The discussion revolves around the behavior of a balanced wye configuration in three-phase systems, focusing on the neutral point, line-to-line voltage, and the effects of load balance on current and voltage. Participants explore theoretical concepts, practical implications, and experimental observations related to these electrical systems.

Discussion Character

  • Technical explanation
  • Conceptual clarification
  • Debate/contested

Main Points Raised

  • One participant questions whether the line-to-line voltage remains constant in a balanced wye configuration and considers the implications of sine waves being 120° apart.
  • Another participant asserts that if the system is balanced, the neutral potential would be zero and that the line-to-line voltages would also be sinusoidal.
  • There is a discussion about the relationship between phase voltages and the neutral point, with participants agreeing that Va + Vb + Vc = 0 in a balanced system.
  • Concerns are raised about the impact of an unconnected load on the balance of the system, with questions about whether this would lead to infinite impedance and unbalanced currents.
  • Participants note that if the load is unbalanced, the currents in the lines will also be unbalanced, but the total current will still sum to zero if one line is disconnected.

Areas of Agreement / Disagreement

Participants generally agree on the behavior of the neutral point in a balanced system and the sinusoidal nature of line-to-line voltages. However, there is ongoing discussion about the implications of unbalanced loads and the conditions under which the system remains balanced, indicating that multiple competing views remain.

Contextual Notes

Some assumptions about the nature of the loads and their connections are not fully explored, particularly regarding the effects of open circuits on system balance. The discussion also touches on the distinction between peak and RMS values, which may affect interpretations of measurements.

Who May Find This Useful

This discussion may be useful for students and professionals in electrical engineering, particularly those interested in three-phase systems, load balancing, and the practical implications of wye configurations.

jendrix
Messages
120
Reaction score
4
Hello,

I have been going over the above topic and have a question about the neutral point of a balanced wye configuration. Would the line to line voltage remain constant? I am trying to picture two sine waves 120° apart and it's making me think the Va would be reducing as Vb was increasing at certain points? So would Vline still be alternating sinosoidally?

The reason I ask is I did an experiment in class where we had to set the line voltage to 10V and confirm it with a multimeter. Is it possible the multimeter was showing the peak value?

On another note, am I correct in thinking the voltage potential at the neutral point would be zero provided the system was balanced?

Thanks
 
Last edited:
Engineering news on Phys.org
You are correct in your thinking that, if the system is balanced, the neutral potential would be zero.

You are also correct in your thinking that, as one of the phase to neutral voltages changes, the other two will also change such that Va + Vb + Vc = 0. The line to line voltages would also be sinusoidal.
 
magoo said:
You are correct in your thinking that, if the system is balanced, the neutral potential would be zero.

You are also correct in your thinking that, as one of the phase to neutral voltages changes, the other two will also change such that Va + Vb + Vc = 0. The line to line voltages would also be sinusoidal.

So that would mean the current Ia, Ib and Ic have a phase different with each other but at all times the sum of current at the neutral node would be 0?

Therefore in order for a system to be unbalanced the input voltage at A,B,C would either have to have a different peak or not be 120 degrees apart? Or have different loads?Thanks
 
jendrix said:
So would Vline still be alternating sinosoidally?

Yes. The differential voltage between two phases is sinusoidal.

The line voltages will be symmetrical and separated by 120° about the neutral.

The current will be balanced if the load is balanced. The phase of the current will be determined by the impedance of the load.

If the load is not connected to the neutral then the neutral currents will cancel at the centre of the 'Y' and the neutral conductor will carry zero current.

See attached picture. It shows 3 phases, each 230Vpeak, NOT RMS.
It also shows one of the three, two phase differential line voltages, red – yellow.
3PH.png
 
Baluncore said:
Yes. The differential voltage between two phases is sinusoidal.The current will be balanced if the load is balanced. The phase of the current will be determined by the impedance of the load.

If the load is not connected to the neutral then the neutral currents will cancel at the centre of the 'Y' and the neutral conductor will carry zero current.

View attachment 203303

If the load at for example A wasn't connected then wouldn't that cause the system to become unbalanced as the the impedance at A would be infinite as it would be an open circuit?
 
jendrix said:
If the load at for example A wasn't connected then wouldn't that cause the system to become unbalanced as the the impedance at A would be infinite as it would be an open circuit?
Baluncore said:
The current will be balanced if the load is balanced.
If the load is unbalanced then the currents in the lines will be unbalanced.
If one line is disconnected, the total current flowing in the three lines will still sum to zero. There can be no neutral current.
The load may not function correctly if one phase is not connected.
 

Similar threads

  • · Replies 15 ·
Replies
15
Views
6K
  • · Replies 20 ·
Replies
20
Views
4K
  • · Replies 77 ·
3
Replies
77
Views
9K
  • · Replies 27 ·
Replies
27
Views
2K
Replies
14
Views
6K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K
Replies
8
Views
4K
Replies
12
Views
5K
  • · Replies 1 ·
Replies
1
Views
3K