Calculating static pressure in a duct network servicing 360 identical components involves understanding airflow dynamics and pressure drops. The main duct, divided into four tapered branches, aims for a volumetric flow rate of 500 m3/s, with adjustments possible via gate settings. Using a manometer for static pressure measurement may suffice for basic evaluations, but a pitot tube is recommended for more accurate velocity pressure readings. Maintaining constant air velocity through the ductwork can ensure consistent static pressure across all terminals. Consideration of variable speed drives or terminal dampers may complicate calculations, necessitating advanced modeling techniques.
CKSaZaBoN
Messages
1
Reaction score
0
Hi,

My name is CK and I have question on calculating static pressure through a ducting network.

Some context:
The ducting network services 360 identicle components. This is achieved by dividing a main duct into 4 branches, each servicing approximately 90 components. There is a desired volumetric flow rate of 500 m3/s through the main duct, which theoretically breaks down to 1.39m3/s per component.

The 4 branches that the main duct breaks off to, has a tapered design. Components furthest from the branching point have smaller ID's while ones close have a larger, this is done to ensure a 'semi-consistent' air velocity (m/s), pressure drop etc. Additionally, each component is equally spaced out along the branches. The air flow from each component can be adjusted by a gate setting.

The question:
Currently we use a manometer to measure static pressure at a point very close to the component. This is achieved through a 3mm drilled hole on a side of the duct, close the component. It is believed that static pressure is sufficient in evaluating the balance of air flow between components.

What I would like to do is to put together a spreadsheet, that captures the variation in static pressure from component to component. I have drawings of the entire ducting network.


It would be great if you may provide me with some direction or key equations that would be useful in putting this spreadsheet together.
Thanks in advance!

CK
 
Engineering news on Phys.org
If you designed your ductwork to maintain a constant supply air VELOCITY, this method is called "static regain". This maintains a CONSTANT static pressure in all segments of the duct. Hence, all 360 terminals have the full system static pressure available on the duct side. The individual terminals should have a data sheet which correlates P.D. (pressure drop) with either velocity (fpm) or volume (cfm). Naturally, this is a logarithmic graph.
A more accurate measure would be to use a pitot tube to measure velocity pressure and directly determine the volume of air flow. Sounds like you already have a pressure transmitter, you would only need to replace your probe with a pitot tube to have true volume flow.
I have been in building automation for 30 years, and while the simple calculations you desire are theoretically possible for a system in equilibrium, introducing a VFD drive or a VAV terminal will quickly get your calculations into a second order differential equation.
In your system, is the supply air fan constant speed and the terminal dampers fixed?
 
Thread 'I need a concave mirror with a focal length length of 150 feet'
I need to cut down a 3 year old dead tree from top down so tree causes no damage with small pieces falling. I need a mirror with a focal length of 150 ft. 12" diameter to 36" diameter will work good but I can't think of any easy way to build it. Nothing like this for sale on Ebay. I have a 30" Fresnel lens that I use to burn stumps it works great. Tree service wants $2000.
Hi all, i have some questions about the tesla turbine: is a tesla turbine more efficient than a steam engine or a stirling engine ? about the discs of the tesla turbine warping because of the high speed rotations; does running the engine on a lower speed solve that or will the discs warp anyway after time ? what is the difference in efficiency between the tesla turbine running at high speed and running it at a lower speed ( as fast as possible but low enough to not warp de discs) and: i...
Thread 'Where is my curb stop?'
My water meter is submerged under water for about 95% of the year. Today I took a photograph of the inside of my water meter box because today is one of the rare days that my water meter is not submerged in water. Here is the photograph that I took of my water meter with the cover on: Here is a photograph I took of my water meter with the cover off: I edited the photograph to draw a red circle around a knob on my water meter. Is that knob that I drew a red circle around my meter...
Back
Top