Will a 5A Fuse Melt with 20 Bulbs in Parallel?

Click For Summary

Discussion Overview

The discussion revolves around the behavior of a 5A fuse when connected to multiple incandescent bulbs in parallel. Participants explore the implications of current ratings, the characteristics of fuses, and the nature of incandescent loads, focusing on whether the fuse will melt under specific conditions.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Homework-related

Main Points Raised

  • Some participants note that a 5A fuse may not blow immediately at 5A due to the time characteristics of fuses, which can sustain certain currents for limited periods.
  • There is a discussion about the inrush current of incandescent bulbs, which can be significantly higher than their rated current until the filaments heat up.
  • One participant suggests that the fuse may blow at currents slightly above or below 5A, indicating uncertainty about the exact threshold for melting.
  • Another participant emphasizes the importance of considering the thermal mass of the fuse element, which affects its time-to-melt characteristics.
  • Concerns are raised about the maximum number of bulbs that can be connected without risking the fuse blowing, with one participant proposing that 19 bulbs might be a safer limit.
  • There is a mention of the need to protect wiring rather than just the bulbs themselves, highlighting the broader context of fuse applications.

Areas of Agreement / Disagreement

Participants express differing views on the behavior of the fuse under specific conditions, with no consensus reached on the exact number of bulbs that can be safely connected without blowing the fuse. The discussion remains unresolved regarding the precise implications of current ratings and fuse characteristics.

Contextual Notes

Participants acknowledge that the actual current drawn by the bulbs may vary, and the assumptions about the fuse's behavior depend on specific conditions and definitions that are not fully resolved in the discussion.

Who May Find This Useful

This discussion may be of interest to individuals studying electrical engineering, physics, or anyone involved in practical applications of electrical circuits and fuse characteristics.

sgstudent
Messages
726
Reaction score
3
If I have a fuse with a rating if 5A and when I connect 10 bulbs in parallel, the current flowing will be 5A. When this happens will the fuse melt? Or does the current have to be more than 5A for it to melt?
 
Physics news on Phys.org
You'll need to read the spec of the fuse. Fuses have time periods over which they'll sustain a given current. In the case of bulbs, there will be a higher current when you switch them on (until the resistance of the bulbs increases as they get hot), so you'll almost certainly likely burn out a 5A quick-blow fuse if it is 5A during normal operation.

Fuses are coarse devices that help prevent (but do not prevent) further damage and safety issues in fault conditions. They help cut power under conditions of gross faults. For smaller ground faults that might not blow a fuse (e.g. you can't use fuses as a means to prevent electrocution risks), you need a RCD type circuit.

Personally, I'd likely use a regular 13A slow-blow fuse for 5A worth of bulbs, unless there were some other sorts of high value circuitry attached that had some specific need for something more exotic to protect them.
 
Oh, so for a 5A fuse, it will burn out in time depending on the specs, however it will blow if given enough time right? Thanks for the help!
cmb said:
You'll need to read the spec of the fuse. Fuses have time periods over which they'll sustain a given current. In the case of bulbs, there will be a higher current when you switch them on (until the resistance of the bulbs increases as they get hot), so you'll almost certainly likely burn out a 5A quick-blow fuse if it is 5A during normal operation.

Fuses are coarse devices that help prevent (but do not prevent) further damage and safety issues in fault conditions. They help cut power under conditions of gross faults. For smaller ground faults that might not blow a fuse (e.g. you can't use fuses as a means to prevent electrocution risks), you need a RCD type circuit.

Personally, I'd likely use a regular 13A slow-blow fuse for 5A worth of bulbs, unless there were some other sorts of high value circuitry attached that had some specific need for something more exotic to protect them.
 
sgstudent said:
If I have a fuse with a rating if 5A and when I connect 10 bulbs in parallel, the current flowing will be 5A. When this happens will the fuse melt? Or does the current have to be more than 5A for it to melt?
In reality, it is impossible to specify at what current a fuse will blow. It could be slightly more than 5A; it could be slightly less.

Likewise, it is impossible to specify that the 10 bulbs will draw exactly 5A of current. It could be slightly more or less.

So the fuse may or may not blow; it is irrelevant to worry whether it blows for Icircuit>Irating or IcircuitIrating
 
Your incandescent lamps are a deceptive load.
Incandescent lamps draw ~10X rated current until the filament warms up.

For that reason fuses are made with various time-to-melt parameters so you can start difficult loads. They do that by tweaking the thermal mass of the element inside.
A slow fuse will have a massive element and a fast fuse a delicate one.

Fuses have a "let-through" energy rating expressed as I2t, time to melt being inversely proportional to square of current. One always matches that rating to the load he is trying to protect, though in one application i had to match it to what the source could deliver... but that's another story.

Anyhow your 5 amp fuse SHOULD carry 5 amps but you'd be well advised to leave a little extra margin. Being in a hot location reduces a fuse's current carrying ability.

What you are protecting is usually not the light bulb but the wiring to it.
Semiconductors on the other hand used to have the reputation of being "Good fuse protectors" but the manufacturers learned to make lightniing-fast fuses for that application.

Littlefuse has a good reference on fusing, it's called "Fuseology"
if this link doesn't work, a dsearch engine can find it for you.
www.littelfuse.com/data/en/Product.../Fuseology.169-198.pdf
 
Last edited by a moderator:
So then if I have a question that has a 5A fuse. Then with 20 bulbs the current will be 5A. So they ask what's the maximum number of bulbs I can put without melting the fuse. So the answer will be 19 right? Cos the fuse might also melt at 5A?
jim hardy said:
Your incandescent lamps are a deceptive load.
Incandescent lamps draw ~10X rated current until the filament warms up.

For that reason fuses are made with various time-to-melt parameters so you can start difficult loads. They do that by tweaking the thermal mass of the element inside.
A slow fuse will have a massive element and a fast fuse a delicate one.

Fuses have a "let-through" energy rating expressed as I2t, time to melt being inversely proportional to square of current. One always matches that rating to the load he is trying to protect, though in one application i had to match it to what the source could deliver... but that's another story.

Anyhow your 5 amp fuse SHOULD carry 5 amps but you'd be well advised to leave a little extra margin. Being in a hot location reduces a fuse's current carrying ability.

What you are protecting is usually not the light bulb but the wiring to it.
Semiconductors on the other hand used to have the reputation of being "Good fuse protectors" but the manufacturers learned to make lightniing-fast fuses for that application.

Littlefuse has a good reference on fusing, it's called "Fuseology"
if this link doesn't work, a dsearch engine can find it for you.
www.littelfuse.com/data/en/Product.../Fuseology.169-198.pdf
 
Last edited by a moderator:
sgstudent said:
So then if I have a question that has a 5A fuse. Then with 20 bulbs the current will be 5A. So they ask what's the maximum number of bulbs I can put without melting the fuse. So the answer will be 19 right? Cos the fuse might also melt at 5A?
Why are you posting this here and not the Homework & Coursework Questions area? Even if this is for independent study, textbook-style questions should be posted in the homework area.
 

Similar threads

  • · Replies 16 ·
Replies
16
Views
5K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 57 ·
2
Replies
57
Views
14K
  • · Replies 11 ·
Replies
11
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 9 ·
Replies
9
Views
4K
  • · Replies 15 ·
Replies
15
Views
2K
  • · Replies 5 ·
Replies
5
Views
2K