Why does multiplying 120 by 1.73 give me 208 volts in a 3 phase system?

AI Thread Summary
In a 120/208 three-phase system, the voltage between two hot leads is calculated using the formula that incorporates the square root of three. Multiplying 120 volts by 1.73 (the square root of three) yields 208 volts, which represents the line-to-line voltage. The confusion arises from misunderstanding how voltages in a three-phase system interact; they do not simply add together. Instead, the voltage difference between two phases must be considered, not their sum. This clarification helps resolve the initial question about the relationship between the voltages in the system.
Evil Bunny
Messages
241
Reaction score
0
Ok... This is a simple question that I'm having a hard time with. I'm forgetting something that I learned and I want to clear it up...

I know that a 120/208 3 phase system has 3 hot leads that are 120 degrees out of phase with each other with respect to the neutral.

If you multiply 120 X 1.73 (square root of three), you get 208 volts. I'm not sure why...

If I add 120 + 120@120 degrees, my calculator tells me the answer is 120@60 degrees.

I expected it to say 208.

Why? What am I getting confused here?
 
Engineering news on Phys.org
Hi Evil Bunny. The voltage between two points is equal to the difference in their voltages, not their sum.

Try calculating 120 - 120@120 degrees. :smile:
 
Thank you!
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...