Connecting two 240V heater elements in series to a 240V relay will result in reduced power output, approximately half that of a single coil, as the voltage is divided between the two heaters. For optimal performance, the heaters should be connected in parallel to ensure each receives the full 240V. If the combined current draw exceeds 3A (720W), the relay may fail due to overload. It's crucial to check the power ratings of the heaters to avoid exceeding the relay's capacity. Proper configuration is essential for efficient heating and relay longevity.
Etude
Messages
28
Reaction score
0
Ok this might be a really stupid question but I would appreciate some help.

I have a controller with a relay output rated at 240 V 3A. I was wondering what happens if I connect 2 heater elements of 240 V each in series to this relay. Will it ruin the relay over time? Will the output of the heaters be affected?

Help is appreciated. :smile:
 
Engineering news on Phys.org
Welcome to PhysicsForums!

Making the naive assumption that your heating coils have constant resistance at all temperatures (they almost certainly won't, but also shouldn't change drastically for large values of drastic), what'll happen is that the in-series coils will only output a quarter of their power, and the sum of the two will result in only half the power output of a single coil.

You can see this by rearranging Ohm's Law, V=I*R, and the power formula, P=I*V:
P=\frac{V^2}{R}

To double your power output, you should really connect the coils in parallel (so that 240V is present across each coil).

HOWEVER, you don't mention how much power your heating coils are rated for (or equivalently, how much current they consume). If they individually or together draw more than 3A (720W), you have a problem.

If this is the case, your relay may burn out because the coils are drawing too much current. Your controller might need to drive a relay driving the coils (either one supplying both in parallel, or two supplying one each)
 
If you connect in series two identical heating elements, each rated for 240 VAC, then when you power that series circuit with 240 VAC you will be disappointed at the low amount of heat produced. For full power, they'd need 480 VAC.

Though at 240 VAC, so long as the series combination doesn't draw more than 3A, the relay shouldn't be upset.
 
3 A at 240 V gives about 720 watts, check the heater ratings if they add up to more then 720 you need a bigger relay.
 
Thanx so much guys for your great explanations and quick response! :)
The three of your answers put together really explained the situation to me! Thanx a ton!
Am already feeling good about joining PhysicsForum!
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...