Can Voltage Division Be Used to Solve Transformer Line/Load Ratio?

  • Thread starter Thread starter Bluestribute
  • Start date Start date
  • Tags Tags
    Ratio Transformer
AI Thread Summary
Voltage division can be effectively used to determine the load voltage in transformer line/load ratio problems. The proposed calculation of Vload/VG using voltage division appears valid, yielding a load voltage of 11.83<-1.726, which indicates a favorable real part of 0.89. This simplicity in the problem is consistent with its placement early in the chapter, suggesting it is designed to reinforce fundamental concepts. For distribution losses, the approach of using V^2/R while focusing on the resistive component of the line impedance is appropriate, as losses are primarily due to resistance. Overall, the low losses observed are attributed to the efficient design of the power delivery system.
Bluestribute
Messages
192
Reaction score
0

Homework Statement


(in picture)

Homework Equations


V=IZ

The Attempt at a Solution


So last time I had to do KCL to find voltages, so I want to make sure I'm doing this one right. Can I do voltage division and do Vload/VG?

My division would be VG(500<36.87)/(500<36.87 + 60<53.13)

But that approach seems incredibly simply when normally, these problems have some more work involved . . .
 

Attachments

  • Photo on 4-7-15 at 11.13 AM.jpg
    Photo on 4-7-15 at 11.13 AM.jpg
    32.6 KB · Views: 515
Physics news on Phys.org
It's an early problem in the chapter, so it is probably just that simple to provide voltage division across the load. Confirm you don't need to use complex conjugate for power across load.
 
Really? So I got VL as 11.83<-1.726. The ratio is a complex number, but the real part is 0.89 . . . That seems incredibly good? Is it too good?

And for the second part of the question (distribution losses), I'm assuming V^2/R over the Zline component, ignoring the "imaginary" portion of the impedance because it's power losses . . .
 
Your answer looks correct to me. And it looks good. It is supposed to look good. The low losses are due to the low resistance of the power lines (delivery system) of the grid. Power lost on the line doesn't get metered and sold.
 