What Is the Shear Strength of a Cut I-Beam in a Cantilevered Structure?

AI Thread Summary
The discussion centers on the shear strength of a cut I-beam in a cantilevered structure for a two-story townhome project. The structural engineer specified a W10x19 beam that will span 10 feet over a garage, with the load resting solely on the top flange. Key considerations include controlling buckling of the top flange, calculating design loads, and assessing bearing stress at support points. The lower flange and web are cut back to fit between the foundation, leaving the top flange to support the entire weight of the structure. The AISC Steel Construction Manual is recommended as a resource for further calculations and understanding of the beam's performance.
vernierdesign
Messages
2
Reaction score
0
Hello, I'm in the process of building a 2 story townhome project and had a question on a beam. The structural engineer is calling for a cut I-beam on top foundation which spans over the garage (10') and the load will be placed on just the top flange (see attached). The structure will cantilever 6' over this beam and I'm curious on the shear strength of the beam with this type of alteration.
 
Engineering news on Phys.org
There is no attached ...
In a span, buckling of the top flange must be controlled.
In a cantilever, buckling of the lower flange must be controlled.
 
  • Like
Likes Bystander
If you want to cross check the engineer, you need to calculate the following:

1) The design loads on the beam. Your building code specifies design loads and safety factors, which could be snow, wind, earthquake, equipment, people, etc.
2) Buckling of whichever flange is in compression.
3) Yielding of flanges.
4) Web crippling.
5) Bearing stress at support points.
6) Shear in web.
7) Deflection, and its effect on the structure.
8) Strength of connections.

A good resource is the AISC Steel Construction Manual. Note that this manual assumes a background consisting of several engineering courses, so our ability to help you is quite limited. Especially in the context of an internet forum.
 
Thank you for your response... I know there's many variables to this question but I'm trying to just focus on the bearing stress of the top flange.

The pic that I attempted to download shows that the lower flange and web is cut back 8" on both sides of the beam so the beam would fit between the foundation over the garage entrance. Then top flange will extend 8" over to top of the foundation. The top flange will be welded to a beam plate that's embedded in the concrete on the top of the foundation. There will be no support under the web/lower flange. So, the the weight of the structure will essentially resting on the top flange. The engineer is calling out for a w10x19 beam.

Any thoughts on this would be greatly appreciated.
 
vernierdesign said:
The pic that I attempted to download
Try the "Attach files" link below the Edit window to upload a JPG or PDF file with the image.

You may also be able to drag and drop the image into the Edit window as another way to attach it to a Reply.
 
Thread 'I need a concave mirror with a focal length length of 150 feet'
I need to cut down a 3 year old dead tree from top down so tree causes no damage with small pieces falling. I need a mirror with a focal length of 150 ft. 12" diameter to 36" diameter will work good but I can't think of any easy way to build it. Nothing like this for sale on Ebay. I have a 30" Fresnel lens that I use to burn stumps it works great. Tree service wants $2000.
Hi all, i have some questions about the tesla turbine: is a tesla turbine more efficient than a steam engine or a stirling engine ? about the discs of the tesla turbine warping because of the high speed rotations; does running the engine on a lower speed solve that or will the discs warp anyway after time ? what is the difference in efficiency between the tesla turbine running at high speed and running it at a lower speed ( as fast as possible but low enough to not warp de discs) and: i...