Calculate Flow Rate: Inlet & Outlet Diameters & Pressures

AI Thread Summary
Calculating the flow rate of water through a restrictionless device, such as a tank, is not feasible since such devices do not impact flow rate. The discussion highlights that flow rate is determined by the input and output piping, which includes restrictions like valves. In the case presented, with a 3" pipe and specific inlet and outlet pressures, the flow rate can be influenced by the pressure drop across the system. To accurately determine flow rate, knowledge of the flow coefficient (Cv) is essential, which can be derived from pressure drop measurements. The conversation emphasizes the importance of understanding the system's configuration and available pressure data for accurate flow calculations.
DHJenkins
Messages
2
Reaction score
0
Is it possible to calculate the flow rate of water through a restrictionless device (a tank, for example) if you know the inlet & outlet diameters and pressures?

I've been looking all over, but all I can seem to find is formulas for pressure drop in a length of pipe...

Thanks!
 
Engineering news on Phys.org
No, it is not. Such a device has no effect on flow rate, if it provides no restriction.
 
DHJenkins said:
Is it possible to calculate the flow rate of water through a restrictionless device (a tank, for example) if you know the inlet & outlet diameters and pressures?

I've been looking all over, but all I can seem to find is formulas for pressure drop in a length of pipe...

Thanks!
A pipe is not a "restrictionless device", there is a very real restriction to flow through a pipe, so the question needs a bit of help. Are you looking to find out how to determine pressure drop (ie: restriction to flow) through a pipe? Or are you asking about something else?
 
Thanks for the replies.

Russ - I'm not looking for the effect on flow rate, I'm looking the actual flow rate - a number, specifically in GPM and preferably within 5% +/-

Q_goest - Basically, I have a 3" pipe that enters the heat exchanging portion of a packaged A/C unit. The water flows in, flows through 4 different tube-style heat exchangers (in parallel), then out of a 3" pipe; I'd say total trip of about 22 linear feet from pressure gauge to pressure gauge.

This small loop is tapped off of a larger supply/return loop. There are 2 valves - an inlet & and outlet. The inlet remains wide open so as to not starve the coils for water, and flow rate is adjusted by opening/closing the outlet valve. The inlet pressure is 45psi, and the outlet pressure is 35 psi - what is the flow rate of water through this machine? Also, maximum pressure drop (with both handles wide open) is 20 psi - I imagine this has to do with the height; the machine is located approximately 50' below the pumps.

Thanks
 
DHJenkins said:
Russ - I'm not looking for the effect on flow rate, I'm looking the actual flow rate - a number, specifically in GPM and preferably within 5% +/-
You missed my point. My point was that if the device has no effect on the flow rate, then the flow rate is determined entirely by what is going on with the input and ouput piping: and you provided no information about them besides their size.

That said, I should have realized by your wording that your "restrictionless" device is not restrictionless:
This small loop is tapped off of a larger supply/return loop. There are 2 valves - an inlet & and outlet. The inlet remains wide open so as to not starve the coils for water, and flow rate is adjusted by opening/closing the outlet valve. The inlet pressure is 45psi, and the outlet pressure is 35 psi...
If there is a pressure drop, then that means there is a restriction. The restriction causes the pressure drop. Unfortunately, you need to know the flow coefficient (Cv) to find the flow at a given pressure drop. That's based on this formula (in step 3): http://www.cheresources.com/valvezz.shtml
...what is the flow rate of water through this machine? Also, maximum pressure drop (with both handles wide open) is 20 psi.

- I imagine this has to do with the height; the machine is located approximately 50' below the pumps.
If it is a closed system, the height doesn't matter. Do you have pressure gages anywhere else? At the pumps? At the mains before the valves? It sounds like the pressure gages you are referring to are on either side of your heat exchanger, between the valves. Is that correct?

Is this heat exchanger something you built yourself or is it manufactured? If it is manufactured, it should have a performance curve. If nothing else, the valves should have published Cv's, so if you can measure the pressure drop across them, you can calculate the flow that way.
 
Here's a video by “driving 4 answers” who seems to me to be well versed on the details of Internal Combustion engines. The video does cover something that's a bit shrouded in 'conspiracy theory', and he touches on that, but of course for phys.org, I'm only interested in the actual science involved. He analyzes the claim of achieving 100 mpg with a 427 cubic inch V8 1970 Ford Galaxy in 1977. Only the fuel supply system was modified. I was surprised that he feels the claim could have been...
Thread 'Turbocharging carbureted petrol 2 stroke engines'
Hi everyone, online I ve seen some images about 2 stroke carbureted turbo (motorcycle derivation engine). Now.. In the past in this forum some members spoke about turbocharging 2 stroke but not in sufficient detail. The intake and the exhaust are open at the same time and there are no valves like a 4 stroke. But if you search online you can find carbureted 2stroke turbo sled or the Am6 turbo. The question is: Is really possible turbocharge a 2 stroke carburated(NOT EFI)petrol engine and...