Anchoring battery racks to both the floor and wall is discouraged due to the potential for relative movement during earthquakes, which can lead to structural failure of the rack. The National Electrical Safety Code (NESC) suggests this practice to prevent damage during seismic events. If the wall and floor shift independently, a dual anchoring could result in tearing apart the rack. Conversely, a robust rack could impede wall movement, potentially damaging the building itself. Understanding these dynamics is crucial for ensuring safety in earthquake-prone areas.
MitYeltu
Messages
8
Reaction score
0
I am working on putting a new battery rack into a substation. I was re-reading the NESC and came across section 143. This section suggests it is not recommended to anchor my rack to both the floor and the wall. Can anyone explain why this is not recommended?
 
Engineering news on Phys.org
If you are in an earthquake zone, the wall and floor could move relative to each other in minor quakes.
This could tear your rack apart if it was connected to both of them.
 
vk6kro said:
If you are in an earthquake zone, the wall and floor could move relative to each other in minor quakes.
This could tear your rack apart if it was connected to both of them.

Brilliant. I learn something new every dang day here on the PF.
 
That makes sense. I hadn't thought about that, but I agree now that I have. Now, don't be angry for my asking it this way, but, is that the NESC reason for not attaching it to both? I have not seen that specified anywhere.
 
It could work the other way, too.

If the rack was very strong, it could stop part of the wall moving and cause damage to the building.
 
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...