BjornFanden said:
Yes, that helps, thank you for your time.
@cabraham and
@jim hardy , one last follow up question:
If we have a wye-wye transformer where only 1 side is grounded, this means no zero sequence current can flow in the transformer, correct?
Correct.
What would happen if this transformer were supposed to supply a load that produces 3rd harmonics i.e. zero sequence currents, would it be impossible for this transformer setup to supply the load?
Yes, but I need to emphasize the following. "Zero sequence" & "3rd harmonic" currents are NOT one & the same. Zero sequence currents exist when the line and/or load is unbalanced. The triplen harmonic currents are a natural property of the non-linear transformer core. Zero sequence currents are bound by the law of balancing ampere-turns. A zero sequence current on the secondary can exist only if there is an equal amp-turn value on the primary, & vice-versa. The triple harmonics, OTOH, are NOT bound by amp-turn balance. The triple harmonic is a part of the magnetizing current, & magnetizing current does not get balanced.
Take a single phase unit with no load. The magnetizing current exists in the primary but not in the secondary, thus amp-turns do not balance. The triple harmonic exists as the primary path is 2 wires, so all harmonics have a path. But if the unit is a 3-phase with a Y on both primary & secondary, w/o a delta tertiary, the magnetizing current in the primary will contain non-triplen harmonics, i.e. 1st, 5th, 7th, 11th, etc., with or without a neutral. But the triplens, i.e. 3rd, 9th, 15th, etc., will exist only if a neutral path exists.
Now getting back to zero sequence current, if the xfmr is Y-Y, no delta tertiary, an unbalanced load on the secondary from line to neutral will result in the 3 phase voltages going out of balance. With 3 phase shell type core, or 3 single phase units ganged together for 3 phase operation, the Y-Y configuration is avoided, since it cannot support an unbalanced load with only 3 wires. A 4th wire, neutral wire, mitigates this problem. But the whole purpose for using 3 phase is to save conductor cost/space. A 3 phase system requires only 75% the aluminum (or copper) of single phase, or any other number of phases. Using a 4th wire for the neutral defeats the savings, so that a 3 phase system consumes 100% the amount of conductor as any other number of phases.
If the distance is large, a 4th wire adds a lot of cost as well as support structure needed to carry this wire. Also, with a Y-Y, even if the secondary load is balanced, the flux gets distorted by the absence of triplen harmonics. The line to neutral voltages can exhibit peaks that are 40 to 70% higher than a pure sine curve. This is mitigated by a delta tertiary. The delta requires an additional set of windings, light gauge since the current is small. The cost is much less than miles of extra wire. The triplen harmonics circulate in the delta, & are not balanced in the primary.
For these reasons it has been standard practice in the power industry to avoid a pure Y-Y connection. With 3-phase shell type cores, & 3 individual cores, the Y-Y is very problematic. But if a delta is present, then zero sequence currents due to unbalanced loads circulate in the delta, as well as triplen harmonics. The delta mitigates both problems. Sometimes it is desirable to connect both primary & secondary in Y. A Y can provide a very good ground point, & is robust for high voltage insulation stress relief. But a delta is added via a tertiary to maintain support for unbalanced loading, & harmonics.
There is, however, another core type in use, the 3-phase core type unit. This is a pair of "E" shaped cores. Each core half has 3 legs of equal width, 2 pieces joined together. This type of core has all 3 phases **magnetically** coupled in addition to electrically coupled. The other 2 have only electrical coupling. This core type behaves as if it had a delta tertiary. The technical reason is involved, I don't have time, but maybe I can write a paper soon. The 3 fluxes are forced to sum to zero. A delta forces the 3 voltages to sum to zero via its closed loop. But voltage is the time derivative of flux, times turns, with a minus sign. Anyway, if the core is a 3-legged "E" type pair,
a Y-Y configuration supports unbalanced loading on the secondary, using only 3 primary wires, without a delta.
Maybe I can explain why later.
However if a delta tertiary winding were to be introduced this transformer could supply the load that produces 3rd harmonics, am I correct?
Yes.
:-) Claude