Calculating the Dimensions of a Reinforced Concrete Column Under Stress
  • Thread starter Thread starter anthonyk2013
    Stress
A reinforced concrete column is analyzed with a modulus of elasticity of 20 GN/m² and two steel bars of 25 mm diameter, with a modulus of 200 GN/m². The stress in the concrete must not exceed 7 MN/m² under a load of 400 kN. Calculations show the area of the steel bars and derive the necessary cross-sectional area of the concrete. The total area is then used to determine the dimensions of the square section strut, ultimately leading to a required side length of approximately 220 mm for the column. Accurate unit management is emphasized throughout the calculations to ensure correctness.
anthonyk2013
A concrete column having a modulus of elasticity of 20GN/m2 is reinforced by two steel bars of 25mm diameter having modulus of 200GN/m2.
Calculate the dimensions of a square section strut if the stress in the concrete is not to exceed 7MN/m2 and the load is to be 400KN.
σ in conctete not to exceed 7*106
Load =400KN
E of steel=200GN/m2
E of concrete=20GN/m2
Area of steel=3.14*252/4*2=982*10-3m2
Area of concrete=?
σc/Ecs/Es
σcs*Ec/Es
σcs*20/200
σcs*.1
7*106s*.1
7/.1*106s
σs=70*106MN/M2
Wondering if I m on the right track?
You could indicate the units of your calculations.
Well do. Bad habit
Any help would be appreciated
Let S be the side of the square cross section column. What is the total area of the cross section. What is the cross sectional area of the steel rods (this time calculate it correctly, taking into account that 1 mm = 0.001 m)? In terms of S, what is the cross sectional area of the concrete?
Area of the steel is 3.14*.0252/4=.0004908
Because there is two rods I multiply .0004908*2=.000981747m2
S=L*B
S=L*B
What are L and B?
For the cross sectional area of the concrete, I get (S - 0.000981747) m2.
Chestermiller said:
What are L and B? Length x breath
Yes S-0.000981747
anthonyk2013 said:
Yes S-0.000981747
Actually, S2-0.000981747. What is your recommendation as to what to do next in this problem?
I need the get area using the values I have.
do I use σc/Ecs/Es
σcs=Ec/Es
σc=Fc/Ac and σs=Fs/As
THEN Fc/Ac*As/Fs=Ec/Es
do I use σc/Ecs/Es
σcs=Ec/Es
THEN Fc/Ac*Fs/As=Ec/Es
Let ε be the compressive strain in the steel and concrete. What value of ε causes the stress in the concrete to equal 7MN/m2? What is the stress in the bars? In terms of S, what is the compressive force in the bars and in the concrete? What are the sum total of the compressive forces? What value of S causes this total compressive force to equal 400 kN.
ε of concrete=ε in steel?
σ=E*ε
ε=σ/E ε=7MN/m2/20N/m2
Would the correct way the write this be ε=7*106/20*109=.35*10-3
σ in steel=.35*200=70MN
Total force is 400KN so I need to find what load is on the steel.
σ=E*ε
So far, so good. Now, you know the stress in the steel. What is the load carried by the two steel bars?
σ=F/A→F=σ*A→F=70*106*0.000981747m2=.06872MN/m2
or 69KN/m2
Total force is 400KN, force in steel is 69KN so 400KN-69KN=331KN
Force in concrete=331KN
σ in concrete=7MN/m2
Area=f/σ A=331*103/7*106=47.285*103 or 47285
\sqrt{}47285=217.45mm2
Answer in my notes is 220mm2
You're still not being careful about units. You made two errors that canceled each other out. Incidentally, the length of the side of the square cannot be in mm2. It has to be mm.
217.45mm is what should have wrote?
Not exactly. You had to add the area of the bars back to get the total area. Then take the square root. That's probably why you got 217 and the book had 220.
To get the dimensions I need to find the total area. Concrete +steel and square root that.
Thanks for your help Chester, big help again.