Caculation of line current on a 3 phases unbalanced delta

AI Thread Summary
The discussion revolves around calculating line currents in a three-phase unbalanced delta system with a 220V AC supply and a 3300W pure resistance load. The participants use Kirchhoff's Current Law (KCL) and complex numbers to derive the currents I1, I2, and I3, ultimately finding I1=15A, I2=15A, and I3=26A. They also explore alternative methods, including trigonometric calculations, to arrive at the same results. Additionally, there is a brief mention of the differences in voltage terminology between the US and Europe, highlighting potential confusion in phase and line voltage interpretations. The conversation emphasizes the importance of clarity in calculations and terminology in electrical engineering.
JumpZero
Messages
2
Reaction score
0
Hello,
I cannot find back from school, the formula to use:
A 3 phases 220Vac system, no neutral, 3300W of pure resistance load between L2 and L3, the same load between L1 and L3, nothing between L1 and L2.
What will be I1, I2, I3 the current in the 3 lines of the network?

Thanks in advance
--
Jmp0
 
Engineering news on Phys.org
Assume V1 = 220 / 0, V2 = 220 / 120, V3 = 220 / 240.

Calculate I23 and I13. (I23 is current from L2 to L3 ).

I2 = I23, I3 = -I23 - I13 (KCL)

I1 + I2 + I3 = 0 (KCL)

Calculate with complex numbers all the way.
 
Last edited:
I agree with Hesch except the voltages are V12=220>0,V23=220>-120,V31=220>-240[or +120] and since the load it is declared as “pure resistance” [cos(fi)=1] the currents will be:

I12=0;I23=3300/220*[(COS(-120)+SIN(-120)j];I31=3300/220*[(COS(+120)+SIN(+120)j]
upload_2015-4-28_7-52-7.png


Considering all currents “entering” position:

I1=I13=-I31=-15*[(COS(+120)+SIN(+120)j] =7.5-12.99j;I2=I23=-7.5-12.99j;I3=-I1-I2=2*12.99j=25.98j.Remark: the imaginary part of the current here it does not mean reactive part. The reactive part will be proportional with the sinus of angle between current and supplied voltage[fi] which remains 0 [in this case].

One could calculate also-following Hesch logic-using a trigonometric circle and use X and Y coordinates instead of complex number. The circle radius is equal to I=P/V=3300/220=15 [A]. Then:
upload_2015-4-28_7-52-45.png


I23X=-15*SIN(30)=-7.5[A]; I23Y=-15*SIN(60)=-12.99 [A]; I31X=-15*SIN(30)=-7.5 [A]; I31Y=+15*SIN(60)=12.99[A].

I1=I13=-I31 =7.5X-12.99Y;I2=I23=-7.5X-12.99Y;I3=-I1-I2=-(I1+I2)=2*12.99Y=25.98[A].
 
Hello,

Thanks for your answers. This is correct. I found it also (with help) with another method and result are the same:
I1=15A I2=15A I3=26A
This method:
Phase currents = I=P/E, = O amps for L1-L2 (ab) 3300/220 = 15A for L2-L3 (bc) & 15A for L3-L1 (ac)
Line currents =
L1 =√(ab²+ac²)+(ab x ac),
L2 =√(ab²+bc²)+(ab x bc),
L3 =√(ac²+bc²)+(ac x bc)

Thanks everybudy
--
Jmp0
 
It is a very interesting formulas. The complete one it is as following:

L3 =√(ac²+bc²)-2x(ac x bc)xcos(angle)

and for "angle" between ac and bc vectors[let's say "phasors"] of 120o turn it in:

L3 =√(ac²+bc²)+(ac x bc) [as you said]

As you can see for any other angle an error occurs.
 
Hesch said:
Assume V1 = 220 / 0, V2 = 220 / 120, V3 = 220 / 240.
(note my underline).
Babadag said:
I agree with Hesch except the voltages are V12=220>0
JumpZero said:
A 3 phases 220Vac system

Well, in Denmark (Europe) we operate with a phase-system (voltages and currents are as per phase) and a main-system (voltages and currents are phase to phase). So when I read "3 phases 220V", I regard 220V per phase to be meant ( V12 = 220V*√3 )?? In Europa we would write this: A 3×380V system.

I don't want to introduce a discussion about these different terms in US/EU, this is meaningless. I'm just trying to clarify the reason to some confusion
 
Last edited:
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Back