they are the same thing - inasmuch as the only circuitry difference is that, in the left diagram the black-to-white wire is longer, whereas it is zero length in the right diagram.

Question for clarity: do both diagrams contain a hot leg? i.e. a hot leg describes a part of a circuit, not a type of circuit.
 
Last edited:
  • #21
DaveC426913 said:
OK, so it sounds like you're talking about the same setup, just describing it from a different point of view.


DaveC426913 said:
A switch leg runs to a switch first, then to the load.
No.
 
  • #22
Averagesupernova said:
This diagram contains a switch leg:
View attachment 360801
Ahh, I get it. So is it sometimes done that way due to proximity of the ceiling box to the source? If you run the source through the switch box you'd end up with more wiring in that case.
 
  • #23
Averagesupernova said:
No.
I see I was in error at first, or at least I was sloppy in my description.

I've amended post 20 with a diagram based on yours. Do I have it right?
 
  • #24
@DaveC426913 yes basically correct. Notice in the first diagram I posted the little circles drawn. They depict the wires going into a cable sheath or conduit. Basically the entrance/exit to the box. The one diagram you posted has a circle out in the middle of nowhere. A bit confusing but the colors are done right concerning a switch leg.
-
Now here's something that throws a monkey wrench into the gears concerning the terminology. Many places now it is necessary to have a neutral at the switch to power occupancy sensing switches. In the case of a switch leg we just run three conductor cable. And of course now we can continue the circuit on from there. So is it still considered a switch leg? If we chose to wire it so the source stops at the switch first we could eliminate the run with three wires and just use two. But in that case there won't be a constant hot in the ceiling and some day we might want a ceiling fan. So, best to run three wires between the switch and load and the source goes to whichever box it is convenient.
 
  • #25
Averagesupernova said:
@DaveC426913 yes basically correct. Notice in the first diagram I posted the little circles drawn. They depict the wires going into a cable sheath or conduit. Basically the entrance/exit to the box. The one diagram you posted has a circle out in the middle of nowhere. A bit confusing but the colors are done right concerning a switch leg.

The circles are electrical boxes. One for the switch, one for the receptacle and one octagon for the split. (In your diagram you have a Marrette connector, but any connection like that would be in a box, not loose in the wall.)

The only functional difference between the two setups is that there is no split, therefore no octagon box.

Averagesupernova said:
Now here's something that throws a monkey wrench into the gears concerning the terminology. Many places now it is necessary to have a neutral at the switch to power occupancy sensing switches. In the case of a switch leg we just run three conductor cable. And of course now we can continue the circuit on from there. So is it still considered a switch leg? If we chose to wire it so the source stops at the switch first we could eliminate the run with three wires and just use two. But in that case there won't be a constant hot in the ceiling and some day we might want a ceiling fan. So, best to run three wires between the switch and load and the source goes to whichever box it is convenient.
Over my head. o0)
 
  • #26
DaveC426913 said:
The circles are electrical boxes. One for the switch, one for the receptacle and one octagon for the split.
I've never seen that in the wild. It would never be done in residential work since each box has to be accessible. Can't bury one in a wall or ceiling. Happy homeowner will not want boxes with blank covers.
-
Also a good way to irritate the drywallers. I've been asked by a drywaller "What are these boxes for!?!?!?!" in less than pleasant tone. Yep, the dumb electricians put in extra boxes for you to cut around just because.
 
  • #27
Averagesupernova said:
I've never seen that in the wild. It would never be done in residential work since each box has to be accessible. Can't bury one in a wall or ceiling. Happy homeowner will not want boxes with blank covers.
-
Also a good way to irritate the drywallers. I've been asked by a drywaller "What are these boxes for!?!?!?!" in less than pleasant tone. Yep, the dumb electricians put in extra boxes for you to cut around just because.
So where would you put the split, if not in a box? Just loose in the wall cavity? Or is that within the light receptacle box?
 
  • #28
DaveC426913 said:
So where would you put the split, if not in a box? Just loose in the wall cavity? Or is that within the light receptacle box?
NEVER loose in the wall.*

You would run the source wire all the way to one of the boxes that had a function (switch, light, etc.) first. This could also be a box that was present for some other reason, like an outlet.

*In the US there is an approved in wall splice fitting. But they are expensive and hard to buy because no one uses them. You'd only do this for remodeling work, I think. Never in commercial or industrial buildings.
 
Last edited:
  • #29
BTW, you will sometimes see junction boxes in attics and crawl spaces, which are accessible. But again, really only in remodeling, I think.
 
  • #30
DaveE said:
NEVER loose in the wall.*

You would run the source wire all the way to one of the boxes that had a function (switch, light, etc.) first. This could also be a box that was present for some other reason, like an outlet.
Ah, so this:
1746722730425.webp



It sounds like Russ has hit on it.
You might use the first configuration if the line is nearest the light receptacle, whereas you'd use the second configuration if the line is nearest the switch.
 
  • Like
Likes russ_watters, DaveE and Averagesupernova

Similar threads

  • · Replies 2 ·
Replies
2
Views
1K
Replies
24
Views
2K
Replies
18
Views
2K
Replies
33
Views
4K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 49 ·
2
Replies
49
Views
4K
  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 9 ·
Replies
9
Views
12K
  • · Replies 13 ·
Replies
13
Views
5K
  • · Replies 25 ·
Replies
25
Views
6K