Air required to cool water temperature

AI Thread Summary
To cool 8 ounces of water from 70°C to 38°C in 2 minutes, a cooling rate of 249 W is required. The discussion suggests using a fan or air pressure to enhance cooling, with calculations based on the heat transfer equation Qrate = m-water X cp-water X (T final - T initial) / elapsed time. Participants recommend estimating the convection heat transfer coefficient (h) and considering methods like a heat exchanger or a cold air gun for efficient cooling. Additional room temperature water can help, but the final volume must remain 8 ounces. Effective cooling strategies involve calculating the necessary air velocity and flow rate to achieve the desired temperature drop.
Vig16
Messages
7
Reaction score
0
I'm trying to cool 8 ounces of 70 deg C water down to 38 deg C. I want to do this all in 2 minutes, but with as low a cost as possible. I was thinking of using a fan or air pressure of some short to do this. The only question I had is how do I determine the pressure or amount of air that I'll need to obtain the temperature drop?

My initial test was to dispense 3 ounces at 70dC and then have room temperature water dispensed into the 70dC water. In my two attempts at this, I got the temperature in the cup down to 44dC and 47dC, but am still off by a bit. I was thinking that if I introduced air of some sort into the flow of room temperature water, that I'd be able to have the final water temp drop the 5-10dC that I'm looking for.

Does anyone have any insight as to how I'd go about calculating the amount of cooling that I'd need to get to the desired temperature? Even just the equation to start with would be greatly appreciated!

Thanks so much!
 
Engineering news on Phys.org
Could you dispense just a little more room temperature water to get to your final temperature?

If not, you cooling heat rate is:

Qrate = m-water X cp-water X (T final - T initial) / elapsed time

You can then determine the velocity of coolant as follows; from Newton's law of cooling:

Qrate = h A (Tsurface - Tfluid)

You can estimate h, the convection heat transfer coefficient, from the Dittus Boelter correlation corrected to your geometry or a simlilar one. The h is a function of velocity.
 
edgepflow said:
Could you dispense just a little more room temperature water to get to your final temperature?

If not, you cooling heat rate is:

Qrate = m-water X cp-water X (T final - T initial) / elapsed time

You can then determine the velocity of coolant as follows; from Newton's law of cooling:

Qrate = h A (Tsurface - Tfluid)

You can estimate h, the convection heat transfer coefficient, from the Dittus Boelter correlation corrected to your geometry or a simlilar one. The h is a function of velocity.

I can add a little more room temperature water, but the final solution needs to be 8oz.

Thank you for the equation, I'll plug some numbers into it and see what I come up with!
 
edgepflow - I did all the math for my cooling rate and I came up with this...

Mass = 8 ounces = 0.237 kg (approx)
Specific heat of water = 4187 J/kgK
Temperature decrease = 32 °C
Time = 2 mins = 120 seconds

Power = 4187 * 0.237 * 32 /120 = 249 W

How would you suggest I determine the velocity if I'm unsure about the Tsurface? Also, is this the fluid temp when it's hot or the ideal temp that I'd like to get it down to?
 
There are two ways to approach this.

1. Perform a time dependent solution.

You could apply the simple but powerful "lumped capacity" model if the Biot number is < 0.1. If not, you would need to include spatial effects. Most good heat transfer textbooks present both of these.

2. Assume an average surface temperature.

For a back of the envelope crude estimate, you could assume the surface temperature is constant and the average of the initial and final temperature.

You could figure out the velocity and hence volumetric flow rate and then size a fan or whatever device you may need. You may also consider a "cold air gun" which supplies chilled air and only requires a supply of compressed air.
 
Vig16 said:
I'm trying to cool 8 ounces of 70 deg C water down to 38 deg C. I want to do this all in 2 minutes, but with as low a cost as possible. I was thinking of using a

How about a heat exchanger? Just pour the hot water through a room-temperature metal pipe and it'll come out colder at the other end.

If you have to repeat the process quickly you'd need to then cool the pipe, maybe with a fan or just passively.
 
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
Back
Top