Calculating Total Power and Power Factor for Parallel Loads in an AC Circuit

  • Thread starter Thread starter ridemx
  • Start date Start date
AI Thread Summary
Three loads are connected in parallel to a 1000Vrms, 60Hz AC source, consisting of an inductive load (125kVA, 0.28 pf lagging), a capacitive load (10kW, 40kVAR), and a resistive load (15kW). The calculations for apparent power (S), real power (P), and reactive power (Q) were performed for each load, resulting in total values of S=181.23kVA, P=60kW, and Q=160kVAR. However, a discrepancy arose when checking the totals using the power factor equation, leading to a revised total of Q=80kVAR after considering the effects of adding a capacitor to the inductive load. The final circuit totals were confirmed as P=60kW, Q=80kVAR, and S=100kVA, indicating the calculations were corrected.
ridemx
Messages
5
Reaction score
0

Homework Statement



3 loads are connected to a source (1000Vrms, 60hz, 1 phase) in parallel
load 1:Inductive, 125kva, .28pf lagging
load 2:capacitive, 10kw, 40 kvar
load 3:resistive, 15kw

Find total S, P, Q, PF

Homework Equations



S=apparent (VA)
P=real (W)
Q=reactive (VAR)

S^2=P^2+Q^2
PF=P/S

The Attempt at a Solution



Using the above equations, I found the S,P,Q for all 3 loads as follows,

Load 1:
S=given=125kva
P=(125kva)(.28)=35kw
Q=sqrt[(125kva^2)-(35kw^2)]=120kvar

Load 2:
S=sqrt[(10kw^2)+(40kvar^2)]=41.23kva
P=given=10kw
Q=given=40kvar

load 3:
S=sqrt[(0^2)+(15kva^2)]=15kva
P=given=15kva
Q=0 since resistive

I added up all the P's Q's and S's to get

S=181.23kva
P=60kw
Q=160kvar

but then I checked myself using S^2=P^2+Q^2 and it doesn't work out

sqrt[(60kw^2)+(160kvar^2)]=170.9kva not 181.23kva

where did I screw up, can you not just add the loads?
 
Physics news on Phys.org
If you have an inductive load and you draw the Power Factor Triangle for it, and then you want to improve the Power Factor by adding in a capacitor, what will happen to the Power Factor Triangle?
 
Adding a capacitor to and inductive load, it will decrease total Q, I guess I never thought of it that way for some reason, but in that case would the Q's be

Load 1: 120kvar
Load 2: -40kvar
Load 3: 0

which gives a total of 80kvar, so:

circuit totals are
P=60kw
Q=80Kvar
S=sqrt[(60^2)+(80^2)]=100VA

Is this at all correct?
 
You mean S=sqrt[(60k^2)+(80k^2)]=100kVA, and yes this looks correct.
 
yep, that's definitely what I meant, more of just a typo. Thank a lot for the help!
 