Choice of a generator set for a drilling pump

AI Thread Summary
A user faced issues powering a 30kw drilling pump with a 45kw generator due to excessive inrush current, which peaked at 190 A during startup, causing the generator to fault. The discussion highlighted that generators should ideally have a power capacity of at least three times that of the pump to handle startup currents effectively. Adjustments to the starter parameters, specifically reducing the acceleration ramp from 15 seconds to 3 seconds, resolved the issue by minimizing the generator's exposure to prolonged overcurrent. The conversation also noted the importance of correctly sized cables to prevent voltage loss, which can increase current draw. Ultimately, the user learned that longer acceleration times are more beneficial for loads with high inertia, not for their specific application.
bachir1994
Messages
18
Reaction score
2
Hello everyone,
I am faced with a problem where I have to power a 30kw drilling pump, with a generator of 45kw (model Gesan), but it does not work. At start-up the current reaches the peak of 190 A and descends gradually, for information the start-up of the pump of the drilling is done by a starter Altistart 22 of Schneider with an acceleration set to 15 seconds, and the generator sets overcurrent fault and stop.
I heard that for this kind of application the generator must have a power of at least 3 times the pump.
At the moment I am doing tests by acting on the parameters of the starter: acceleration and limitation of current.
Thanks in advance for any help.
 
Engineering news on Phys.org
The inrush current for starting a motor can reach as much as 7 times the running current. Most gensets can stand a very brief overload, but it sounds like your situatation involves a much longer inrush period. I suspect you have two choices: (1) get a bigger genset, or (2) get a different pump motor with more acceptable starting characteristics. Not always a happy choice, but that's life!
 
You don't mention the voltage but is that France in your profile picture? In which case..

Quick and dirty calculation for the peak power gives 190 * 230 = 43.7 kW

My guess is the peak current might even be a bit more than 190A? What's the overcurrent trip set to on the generator?

Are the cables between generator and pump correctly sized? If there is any voltage loss in the cables then the current drawn might be higher. For example if the pump load remains constant as the voltage reduces then the current increases. For example 43.7kW at 210V needs 208A.
 
Fit an unloading valve to the pump .
 
  • Like
Likes russ_watters
Thank you for your answers,
I solved, as even the problem by setting the boot ramp to 03 sec, I guess the generator does not see such a short startup overcurrent.
Just before finishing, I have long believed that by increasing the acceleration ramp (either in the dimmer or in the starter) the current is lowered, except in my present case I notice that the current Of startup persisted during the acceleration phase (which was before 15 sec) and my genset fails after 5 sec.
And by looking at the startup curve of an asynchronous motor, I notice that what happens is very logical. And the lengthening of the starting time of an engine serves much more in applications with mechanical loads which present a great deal of inertia. And in my case it was useless to delay the start too much.
A +
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...