How to calculate reactive power for 3 phase induction motor

AI Thread Summary
To calculate the reactive power for a 10HP 3-phase induction motor, the formula P = √3 x V x I x sin(θ) can be used, where V is the voltage and I is the current. The measured current of 7.8A and voltage of 415V can be plugged into this formula, but it assumes a unity power factor. The actual power factor must be considered for accurate calculations, as it varies with the motor's load. It's recommended to use a true power meter for precise measurements, and consulting the motor's specifications can provide further insights. Additionally, utilities may offer assistance if KVAR charges appear on electric bills, as they prefer to sell energy rather than reactive power.
ws0619
Messages
53
Reaction score
0
Hi all,
I would like to install Capacitor Bank into my control panel board which contains of few 10HP induction motors. Currently I'm just able to measure the Ampere for every induction motor by using current meter.
How to calculate the reactive power for 10HP 3phase 4pole induction motor by just using Amp value?

One of my 10HP motor:
Voltage: 415V
Amp: 7.8A (measure)
I am using 10HP Teco motor with 4pole and 1450rpm.
Please enlighten me.
Thanks!
 
Engineering news on Phys.org
It can't be calculated from that information. Can you read the motor nameplate? What is the model number? Full load amps?
 
This will really depend on how the motors are loaded as well - a 10HP motor that is mechanically delivering 10HP has much better PF than the same motor with only 7HP pf load. Really the only way to do this IMO is with measurements - and if the load on the motor varies, you really only want to compensate for the "best case" - not the worst.
Starting motors on a system with excessive online capacitance provided too much inrush and can over time damage the motor.
You can add the cap to each motors line - so they are switched on an off with the motor - but this also causes large inrush currents - not something I would just throw together. In larger systems they actually us a controller that measures the current and PF and then switches in the appropriate capacitance...
Lastly - if you are getting a KVAR charge on your electric bill the utility may offer some engineering - they would prefer to sell you energy - not VARs because they can charge more for them.
 
Windadct said:
This will really depend on how the motors are loaded as well - a 10HP motor that is mechanically delivering 10HP has much better PF than the same motor with only 7HP pf load.
I'm a bit unclear on this point. My thought was that while you are certainly correct that the PF depends on the load, that's just because the active power depends on the load. That would leave the reactive power constant and make the the PF (the ratio of the active to total) vary. The OP actually just asked about the reactive power. I am uncertain of this, but I do know that motors are generally provided constant size/output capacitors for PF correction. Still:
Really the only way to do this IMO is with measurements - and if the load on the motor varies, you really only want to compensate for the "best case" - not the worst.
Agreed. Another reason besides what you said is the utilities generally don't want leading power factor, so the capacitors should be sized to not quite compensate for all of the reactive power.
Lastly - if you are getting a KVAR charge on your electric bill the utility may offer some engineering - they would prefer to sell you energy - not VARs because they can charge more for them.
Indeed the bill itself probably provides some insight. But depending on how big of a facility it is, it may not be enough information to size the capacitors.

Either way, yes: a true power meter attached to the motor is preferred here. Second choice would be to find the manufacturer's rating.
 


To calculate the reactive power for a 3-phase induction motor, you will need to use the formula P = √3 x V x I x sin(θ), where P is the reactive power, V is the voltage, I is the current, and θ is the angle between the voltage and current. In this case, since you have measured the current (7.8A) and know the voltage (415V), you can plug those values into the formula to calculate the reactive power for your 10HP motor. However, it is important to note that this formula assumes a unity power factor, meaning that the angle between the voltage and current is 0 degrees. If your motor has a different power factor, you will need to factor that in to your calculation. Additionally, the specific characteristics of your motor (such as the type of winding and the type of load it is driving) can also affect the reactive power. It may be helpful to consult with a professional or refer to the motor's specifications to get a more accurate calculation.
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Back
Top