Zone heating with a single furnace

  • Thread starter Thread starter mheslep
  • Start date Start date
  • Tags Tags
    Heating
AI Thread Summary
The discussion revolves around optimizing heating in a two-story home currently using separate furnaces for the basement and attic. The basement furnace is a high-efficiency hybrid unit, while the attic unit is less efficient and may be replaced soon. With proposed insulation improvements, the total heat loss could be reduced significantly, allowing the basement unit to potentially serve the entire house. A two-zone control system is necessary for maintaining comfort across multiple levels, with controlled dampers being a suggested solution, although concerns about humidity and airflow arise from using a larger duct system. Ultimately, careful planning is required to avoid issues related to air temperature and humidity while maximizing efficiency.
mheslep
Gold Member
Messages
364
Reaction score
719
Given: a two-story residence currently with separate basement and attic gas forced air furnaces-chillers. The basement furnace is a recently updated high efficiency (96%) hybrid heat pump/aux gas heat at around 80,000 btuh (out); the attic unit is much less efficient and maybe 60-70,000 btuh (out), gas only. The home insulation and construction is oldish - walls, windows, etc. With the house as is, a Model J analysis tells me the current total house heat loss is ~110,000-120,000 btuh. In looking at a serious improvement in the insulation - walls, new windows, R-30 attic - it appears as if I could easily bring down the loss to ~60,000 btuh. The heat gain numbers present a similar case in that the entire house, well insulated, could be supplied by just the basement chiller equipment.

In that case, I'm wondering if I could find away to stop using the older, more expensive attic furnace and chiller, along with its duct system that runs in the outside ventillated ~ambient attic space. I'd especially like to know that answer before replacement time of the old attic unit anyway at end of life in 3-5 years. Currently the basement unit duct system supplies just the basement and the first floor. I understand that to maintain comfort in all rooms of a such a multi-story house, it will need at least a two zone control system. How might that be done with one heat source? I'm aware of some controlled damper solutions, but I also read, vaguely, about over heating or freezing problems caused by damper on/off instead of furnace-chiller on/off. Is there no answer but continuing to run the attic unit, and having to replace it in a few years?
 
Engineering news on Phys.org
If you have a good location where you can cross-connect the two systems, you'll have a vastly larger ductwork system than a single unit was designed-for and as a result, when feeding air to either level, you'll have plenty of airflow to avoid the problems typically seen with zoning. You'll create a new problem, though, which you may or may not care about: your cooling supply air temperature will be too warm to adequately dehumidify the space and your house will be more humid than is typically designed-for.

Try browsing smarthome.com for some ideas on solutions. Basically, though, you get a controller with two thermostat inputs and one HVAC unit output plus multiple damper outputs (you can actually slave all of the dampers for each zone to a single output). The controller decides whether/when to heat/cool and sets the dampers appropriately to send air where it needs to go.
 
russ_watters said:
If you have a good location where you can cross-connect the two systems, you'll have a vastly larger ductwork system than a single unit was designed-for and as a result, when feeding air to either level, you'll have plenty of airflow to avoid the problems typically seen with zoning. You'll create a new problem, though, which you may or may not care about: your cooling supply air temperature will be too warm to adequately dehumidify the space and your house will be more humid than is typically designed-for.

Try browsing smarthome.com for some ideas on solutions. Basically, though, you get a controller with two thermostat inputs and one HVAC unit output plus multiple damper outputs (you can actually slave all of the dampers for each zone to a single output). The controller decides whether/when to heat/cool and sets the dampers appropriately to send air where it needs to go.
Thanks russ_watters. Regarding the humidity problem, the issue there, if I understand correctly, is that the humidity tied to vent outlet air temperature, and that by using a larger duct system on a single chiller the outlet air temperature must inevitably increase, and any increase will raise the humidity over what it would have been previously with a smaller duct system?
 
Correct. A psychrometric chart will tell you the resulting relative humidity from a certain dew point. http://docs.engineeringtoolbox.com/documents/816/psychrometric_chart_29inHg.pdf

Room (dry bulb) temperature is at the bottom. Dew point temperature is horizontally across the chart. When you cool air, it becomes saturated, so the supply air temperature is roughly equal to the dew point (plus a degree or two due to heat gain in the duct and inefficiency of the coil). Where the dew point line and the dry bulb temperature line cross, you can read the RH. For example, if the room temperature is 75F and the dew point (supply air temperature) is 55F, the resulting RH is 51%.
 
Last edited:
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly
Back
Top