The discussion centers on the use of wye versus zigzag connections for earthing transformers, particularly in medium voltage applications. A direct wye connection requires sufficient reactance for exciting voltage, which can increase construction costs and pose dangers if shorts occur. Zigzag transformers are favored globally for earthing due to their cost-effectiveness, especially when grounding multiple star-connected transformers. The choice between these configurations often hinges on the specific grounding needs of the bus system and the associated costs. Ultimately, while zigzag is a common method, earthing transformers can also utilize standard star-delta configurations.
jacquisdelumen
Messages
1
Reaction score
0
:rolleyes: I'm curious if we use a direct wye connection instead of zigzag in case of earthing transformer.. i know that by merely looking if we use wye connection in earthing specially in medium voltage you have to have enough reactance for your exciting voltage.which will cost more in construction.also should there be shorts you directly ground the system which is very dangerous.does my opinion correct? any opinion might help..thanks
 
Engineering news on Phys.org
I am thoroughly confused by the above.
 
jacquisdelumen said:
:rolleyes: I'm curious if we use a direct wye connection instead of zigzag in case of earthing transformer.. i know that by merely looking if we use wye connection in earthing specially in medium voltage you have to have enough reactance for your exciting voltage.which will cost more in construction.also should there be shorts you directly ground the system which is very dangerous.does my opinion correct? any opinion might help..thanks

If you are describing a three phase transformer, we in the USA usually refer to them as a WYE or Delta configuration. I’m not familiar with “zigzag”. Your post is hard to understand.
 
Folks,

Zigzag transformers are used all over the world for earthing (grounding) and unearthed bus, and in voltage ranges from LV to MV. I think the original question is along the lines "why would you bother earthing a bus with a separate zigzag when star-points (wye-point) are available?" I think it mainly comes down to cost - if there is a need to Earth a bus via several separate star-connected transformers, each with associated neutral bushing and full voltage insulation at the netra end, the lower cost with a single zigzag transformer comes into consideration. I have seen them on a set of 33 kV busses where one of the incomers was delta, so there was a possibility of an ungrounded bus if that incomer was in service with all other star-connected feeders and incomers out of service - a dedicated earthing transformer then makes sense and zigzag construction is a very cost-effective way of achieving that. If all incomers on a bus were star connected and are able to be earthed at tehe star-point, then there is no need for a separate earthing transformer.

Earthing transformers do not have to be zigzag - it is just one method - they can also be a more normal star delta with the star-point earthed and teh delta either used for aux power or not used.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top