Grounding in USA residential homes with 240/120 panel

  • Thread starter Thread starter psparky
  • Start date Start date
  • Tags Tags
    Grounding Usa
AI Thread Summary
Removing the ground rod from a residential service entrance can introduce significant dangers, including the potential for appliances to become electrified due to voltage differences during faults, such as lightning strikes or transformer failures. Without a proper ground, appliances may accumulate dangerous leakage currents, which could lead to electric shocks. The discussion highlights that appliances are effectively connected to the center tap of the transformer, making them vulnerable to voltage fluctuations. Additionally, the absence of a ground rod compromises lightning protection, increasing the risk of severe electrical hazards. Overall, maintaining a proper grounding system is crucial for safety in residential electrical installations.
psparky
Science Advisor
Gold Member
Messages
884
Reaction score
33
I asked the question during a grounding seminar ...talking about grounding in USA residential homes with 240/120 panel. I wasn't quite satisfied with the answer.

The question is...what dangers are introduced when you remove the ground rod from a service entrance like the main panel in a home. And let's assume water line is not used as a ground so the ground is completely floating.

Here are my thoughts:
I believe the breakers are still going to pop in a hot to ground situation due to tying the neutral and ground together in the panel...so any short will hit the center tap of transformer and trip breaker regardless of Earth rod or not.

Someone mentioned the voltage may drop in panel...not sure what that's about. Someone mentioned voltage may be higher...someone mentioned you may end up using your neighbors ground rod...all heresay at this time.

We are clearly going to lose lighting protection.

One danger I can think of is that these appliances need to shed trickle current due to any leakage inside or even static charges. So normally, ground bleeds any of this. Without ground...deadly charges may build up.

And to add more confusion...let's talk about 3 phase feeders (NO neutral) on a aluminum ladder in a factory. When grounded properly...when hot wire touches ladder...we pop the breaker. But how is this current returning? Is it going thru the ground all the way back to the electric company? Or is something else happening?

I'm guessing there is trickle current all over the place. If you think about a 500 KV line coming down the power lines...those insulators on the towers have a resistance of a finite number rather than infinite number, Since V=IR...small current must leak down any insulator into the ground. Even just a 12KV line must be leaking even a little at any insulator. Again, does this leakage go back to the source...electric company?

Can anyone enlighten us further on the subject?
 
Engineering news on Phys.org
There are reasons other than faults.

502ecm17fig1.jpg
 
The question is...what dangers are introduced when you remove the ground rod from a service entrance like the main panel in a home. And let's assume water line is not used as a ground so the ground is completely floating.

You already know that answer.

Per Don's sketch every appliance in the house now has its skin hard wired to the centertap of the service transformer atop backyard power pole.
That point is earthed by the bare copper wire on side of pole. It is coiled on bottom of pole to give good surface area..
So every appliance skin is elevated above Earth by the voltage drop along that neutral wire from your panel to pole. When things are going right it's so small you'd probably not notice.

When lightning strikes the top of that power pole, every 'grounded' appliance in the house is connected directly by wire to the bottom of a lightning bolt.
Were your house's ground rod intact, the Earth's potential at your house would be driven up toward that of the lightning bolt so there'd be little potential difference between your feet and that appliance skin.
Without that ground rod you lose that protection. If you're touching an appliance you will feel voltage difference between whatever you're standing on and the bottom of that lightning bolt.

Granted lightning is rare. But a transformer can fault primary to secondary, or a high voltage wire can fall across your incoming power wires. Same principle applies.

The lightning thing happened to me once, I was out in the yard using a metal cased drill on a 3 conductor extension cord, but fortunately was standing near my house ground rod(20 feet or so). Still the shock was substantial.
Maybe there's something to be said for "double insulated" power tools with plastic cases..

old jim
 
Last edited:
jim hardy said:
... every appliance in the house now has its skin hard wired to the centertap of the service transformer atop backyard power pole.
That point is earthed by the bare copper wire on side of pole. It is coiled on bottom of pole to give good surface area..
So every appliance skin is elevated above Earth by the voltage drop along that neutral wire from your panel to pole. When things are going right it's so small you'd probably not notice.
It only takes once when things aren't going right to notice.


501ecm17fig4.jpg
because
502ecm17fig3.jpg
 
Last edited:
The correct way just for "those who want to be safe" image.

501ecm17fig2.jpg
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...