Calculating Single Phase Transformer Parameters and Performance

Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
3 replies · 13K views
dvep
Messages
43
Reaction score
0

Homework Statement



Figure 1 shows the equivalent circuit of a single phase transformer and figure 2 shows the approximate equivalent circuit.

Reduce the circuit to approximate form and find:
rm, xm, R1, X1

Using the approximate equivalent circuit calculate-

With the transformer operating at no-load:

primary current , primary power factor, primary real power, secondary voltage.

I am given in the equivalent circuit:
r1, r2, rm, x1,x2,xm, turns ratio, V1


Homework Equations



R1 = r1' + r2'
X1 = x1 + x2' = x1 +x2(N2/N1)


The Attempt at a Solution



Using the equations above I have found R1 and X1
I now need to find rm and xm of the approximate equivalent circuit and primary current , primary power factor, primary real power, secondary voltage.


I am struggling with this, any help would be appreciated, thankyou.
 

Attachments

  • Figure 1.JPG
    Figure 1.JPG
    17 KB · Views: 725
  • Figure 2.jpg
    Figure 2.jpg
    7.5 KB · Views: 689
Last edited:
Physics news on Phys.org
To my knowledge, rm and xm do not change when converting to the approximate equivalent circuit.
To go about finding the primary current (Io) you will have to calculate the currents Ioa (active component) and Ior (reactive component). The formulae for finding these are:
Ioa = V1 / rm
Ior = V1 / xm
Then, to find Ioa, use the formula: Io = √((Ioa)^2 + (Ior)^2)
The primary power factor is found using: Ioa / Io
Primary real power is found by: Poc (which means Open circuit power) = (V1)^2 / rm
The secondary voltage is calculated using: V2 = V1 x N2/N1

Hope this helps.
 
Samtheguy said:
To my knowledge, rm and xm do not change when converting to the approximate equivalent circuit.
To go about finding the primary current (Io) you will have to calculate the currents Ioa (active component) and Ior (reactive component). The formulae for finding these are:
Ioa = V1 / rm
Ior = V1 / xm
Then, to find Ioa, use the formula: Io = √((Ioa)^2 + (Ior)^2)
The primary power factor is found using: Ioa / Io
Primary real power is found by: Poc (which means Open circuit power) = (V1)^2 / rm
The secondary voltage is calculated using: V2 = V1 x N2/N1

Hope this helps.

Thank you for your reply it does help.

Now with a load impedance I now need to calculate:

primary current, secondary current, secondary apparent power, secondary reactive power, the effiency, primary power factor, secondary voltage, secondary real power, secondary power factor, and voltage regulation.

I have referred the load impedance to the primary and calculated ZL', I added this impedance to R1 and X1.
So I am now left with three impedances, I took the reciprocals of these and added them together, then took the reciprocal of this again, and this gives me the input impedance.

So to calculate the primary current I used V1/ZL, however it gives me a very big number, is this the correct method?
 
Samtheguy said:
To my knowledge, rm and xm do not change when converting to the approximate equivalent circuit.

I'm interested in knowing if anyone else can confirm this statement? I have a very similar problem to yours that I need to solve.