Can I Calculate the Maximum Air Flow for Maintaining Room Temperature Below 36C?

AI Thread Summary
To maintain a room temperature below 36C with a heat dissipation of 4kW in a 3m x 7m x 3.5m room, the airflow must be calculated considering well-mixed air. The formula involves the mass flow rate (W) and the heat capacity (Cp) of air, which is approximately constant and can be found online. Proper air mixing is essential, potentially requiring additional fans and ensuring that intake air does not directly channel to exhaust points. The room volume is relevant for estimating how long it takes to reach steady-state conditions, calculated by dividing the room volume by the airflow rate. The discussion highlights the need for a deeper understanding of thermodynamics rather than seeking free consultation.
yeswan
Messages
3
Reaction score
0
Hi all,

I have a question here. If I have a room with size of 3m x 7m x 3.5m with equipment of heat dissipation of 4kW. A blower fan is installed in the room to draw in the ambient air into the room to reduce the room temperature. At extreme condition the ambient temperature is around 33C. What is the calculation of the maximum air flow is if we want to maintain the room temperature below 36C?

Thanks.
 
Engineering news on Phys.org
Welcome to physics forums.

You need to make sure that the air in the room is well mixed. Then,

WC_p(T - T_{amb}) = 4 kilowatts
 
Hi! Thanks for your reply in advance!

By the way, how to consider the room is well mixed?

And for your formula, what is the W and Cp stand for?

Since this is related to a room volume, doesn't it the room volume have to be considered as well??
 
yeswan said:
Hi! Thanks for your reply in advance!

By the way, how to consider the room is well mixed?

And for your formula, what is the W and Cp stand for?

Since this is related to a room volume, doesn't it the room volume have to be considered as well??

Well, you have a fan blowing air in, so that does some mixing, but the room is pretty big. Maybe another fan would help. You also need to provide an opening where the air can exit the room, and, by supplying the mixing, you want to make sure that the intake air does not channel directly to the exhaust fan so that it avoids mixing with the other air in the room. You can check to see if more mixing is needed by moving a thermometer around the room.

In the formula, W is the mass rate of flow of air through the fan and exit port, and Cp is the heat capacity of air.

The room volume only has to be considered if you are trying to estimate how long it takes for the system to reach steady state. That amount of time will be on the order of the room volume divided by the volume rate of flow of air through the room.
 
Mmm... What is the unit for heat capacity? How do we know that the heat capacity is? Is it get from Psychometric chart or there actually is a constant?

If we also want to calculate the time to steady the room temperature, what is the formula like?

Thanks.
 
It is close enough to constant. You can google specific heat capacity of air...
 
yeswan said:
Mmm... What is the unit for heat capacity? How do we know that the heat capacity is? Is it get from Psychometric chart or there actually is a constant?

If we also want to calculate the time to steady the room temperature, what is the formula like?

Thanks.

I'm beginning to get the feeling that you are not so much interested in learning Physics as you are in getting some free consultation on a specific system you are dealing with. If you want some consultation, many of us can accommodate you, but not for free.
 