Delta wye connection using 3 small transformers

AI Thread Summary
The discussion centers on wiring three small transformers to create a delta-wye connection, addressing confusion over whether to connect X1 or X2 as the neutral. Both configurations yield a three-phase output, but the phase rotation differs by 180 degrees depending on the choice of connections. The industry standard recommends that the higher voltage side (wye) leads the lower voltage side (delta) by 30 degrees. Proper labeling and grounding of the neutral are emphasized for safety and compliance with NEMA standards. The conversation concludes with the sharing of a detailed schematic to aid in understanding the connections.
sauce6358
Messages
3
Reaction score
0
I am confused from a couple of diagrams I have about how to correctly wire 3 small transformers to form a delta wye connection. The transformers are labeled as
Primary H1 H2, H1 H2, H1 H2
Secondary X2 X1, X2 X1, X2 X1

My question is in all the diagrams I have the Delta connections are identical, but the wye connections in one of the diagrams shows all of X1's tied together to form the neutral and another diagram shows all of X2's tied together to form the neutral. So does it matter whether I use X1's as the hot connections and X2's as the neutral connections or viceversa?
THANKS!
 
Engineering news on Phys.org
Connecting all X2 together will give 3 phase output.
Connecting all X1 together will give 3 phase output.
There will be a difference of 180 degrees between the 3 phases depending on which connection is used. ?There may be a difference in phase rotation, will have to think about that?
The output voltage will be the same for both connections.
If you are using the output for a rectifier the connection will not make any difference.
If you are using the output for phase control, it may make a difference depending on the circuit you are using.
 
Is the higher voltage side connected in wye? I would recommend using NEMA standardized connections. The industry practice is that the higher voltage side be labeled so as the line to line voltages on the high voltage side lead those of the low voltage side by 30 degrees electrical phase.

If the high side is in wye, low side in delta, here are the connections:

Y-side: Let us use "H2" as the neutrals. All 3 "H2" terminals are joined. Phase A hot connects to H1 of xfmr A, phase B hot connects to H1 of xfmr B, phase C hot connects to H1 of xfmr C. If this Y-side is a secondary, then it might be desirable to connect the neutral (H2-H2-H2) to Earth ground. It depends on the application. If the Y-side is the primary, then an Earth ground may already be present. Definitely check if you need to have the neutral grounded.

Delta-side: Connect X2 of xfmr A to X1 of xfmr B. Connect X2 of xfmr B to X1 of xfmr C. Connect X2 of xfmr C to X1 of xfmr A. Then label as follows.

The junction of xfmr A X1 & xfmr C X2 becomes phase A. The junction of xfmr B X1 & xfmr A X2 becomes phase B. The junction of xfmr C X1 & xfmr B X2 becomes phase C.

With these connections & phase labeling, the line to line voltages on the lower voltage delta side will lag those on the higher voltage wye side by 30 degrees, in accordance w/ power industry standard practice in North America. I.e. the A-B line-to-line voltage on the wye side leads the A-B l-l voltage on the delta side by 30 degrees.

If you're using the delta as the high side, let me know & I'll help you, as the designations would be different. Have I helped? Later, I'll attach a sketch.

Claude
 
cabraham said:
Is the higher voltage side connected in wye? I would recommend using NEMA standardized connections. The industry practice is that the higher voltage side be labeled so as the line to line voltages on the high voltage side lead those of the low voltage side by 30 degrees electrical phase.

If the high side is in wye, low side in delta, here are the connections:

Y-side: Let us use "H2" as the neutrals. All 3 "H2" terminals are joined. Phase A hot connects to H1 of xfmr A, phase B hot connects to H1 of xfmr B, phase C hot connects to H1 of xfmr C. If this Y-side is a secondary, then it might be desirable to connect the neutral (H2-H2-H2) to Earth ground. It depends on the application. If the Y-side is the primary, then an Earth ground may already be present. Definitely check if you need to have the neutral grounded.

Delta-side: Connect X2 of xfmr A to X1 of xfmr B. Connect X2 of xfmr B to X1 of xfmr C. Connect X2 of xfmr C to X1 of xfmr A. Then label as follows.

The junction of xfmr A X1 & xfmr C X2 becomes phase A. The junction of xfmr B X1 & xfmr A X2 becomes phase B. The junction of xfmr C X1 & xfmr B X2 becomes phase C.

With these connections & phase labeling, the line to line voltages on the lower voltage delta side will lag those on the higher voltage wye side by 30 degrees, in accordance w/ power industry standard practice in North America. I.e. the A-B line-to-line voltage on the wye side leads the A-B l-l voltage on the delta side by 30 degrees.

If you're using the delta as the high side, let me know & I'll help you, as the designations would be different. Have I helped? Later, I'll attach a sketch.

Claude

Yes, Delta Primary Side and Wye Secondary Side. High/Low. Thanks!
 
The attached pdf details how to obtain the industry standard high voltage side 30 degree phase lead using a wye-delta as well as a delta-wye xfmr configuration. I added polarity dots to the schematics as a visual aid. This should be what you are looking for. Hopefully it is legible.

Claude
 

Attachments

cabraham said:
The attached pdf details how to obtain the industry standard high voltage side 30 degree phase lead using a wye-delta as well as a delta-wye xfmr configuration. I added polarity dots to the schematics as a visual aid. This should be what you are looking for. Hopefully it is legible.

Claude

Thanks So Much! Sauce
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...